    I did not calculate it myself, but I trust the calculation:

    4th stage 315 W at -160°C
    compressor size 20 ccm / 3,48 m³/h
    Max. motor power ~ 585 W
    Max condensor power ~ 900 W
    COP ~ 0,54

    sorry, I don't know more e.g. superheat or something...

    In few weeks we will see how it works out

  2. #52
    Aussie God
    Join Date
    Feb 2005
    Location
    Copenhagen, Denmark
    Posts
    4,596
    Outstanding... :|
    Competition ranking;
    2005; Netbyte, Karise/Denmark #1 @ PiFast
    2008; AOCM II, Minfeld/Germany #2 @ 01SE/AM3/8M (w. Oliver)
    2009; AMD-OC, Viborg/Denmark #2 @ max freq Gigabyte TweaKING, Paris/France #4 @ 32M/01SE (w. Vanovich)
    2010: Gigabyte P55, Hamburg/Germany #6 @ wprime 1024/SPI 1M (w. THC) AOCM III, Minfeld/Germany #6 @ 01SE/AM3/1M/8M (w. NeoForce)

    Spectating;
    2010; GOOC 2010 Many thanks to Gigabyte!


  3. #53
    Xtreme Legend
    Join Date
    Mar 2005
    Location
    Australia
    Posts
    17,242
    talk about having some muscle

    good luck with your build man
    Team.AU
    Got tube?
    GIGABYTE Australia
    Need a GIGABYTE bios or support?



  4. #54
    Xtreme Member
    Join Date
    Dec 2005
    Location
    Rennes (france)
    Posts
    443
    Quote Originally Posted by godmod View Post
    I did not calculate it myself, but I trust the calculation:

    4th stage 315 W at -160°C
    compressor size 20 ccm / 3,48 m³/h
    Max. motor power ~ 585 W
    Max condensor power ~ 900 W
    COP ~ 0,54

    sorry, I don't know more e.g. superheat or something...

    In few weeks we will see how it works out
    Qv = (P / (h_gaz - h_bub)) * Ug (*3.6 to get m³/h)

    For -160°C captube end, -145°C out, 20°C suction temperatue you get
    Qv = (315 / (705-165))*1.32*3.6 = 2.8 m³/h

    Which is in fact achievable with his last compressor I think

  5. #55
    Xtreme Member
    Join Date
    Jul 2005
    Location
    Austria
    Posts
    428
    Is there a post missing?
    I thought i would have been replying to a very certain post this morning

  6. #56
    Registered User
    Join Date
    Oct 2006
    Location
    Germany
    Posts
    73
    THx for all the nice words guys



    Quote Originally Posted by 7499richard View Post
    how do you like those Allen Bradley terminals, I work in automation and work with those a lot, as well as Phoenix terminals, I find the Phoenix much nicer to work with.
    I took these form an old A/C unit, manufactor is “Weidmüller”. For final electrics I will use Phoenix- Contact terminals.

    Quote Originally Posted by Clemmaster View Post
    Impressive work and very nice compressors you've got there! Second stage seem a bit overkill with only -75.5°C evaporating temperature don't you think? Don't you think you could also switch 2nd and 3rd stage compressor to get benefit of the 67ccm for a gas with high specific volume like R14? In every case this beauty may work like a charm
    It looks like the second compressor is a little bit too big, but we will se how it performs when all four stages are running. I can use frequency modifier here, too As you see, I like this machines.



    Quote Originally Posted by 4Qman View Post
    Are you implementing any features to allow control of the temperatures for Cold bugged CPU's ?

    Oh and awesome work. Very skilled indeed
    As teurorist said, there will be the possibility to change compressor speed, or do some regulation with hot- gas.


    Efficience… When you want to have a fast and energy saving PC, buy an new CPU instead of using phase change und overclocked CPU


    Quote Originally Posted by piotres View Post
    What are fuctions of that XMT7100 controller ? This is controller till -100C ?
    Till -200°C, takes PT100 and K-Type. Little bit cheaper than dixell, only "problem" is that the display is little bit small i think.
    Write me PM.

    Quote Originally Posted by Clemmaster View Post
    Qv = (P / (h_gaz - h_bub)) * Ug (*3.6 to get m³/h)

    For -160°C captube end, -145°C out, 20°C suction temperatue you get
    Qv = (315 / (705-165))*1.32*3.6 = 2.8 m³/h

    Which is in fact achievable with his last compressor I think
    Can you give me a tip how long captube for last stage have to be and what diameter it should have? Need to prepare the "extreme" suction line soon, insulation is really heavy Pics in some weeks.

    Quote Originally Posted by godmod View Post
    Is there a post missing?
    I thought i would have been replying to a very certain post this morning
    Yes, there was an post with an really huge compressor and some calculation this morning, don`t know what happend .


    stay extreme!

    august

  7. #57
    Xtreme Enthusiast
    Join Date
    Oct 2006
    Location
    England
    Posts
    702
    Truly outstanding workmanship and spec august123, this has got to be the best cascade on all accounts for loaded cooling power.

