    Needing some Residential Electrical Help.....Major 56K Warning!

    Any Electricians in the House?

    I've pretty much finished up the plumbing end of my project here:

    Yes, Another Car Radiator Thread....Major 56K Warning!

    Its up and running. Problem is: Its current electrical supply is a 100Ft extension cord. That cord is plugged into a circuit--that I don't know what all else is drawing power from it. Basically, I just need to run power from the meter box outside--to the out-building.

    I've installed circuits before. I'm not new, but I'm not an Electrician either. I have a 60amp breaker box and a 60amp switch for the out-building. I really have 1 main question that I'm a bit uncertain about, and I need to know: What is Safe and what is legal!


    Here's the meter box--Outside:



    Here is the inside:



    With a few lines added:



    RED: The yellow terminal wires connect at the bottom of the 200amp breaker and then loop up and connect at the top.

    GREEN: My question is: Can I just connect up to the yellow terminals and run to the switch and breaker box? Or, do I need to install another breaker next to the 200amp that's there? What's Legal? What's Safe?


    I have 1x15amp and 1x20amp breakers for the 60amp breaker box. I only expect to be pulling ~250w (or less) 24/7. But I do have 3x 4' flourescent shoplights (80w each--only need one most of the time), but I don't expect to use them much. And an air compressor (~20gallon) that will only run as needed--which will be every 2 months or less.


    Can anybody point me in the right direction......?
    Last edited by Naja002; 06-15-2008 at 07:17 AM.

  2. #2
    I am Xtreme
    Join Date
    Sep 2007
    Location
    New Jersey, U.S.
    Posts
    2,329
    I'm not an electrician, but I was curious. Wouldn't it be better to put an additional breaker in your existing breaker box and run a wire from that? Otherwise, the only breaker you'll have on the line is the 200amp and that sounds dangerous. Even if you put a breaker on the new line, there is still the chance of a short between the 200amp breaker and the out building breaker.

    Are you even allowed to such things on your own? In NJ I'm pretty sure that you're required to use an electrician. In cases where you can do things yourself, you're still supposed to get them inspected afterwards.

  3. #3
    SSD faster than your HDD
    Join Date
    Feb 2005
    Location
    Kalamazoo, MI
    Posts
    2,627
    You cannot attach to the meter box, at least not in this state. That would have to be done by the Power company.

    You can, run a new circuit in the house, using a 220V breaker of your choice and some good heavy cable out to the shed. Then install the box out in the shed with other breakers to distribute the power.

  4. #4
    Xtremely High Voltage Sparky's Avatar
    Join Date
    Mar 2006
    Location
    Ohio, USA
    Posts
    16,040
    You must attach a line from your breaker box in your house. You cannot attach to the meter box like that, not only is it illegal to do so but highly dangerous.

    How far is the main panel from the out building?
    The Cardboard Master
    Crunch with us, the XS WCG team
    Intel Core i7 2600k @ 4.5GHz, 16GB DDR3-1600, Radeon 7950 @ 1000/1250, Win 10 Pro x64

  5. #5
    Xtreme Addict
    Join Date
    Jul 2006
    Location
    Usa
    Posts
    1,166
    Ok, slow down folks.....I'm not sure you are understanding what I am saying/wanting to do.....





    Quote Originally Posted by twilyth View Post
    I'm not an electrician, but I was curious. Wouldn't it be better to put an additional breaker in your existing breaker box and run a wire from that? Otherwise, the only breaker you'll have on the line is the 200amp and that sounds dangerous. Even if you put a breaker on the new line, there is still the chance of a short between the 200amp breaker and the out building breaker.

    Are you even allowed to such things on your own? In NJ I'm pretty sure that you're required to use an electrician. In cases where you can do things yourself, you're still supposed to get them inspected afterwards.
    I have a 60amp breaker box with a 15 amp breaker and a 20 amp breaker that will go into the out-building. Meter Box>Switch>60amp breaker box>appliances. I'm not looking to wire up a 110 outlet directly to my meter box or anything like that.....



    Quote Originally Posted by RyderOCZ View Post
    You cannot attach to the meter box, at least not in this state. That would have to be done by the Power company.

    You can, run a new circuit in the house, using a 220V breaker of your choice and some good heavy cable out to the shed. Then install the box out in the shed with other breakers to distribute the power.
    With an electrician friend, we connected to it as you see for the main power supply/breaker panel. AFTER the meter is the resident's responsibility. I'm not looking to connect to the meter--what you see in the pic is AFTER the meter. That's on me, not them.....

    Quote Originally Posted by SparkyJJO View Post
    You must attach a line from your breaker box in your house. You cannot attach to the meter box like that, not only is it illegal to do so but highly dangerous.

    How far is the main panel from the out building?
    Ok, see my reply above. The run is only about 15' linear feet--not a big deal, but really doesn't matter anyway. The breaker panel inside here is FULL--Yes, completely. I could remove a 20amp breaker and replace it with a twin 20amp breaker--but that's not really the best idea. I might go that route to simply this, but i'd really rather not.

    I'm not so sure what is so dangerous about it. The yellow terminals are connected to the 200amp breaker on the "Off" side. I trip the 200amp breaker and---there's no juice.

  6. #6
    V3 Xeons coming soon!
    Join Date
    Nov 2005
    Location
    New Hampshire
    Posts
    36,363
    We don't know one another but I will speak as if we're old friends.
    I want to see you here alive and healthy long term so please, spend the money and have a lisenced electrician come and do this the right and legal way. It will cost more but that cost is minor to your sleeping better and all the other factors that I'm sure I don't have to include.
    Please..
    Thanks for reading.
    Crunch with us, the XS WCG team
    The XS WCG team needs your support.
    A good project with good goals.
    Come join us,get that warm fuzzy feeling that you've done something good for mankind.

    Quote Originally Posted by Frisch View Post
    If you have lost faith in humanity, then hold a newborn in your hands.

  7. #7
    HARD CRUNCHER!!
    Join Date
    Nov 2006
    Location
    Chicago
    Posts
    1,787
    Electrician here bro!!! Got msn? yohanthe1 at sbcglobal dot com


    I need the Milbank part # off the meter socket.

    edit: Ok found the socket, yes you can add a single or 2 pole or single pole breaker in that box no problem.
    Last edited by [XC] Hicks121; 06-04-2008 at 11:06 AM.
    Quote Originally Posted by mike047 View Post
    CRUNCH HARD, it may not help me and you, but it might help the Kids.

  8. #8
    Xtreme Addict
    Join Date
    Jul 2006
    Location
    Usa
    Posts
    1,166
    To add to the above, this is what's going inside the out-building:

    Breaker box and switch:
















    I understand everything from the meter box on......my only question is: Do I need to add another breaker inside the meter box? Or, can I connect directly to the yellow terminals......?

  9. #9
    Xtreme Addict
    Join Date
    Jul 2006
    Location
    Usa
    Posts
    1,166
    Ok, its sorted. Got it--No sweat. Thanks everyone for your concern, but I can do this--its really not a big deal.....

    It'll get done some time between tomorrow and tuesday!

    Many Thanx!
    Last edited by Naja002; 06-04-2008 at 12:21 PM.

  10. #10
    HARD CRUNCHER!!
    Join Date
    Nov 2006
    Location
    Chicago
    Posts
    1,787
    Ok we got him sorted out. He can add up to 4 branch circuit breakers off that box.

    Naja, dont forget to pull a ground man!!!
    Quote Originally Posted by mike047 View Post
    CRUNCH HARD, it may not help me and you, but it might help the Kids.

  11. #11
    Xtreme Addict
    Join Date
    Jul 2006
    Location
    Usa
    Posts
    1,166
    Quote Originally Posted by [XC] Hicks121 View Post
    Ok we got him sorted out. He can add up to 4 branch circuit breakers off that box.

    Naja, dont forget to pull a ground man!!!
    Yeah, that's the part with the metal plates for my shoes and the metal cap,.......right?

  12. #12
    Xtremely High Voltage Sparky's Avatar
    Join Date
    Mar 2006
    Location
    Ohio, USA
    Posts
    16,040
    OK I got confused there, I thought you were wanting to hook up an outlet directly to those studs in there. Sorry about that.
    The Cardboard Master
    Crunch with us, the XS WCG team
    Intel Core i7 2600k @ 4.5GHz, 16GB DDR3-1600, Radeon 7950 @ 1000/1250, Win 10 Pro x64

  13. #13
    Xtreme Addict
    Join Date
    Jul 2006
    Location
    Usa
    Posts
    1,166
    Quote Originally Posted by SparkyJJO View Post
    OK I got confused there, I thought you were wanting to hook up an outlet directly to those studs in there. Sorry about that.
    No, not an outlet.... I wanted/needed to know if I needed another breaker in there or if I could wire up directly to those yellow terminals--then to the switch, breaker box, etc. in the out-building.

    After Hicks explained that those spots are for normal, everyday breakers (like in your inside panel)--it all started coming together. I took a breaker out there and checked--Yep, sure enough--He's right. Won't be a problem at all.....

    Life is Good!

  14. #14
    Xtreme Cruncher
    Join Date
    Nov 2005
    Location
    Rhode Island
    Posts
    2,740
    So curious, are you just going to tie into those lines driectly, or just throw in a 60-100 amp breaker, and then run the lines to your switch?
    Fold for XS!
    You know you want to

  15. #15
    Xtreme Addict
    Join Date
    Jul 2006
    Location
    Usa
    Posts
    1,166
    Quote Originally Posted by [XC] Lead Head View Post
    So curious, are you just going to tie into those lines driectly, or just throw in a 60-100 amp breaker, and then run the lines to your switch?
    Tossing in a couple 20 amp breakers, but tying into the lines was the question that I originally had. The spaces next to the big 200amp breaker are for normal everyday breakers--so, that's what's going in there. I was going to use a 20 and a 15 in the out-building, but I just got back from Lowes and decided on 2 20amp circuits. So, 2x 20amp breakers are going into the meter box, and 2x 20amp circuits are going into the breaker box inside the out-building. It will be just as easy to run the 2 separate circuits (1 run of pipe) from box to box as it would be to do it with 1 run of wire. Costs a few dollars more, but that's cool.


    Scratching my head and wondering why I even need the breaker box in the out-building---seems like the breakers in the meter box and the switch in the out-building would be enough......hmmmmm Any thoughts on this....?
    Last edited by Naja002; 06-04-2008 at 05:39 PM.

  16. #16
    Xtreme Cruncher
    Join Date
    Nov 2005
    Location
    Rhode Island
    Posts
    2,740
    You shouldn't need the breakers in the building, the switch should be more then enough. The only thing to consider though is that the distance between your buliding and the box, the further the box is away, you'll have to compensate with thicker wire. You may also need to adjust breaker size accordingly
    Fold for XS!
    You know you want to

  17. #17
    V3 Xeons coming soon!
    Join Date
    Nov 2005
    Location
    New Hampshire
    Posts
    36,363
    Let's have a big cheer for Hicks!
    Crunch with us, the XS WCG team
    The XS WCG team needs your support.
    A good project with good goals.
    Come join us,get that warm fuzzy feeling that you've done something good for mankind.

    Quote Originally Posted by Frisch View Post
    If you have lost faith in humanity, then hold a newborn in your hands.

  18. #18
    Xtreme Addict
    Join Date
    Jul 2006
    Location
    Usa
    Posts
    1,166
    The total length of wire from meter box to switch will only be ~25ft, 30Ft max. I picked up 12/2 w/ground. Will handle the 20amps and the length is short enough not to be an issue.

    Inside the building I expect 2 runs of wire from the switch box of 25' or less.

    I don't think there are any issues, or reasons to need the 2nd breaker box.....

    Thoughts?

  19. #19
    Xtreme Cruncher
    Join Date
    Nov 2005
    Location
    Rhode Island
    Posts
    2,740
    I personally wouldn't want to send 20 amps through 12 guage at 30 feet. Most of the wiring in my house is only 15 amps, and that runs on 12/2 w/ground.
    Fold for XS!
    You know you want to

  20. #20
    V3 Xeons coming soon!
    Join Date
    Nov 2005
    Location
    New Hampshire
    Posts
    36,363
    Quote Originally Posted by [XC] Lead Head View Post
    I personally wouldn't want to send 20 amps through 12 guage at 30 feet. Most of the wiring in my house is only 15 amps, and that runs on 12/2 w/ground.
    12/2 is perfect for a 20amp line.
    That's what it is designed to do.
    15amp circuits are fine on 14/2.
    30amp is 10/2 for 110v and 10/3 for 220v
    also a 30ft run is nothing.
    Think about the lengths of runs snaked through your house from the panel to a 2nd floor bedroom or in an apartment house from the panel to the 4th floor.
    Non issue.
    Crunch with us, the XS WCG team
    The XS WCG team needs your support.
    A good project with good goals.
    Come join us,get that warm fuzzy feeling that you've done something good for mankind.

    Quote Originally Posted by Frisch View Post
    If you have lost faith in humanity, then hold a newborn in your hands.

  21. #21
    Xtreme Addict
    Join Date
    Jul 2006
    Location
    Usa
    Posts
    1,166
    Quote Originally Posted by Movieman View Post
    12/2 is perfect for a 20amp line.
    That's what it is designed to do.
    15amp circuits are fine on 14/2.
    30amp is 10/2 for 110v and 10/3 for 220v
    also a 30ft run is nothing.
    Think about the lengths of runs snaked through your house from the panel to a 2nd floor bedroom or in an apartment house from the panel to the 4th floor.
    Non issue.
    Thank You My understanding is the same. Most importantly though, I only plan on pulling ~250w 24/7 on one circuit.

