This temperature difference between water input and output is only a few degrees at most at very low speed and a big power to dissipate. It is less than 1 ° C typically (flow> 2 L / min). With this method, it requires appropriate instruments to measure just 0.01 ° C or better. Indeed, every hundredth of a degree equivalent to several watts after calculation, especially where high-speed input-output gap is reduced, which reduces the sensitivity of the measure:
English version
The advantage of this method is that we know exactly the power dissipated by each radiator. There is no loss side or powers unknown variables introduced in the measuring circuit (eg a pump.). Here, everything happens only between the entry and exit of the radiator.
The method is to measure the temperature rise of water compared to air in a single loop, where we introduce a constant heating power, is another method. It is valid if we take some precautions because it introduces factors more or less unknown, but it does not require tools for high resolution. Each method has its advantages and disadvantages vis-à-vis what is sought and what was available. Either one works at constant power deltaT to find the water-air, or are working on water-air deltaT to find the constant power.