  8. #58
    Xtreme Member
    Join Date
    Dec 2005
    Location
    Rennes (france)
    Posts
    443
    Quote Originally Posted by godmod View Post
    Is there a post missing?
    I thought i would have been replying to a very certain post this morning
    Yes I deleted a post with previous calculation because of wrong starting values (~30m³/h which was off course a freaky value )

  9. #59
    Xtreme Member
    Join Date
    Dec 2005
    Location
    Rennes (france)
    Posts
    443
    Quote Originally Posted by august123 View Post
    Can you give me a tip how long captube for last stage have to be and what diameter it should have? Need to prepare the "extreme" suction line soon, insulation is really heavy Pics in some weeks.
    No I can't sorry, I've never played with such gases (very low density ) and captube diameter (~1 - 1.2mm seen the length of the line )

    Why don't you try any CPEV to start with and high diameter captube after CPEV? That would be a solution for coldbug

  10. #60
    Xtreme Owner Charles Wirth's Avatar
    Join Date
    Jun 2002
    Location
    Las Vegas
    Posts
    11,656
    Moster build, very nice.

    CPEV would be a way to adjust temps on the fly, it took quite a few attempts to get the right one. I am using a half ton valves now on my three stage.

    I love the cleanness of it all, the power is tight too.
    Intel 9990XE @ 5.1Ghz
    ASUS Rampage VI Extreme Omega
    GTX 2080 ti Galax Hall of Fame
    64GB Galax Hall of Fame
    Intel Optane
    Platimax 1245W

    Intel 3175X
    Asus Dominus Extreme
    GRX 1080ti Galax Hall of Fame
    96GB Patriot Steel
    Intel Optane 900P RAID

  11. #61
    Xtreme Member
    Join Date
    Nov 2007
    Posts
    107
    you joke, the tev in third stage lost at -140 a little bit at gas superheat screw CPEV will be critical, too i think ?and 4m away with only 2mm captube from the cpev to evap you think that will work good ??

    i think to find the right captube length this will start with much testing because he also wants to use the 95% methan like ricky

    fugger
    a -160° cpev who wants touch it to change settings no I think the Adjustment screw will freeze like the screw in the r23 stage at the Expansion Valve
    we wanted to change but it was sitting very strange by -80° so what is by -160°C, other problem is the sealing...
    but this is my opinion
    Last edited by teurorist; 03-10-2008 at 12:23 PM.
    little German

  12. #62
    Xtreme Member
    Join Date
    Jul 2005
    Location
    Austria
    Posts
    428
    Since methane is very cheap i would use a captube and try until i got the right lenght. i would not take a cpev because i would be afraid of leak issues.

  13. #63
    Xtreme Member
    Join Date
    Oct 2006
    Location
    B/EH, Germany
    Posts
    219
    Quote Originally Posted by godmod View Post
    Since methane is very cheap i would use a captube and try until i got the right lenght. i would not take a cpev because i would be afraid of leak issues.
    Good solution.
    German Phase Change Builder - Drop me a PM!

  14. #64
    Xtreme Addict
    Join Date
    May 2005
    Location
    Nova Scotia,Canada
    Posts
    1,004
    How are you running this thing? Houses don't come wired for 400v and you'll only see 3phase power in commerical buildings.
    My Rig:

    Q6600 2.4Ghz@2.9Ghz Custom Liquid Cooling
    ATI X1950XTX 512mb DDR4
    MSI 975X Platinum PowerUp Edition
    2gb Kingston Hyper-X DDR2 667
    Sound Blaster Audigy2
    2 IDE HDD, 2 SATA HDD
    LG DL16XDVD Writer,52X CDROM
    OCZ 520Watt PSU 33Amp +12v
    Thermaltake Xaser III case
    Logitech Z560 4.1 400watt Surround Sound

    3Dmark03-21112
    3Dmark05-12154
    3Dmark06-8054

  15. #65
    Xtreme Member
    Join Date
    Nov 2007
    Posts
    107
    we are in Germany we can have in our houses 63a 3phase 400v
    august have 16a 400v 3phase
    august learns Electrician ...
    little German

  16. #66
    I am Xtreme
    Join Date
    Mar 2005
    Posts
    4,849
    Quote Originally Posted by _HL4E_HalfLife_ View Post
    How are you running this thing? Houses don't come wired for 400v and you'll only see 3phase power in commerical buildings.
    You can convert single phase power to 3 phase by making a rotary phase converter out of a 3 phase motor.( You can also boost the power to 460v 3 phase )if needed by use of a transformer. Builing one is simple Depending on HP of load and number of motors run you may also have to add a few capicitors to have a balanced 3 phase load..........
    The Laws of Thermodynamics say:

    Zeroth Law: "You must play the game."
    First Law: "You can't win."
    Second Law: "You can't break even."
    Third Law: "You can't quit the game."