    The other circuit will have 2 motion detector lights (at night), 1-3 4' flourescent shop lights (80w each), the occassional power tool and the air compressor that I rarely use ( every couple of months). Its extremely unlikely that both motion detector lights, all 3 flourescents and the air compressor willing be running while I'm using some power tools!

    The 12/2 is rated for the 20amp, but I don't expect to be using much of its ability at any given time. In reality--its a bit of overkill, but better to have too much power available then not enough!

    Do we agree that I really don't need the breaker box inside the building? I have the switch to cut power in the building and the breakers in the meter box....That enough?
    Last edited by Naja002; 06-04-2008 at 07:27 PM.

  22. #22
    Xtreme Cruncher
    Join Date
    Nov 2005
    Location
    Rhode Island
    Posts
    2,740
    Dunno man, all the 15 amp circuits on my house are run with 12/2, we only have like 2 20 amp circuits, and I'm pretty sure those are on 10/2, although I suppose I'm a bit paranoid as many people I know (including my grandfather) are master electricians, and they always preach always go bigger then what you need.

    Really the only reason to have a breaker box within the building itself is just for convienece, if you want to turn off one circuit, but not the other.
    Last edited by [XC] Lead Head; 06-04-2008 at 07:28 PM.
    Fold for XS!
    You know you want to

  23. #23
    SSD faster than your HDD
    Join Date
    Feb 2005
    Location
    Kalamazoo, MI
    Posts
    2,627
    15 amp here are 14/2 and 20 amp are 12/2

    D'oh.. Dave said it, LOL.

  24. #24
    Xtreme Addict
    Join Date
    Jul 2006
    Location
    Usa
    Posts
    1,166
    Quote Originally Posted by [XC] Lead Head View Post
    ...and they always preach always go bigger then what you need.

    I understand and agree with that principle, but that was my point above: I really don't expect to be using anywhere near 20amps on either circuit, so in reality--I am going bigger than I need.....




    Quote Originally Posted by [XC] Lead Head View Post
    Really the only reason to have a breaker box within the building itself is just for convienece, if you want to turn off one circuit, but not the other.
    That's actually a very Good reason in my case. But I can also just shut off the power at the specific breaker in the meter box. The switch is 2 pole, so the "on" breaker would still be getting juice. The circuits will be very simple and easy to remember, so that won't be an issue. Right now, it looks like I'm just going to return the breaker box and breakers for it.

  25. #25
    Xtreme Addict
    Join Date
    Jul 2006
    Location
    Usa
    Posts
    1,166
    Ok, I just thought that I would update this thread. The 2 circuits to the out-building are installed and operational. Please do not try this stuff at home unless you are certian of what is what and what you are doing!

    I still have 2x 20amp circuits to run a few feet into this room. Thank You all for Your prior concern. With Hicks help--it was a breeze. He stuck with me all the way via email and msn. Answered any question I had--regardless of silly or just being sure, etc. Major Props to You, Hicks!


    Here's some pix:

    First, I had to convince myself of one thing:


    I'm a Tiger!

    I'm a Tiger!
    I'm a Tiger!

    Once psyched--I was ready to roll........


    Here's the start point:



    What it looked like before I started:



    So, I ran the wire (2x 12/2 w/gnd) and 3/4" conduit from the meter box into the ground:



    Under ground ~15':




    Then up into the out-building and into this switch box (disconnect):



    Close-up of the wiring inside the disconnect--black in top, black out bottom, white to white and ground to the ground bar:




    2 Circuits out of the disconnect--1 to a junction box that Y's out to the left and right, 1 to the homemade strip outlet:



    Close-up of the Y-junction box and HM strip outlet. The HM strip outlet is: GFI>outlet>outlet>outlet>Lightswitch for switched outlet:



    From the junction box, the Y to the left runs over to another junction box then up to a motion light and over to a switched outlet:



    And to the right for the same setup on the other end. This way I have light regardless of which door I enter and have motion lights for the outside at both ends:


    I will be adding light switches to the motion light boxes in order to "program" them--now and in the future. I will be mounting 4' double bulb fluorescent light to the 2x4s above each door, so I have light as soon as I enter. I have a 3rd one that will be plugged into the switched outlet on the HM strip.

    So, after running the circuits and getting everything installed--it was time to hook it all up to the meter box:


    And this is what it currently looks like:



    I'll be installing the other 2 circuits this week, so I went ahead and pulled the 2 blanks out.......

    Now as long as the meter-reader guy doesn't mess with me.......

    Hicks---I really can't Thank You Enough! Very Cool!