Yeah 400ml, I only added 300ml, I was even considering not adding any at oil, since there should be more than enough in the compressor. Mainly because the system this compressor would normally be installed in is so much bigger than the system I have it running in. What ya think Nol?
Hey tim, that’s cool, I guess ya been playing dual cap lines with chillers maybe with some insider information?
Lower pressure istn so bad as long as the pressure is enough to condense the refrigerant at its liquid line temp. Ie I have seen 150psi when using r290 with cascades with a big condenser and a cold liquid line even at loadBut then in a 42c warm case that pressure rises to 200psi running for several hours at a time.
I think of dual caplines as a bigger ID capillary line. My main goal is to deliver more liquid refrigerant to the HX and run a lower first stage Low side pressure with colder temps. With my last cascade I had the second stages liquid line leaving the HX at -35c feeding the cpu head.
I charged the cascade so first turn on 1st stage was down to temp in 3mins and second stage at -100c 2 mins later. So first stage doesn run that cold, but has lots of capacity and is flooded well. Result it only takes the cascade 5mins for total pull down to -100c. Havnt seen another cascade pull down that fast yet
Im not really shore what will happen, but I imagine the lower discharge is as a result of less refrigerant backing up in the condenser. As you said though I hope the refrigerant condenses properly, time will tell.





But then in a 42c warm case that pressure rises to 200psi running for several hours at a time.
Lower discharge is usually good thing as long as you have enough to condense in different conditions through cap tubing designated 