    Do you wanna Play Thermodynamics ???????? I forgot "you must"

  17. #67
    Xtreme Enthusiast
    Join Date
    Aug 2006
    Location
    Stockholm, Sweden
    Posts
    701
    _HL4E_HalfLife_:
    in europe almost everyone has 3phase who's living in a detached house.

    i got 3phase 400v 63amps for example.. old house had 3phase 400v 25amps..

    most people has 3phase comming in the house but it's rare people use 3phase for anything else then sauna and kitchen oven..

    [edit]
    mr push the wrong botton is here.. 63amps not 64.
    Last edited by tim-; 03-11-2008 at 04:53 PM.

  18. #68
    Xtreme Member
    Join Date
    Jul 2005
    Location
    Austria
    Posts
    428
    Quote Originally Posted by wdrzal View Post
    You can convert single phase power to 3 phase by making a rotary phase converter out of a 3 phase motor.( You can also boost the power to 460v 3 phase )if needed by use of a transformer. Builing one is simple Depending on HP of load and number of motors run you may also have to add a few capicitors to have a balanced 3 phase load..........
    not necesary to do that. at least in austria and germany all the 3 phases from the generator come directly to your house. you have 230V from phase to neutral and 400V from one phase to another. so you can have 3 phase power in every building, it just depends if you installed the 3 phases in the house. (sorry, i did not formulate the text good, but its a bit hard for me )

    Quote Originally Posted by tim- View Post
    _HL4E_HalfLife_:
    in europe almost everyone has 3phase who's living in a detached house.

    i got 3phase 400v 64amps for example.. old house had 3phase 400v 25amps..

    most people has 3phase comming in the house but it's rare people use 3phase for anything else then sauna and kitchen oven..
    exactly

  19. #69
    Xtreme Member
    Join Date
    Nov 2007
    Posts
    107
    Quote Originally Posted by tim- View Post
    _HL4E_HalfLife_:
    in europe almost everyone has 3phase who's living in a detached house.

    i got 3phase 400v 64amps for example.. old house had 3phase 400v 25amps..

    most people has 3phase comming in the house but it's rare people use 3phase for anything else then sauna and kitchen oven..
    A littele mistak its 63a not 64, 64 is Colloquially august lernd me that
    little German

  20. #70
    Registered User
    Join Date
    Oct 2007
    Posts
    28
    WOW...you are crazy man!
    i'ts the biggest cascade, and probabily the best i've ever seen before...about the temps, i've no words.... -160° degrees, AMAZING!

  21. #71
    Xtreme Cruncher
    Join Date
    May 2007
    Location
    In a hell hole called Sac
    Posts
    1,754
    w O W
    Quote Originally Posted by [XC] Kayin View Post
    Should the RIAA ever target me, I will immediately forfeit US citizenship and move back to reservation, which has no extradition policy and would probably tell Whitey to get bent or we'll scalp you and take your women...
    Free Omastar!

    [SIGPIC][/SIGPIC]

  22. #72
    Xtreme Addict
    Join Date
    May 2005
    Location
    Nova Scotia,Canada
    Posts
    1,004
    Here in Nova Scotia homes have 120/240v 1Phase 60Hz power.
    My Rig:

    Q6600 2.4Ghz@2.9Ghz Custom Liquid Cooling
    ATI X1950XTX 512mb DDR4
    MSI 975X Platinum PowerUp Edition
    2gb Kingston Hyper-X DDR2 667
    Sound Blaster Audigy2
    2 IDE HDD, 2 SATA HDD
    LG DL16XDVD Writer,52X CDROM
    OCZ 520Watt PSU 33Amp +12v
    Thermaltake Xaser III case
    Logitech Z560 4.1 400watt Surround Sound

    3Dmark03-21112
    3Dmark05-12154
    3Dmark06-8054

  23. #73
    Registered User
    Join Date
    Oct 2006
    Location
    Germany
    Posts
    73
    hehe i cold never live without 3 phase power
    Such problems we don`t have in Germany/ Europe. But you in America/ Canada have 60Hz, thats more power with same compressor. Not bad, too.

  24. #74
    Xtreme Member
    Join Date
    Dec 2005
    Location
    Rennes (france)
    Posts
    443
    In france 95% people have only 240~ 1ph in their house even if 3 phases are accessible

  25. #75
    Xtreme Addict
    Join Date
    May 2005
    Location
    POLAND/Cracow
    Posts
    1,246
    Quote Originally Posted by august123 View Post
    hehe i cold never live without 3 phase power
    Such problems we don`t have in Germany/ Europe. But you in America/ Canada have 60Hz, thats more power with same compressor. Not bad, too.
    AWESOME project august
    keep update us
    btw you can buy danfoss frequency changer (dunno what shold be exact name of it)
    but I heard you can overclock copressor to 90Hz

    Quote Originally Posted by Clemmaster View Post
    In france 95% people have only 240~ 1ph in their house even if 3 phases are accessible
    OMG
    here almost ppl in normal houses has 3 phase

    on flats only 220V of course but if someone live in 40-50 old flat he can found 3 phase plug (in kitchen) too lol
    Last edited by Duniek; 03-14-2008 at 01:42 PM.

Page 3 of 7 FirstFirst 123456 ... LastLast

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •