    Hi

    After first bypass tests I can say it's working just as I've thought - discharge is lower when bypass is open, suction is higher - it can't be another , so I trully don't know Patrick, from where You take this idea that discharge will be higher with valve opened ? I was able to hold sth like -91C@260W load with bypass very little opened (with more opened I seen -76C), while when bypass was off I have had sth like -97C@260W . Nevermind, that're just initial tests .

    Regards
    Peter

  3. #28
    -100c Club
    Join Date
    Jun 2005
    Location
    Slovenia, Europe
    Posts
    2,283
    Quote Originally Posted by piotres View Post
    Hi

    After first bypass tests I can say it's working just as I've thought - discharge is lower when bypass is open, suction is higher
    That's how it supposed to be. When you open bypass from high side to low side you basically lower the compression ratio. On old sharp's cascade me & moonman currently use (until i charge mine with R1150a) with bypass (oil return basically) fully opened you get around -65°C (~ 7barg HP), with bypass closed around -105°C (~ 14barg HP) - all measurements on cpu idling in Windows.

    Good work Peter, love your cascade builds!

  4. #29
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Germany
    Posts
    401
    what is lower? pressure or temperature?
    i wrote a few postings ago: "the hotgas bypass will increase discharge and compressor temp"

    and i would say, that this is the "normal" reaktion of the circuit.
    you increase the suction gas temperature and after compressing it, it should be hotter, than compressing a gas that has a suction gas temperature of -50°C.

    our discharge copper pipe was so hot, that you couldnīt realy touch it.
    i donīt know the reason for that, but we used a hot gas bypass before desuperheater. and the regulation of the bypass was controlled by the sps that fully opens the mgv (which has a inner diameter of 3mm) so a lot of hotgas will flow through it at once.

    you have only opened the valve a little bit and you are using gas at room temperature. so this amount of gas is also cooled by the suctin gas. so all at all your suction temp doesnīt rise a lot.

  5. #30
    -100c Club Member
    Join Date
    Mar 2005
    Location
    Poland
    Posts
    1,290
    Quote Originally Posted by Patrickclouds View Post
    what is lower? pressure or temperature?
    i wrote a few postings ago: "the hotgas bypass will increase discharge and compressor temp"

    and i would say, that this is the "normal" reaktion of the circuit.
    you increase the suction gas temperature and after compressing it, it should be hotter, than compressing a gas that has a suction gas temperature of -50°C.

    our discharge copper pipe was so hot, that you couldnīt realy touch it.
    i donīt know the reason for that, but we used a hot gas bypass before desuperheater. and the regulation of the bypass was controlled by the sps that fully opens the mgv (which has a inner diameter of 3mm) so a lot of hotgas will flow through it at once.

    you have only opened the valve a little bit and you are using gas at room temperature. so this amount of gas is also cooled by the suctin gas. so all at all your suction temp doesnīt rise a lot.
    ok sorry I didn't read well I thought You had been saying about discharge pressure .

  6. #31
    -100c Club
    Join Date
    Jun 2005
    Location
    Slovenia, Europe
    Posts
    2,283
    Patrick -> correction here!
    i wrote a few postings ago: "the hotgas bypass will increase discharge and compressor temp"
    It will increase suction temp but it will lower discharge temperature hence lower HP. You should be using desuperheated gas after aux condensor (dshx).

    At least from my experiences.
    Last edited by tiborrr; 11-27-2008 at 02:51 PM.

  7. #32
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Germany
    Posts
    401
    Quote Originally Posted by tiborrr View Post
    Patrick -> correction here!

    It will increase suction temp but it will lower discharge temperature hence lower HP. You should be using desuperheated gas after aux condensor (dshx).

    At least from my experiences.
    yeah you are absolutly right

    we were too lazy to braze a new shrader into the filled unit.
    so we used the existing for our test. if you take a look at the picture on the previous page you can see, that discharge shrader is before desuperheater and that we used the service port on compressor. so there is no chance that the hot gas from the bypass is cooled by suction gas.

  8. #33
    -100c Club Member
    Join Date
    Mar 2005
    Location
    Poland
    Posts
    1,290
    Hello

    Long time no update here, because I met leak problem with this cascade (also I've had problems with 2nd stage compressor and now it's swaped for bit bigger one - Sanyo C-RN112H5A which is sth around 12000-13000 BTU).

    "First time" cascade was ready in the end of December 2008, I made some load tests and left if stay in mine garage for leak testing (cascade have pressure gauges so static pressure can be checked). After some weeks of testing (test in the begining of February 2009) I notticed sth like 1 bara static pressure drop and problems with load holding. So I decided - that must be tiny leak somewhere and I MUST find it . That seems to be very hard work, becuase before put on insulation I test every connection at least 2 times with leak testing spray and all was fine . So again case umounting, removing insulation, ehhh .Again I made test with spray, I remember mine previous problems with leaking straight part of captube, so I sprayed EVERY pipe even staight parts with leak tester - again all seems to be OK :-O .
    I decide to umount every part of cascade's 2nd stage and test it in water,under pressure. And I found it ! - leak was again on straight part of captube, after bypass valve, only test under 20+ bara in water bath show it, I test again leaked place with spray and spray didn't show even the smallest bubbles there even (I tried few sprays - Wigam, Wurth, Tectane) !

    One is sure - I'll never buy those captubes in future -that's second time when I have leak of straight part of captube (another one was in blue cascade) . Fuxxx crap I just want to say about those captubes .

    So I fixed leaked place, changed both driers on 2nd stage, cover pipes again with black pipe, make new insulation for 2nd stage and finally mount case .

    Cascade is already packed .

    Finaly -96*C @ 260W load after 1 hour test but warm but seems like it's the best which I can take from this setup . I tried 320+ cm of 0.9mm captube, and finaly it's 280cm of 0.9mm and same result .

    Some photos from next part of work :






    Making electric instalation (before leak find) .




    Power consumtion of whole unit (when it loaded with 260W) .







    And that's hell captube .






    I use almost all pipes new in 2nd stage ...




    so painting pipes again was a must .



    Final unloaded temperature is around -106*C .



    On 260W after more than 1h of test .




    1st stage loaded by 260W load on evaporator .































    Both units are going in one pack










    I prefer to make 100% "idiot-proof" packing .



    And here is 100% packed .


    Best Regards,
    Peter
    Last edited by piotres; 02-28-2009 at 02:25 PM.

  9. #34
    Admin
    Join Date
    Mar 2003
    Location
    North Texas
    Posts
    5,551
    Bravo mi amigo
    UNDER THE ICE .com
    Phase Change Cooling

    is the remedy

  10. #35
    Xtreme Enthusiast
    Join Date
    Jun 2006
    Location
    Near CeBIT-City Hannover
    Posts
    650
    Very good packing job!
    Quote Originally Posted by Xeon th MG Pony View Post
    ....and avoid being a total venting loser!

  11. #36
    Xtreme Member
    Join Date
    Jul 2006
    Location
    France
    Posts
    107
    Yes you had got the same leak's problem with my cascade

  12. #37
    Registered User
    Join Date
    Mar 2008
    Location
    Sweden
    Posts
    32
    I really need more money, I'd eat noodles for a year to afford this. XD

    Great build.

  13. #38
    -100c Club Member
    Join Date
    Mar 2005
    Location
    Poland
    Posts
    1,290
    Quote Originally Posted by 0cool View Post
    Yes you had got the same leak's problem with my cascade
    You're right 0cool . But with Your unit I have had more luck, because there spray leak detector show the leak, and here only water show the truth . That's why that was really hard way to find this .

    Thanks Guys for all comments .

    During incoming week I'll upload movie on Youtube showing bypass work . I'll paste link here .

    Regards
    Peter

  14. #39
    Xtreme Cruncher
    Join Date
    Dec 2005
    Location
    L.A. ( Latin America)/ 4socket wannabe
    Posts
    2,756
    even though I dont understand the technical part of the refrigeration unit I must say yout unit is gorgeous and you packing in very PRO
    "Study hard my young friend"[/B].
    ---------------------------------------
    Woody: It's not a laser! It's a... [sighs in frustration]

  15. #40
    -100c Club
    Join Date
    Jun 2005
    Location
    Slovenia, Europe
    Posts
    2,283
    One of the best jobs I have ever seen lately - both cascade & single-stage aswell as packaging look very industrial like. Top notch!

    P.S.: Who is the manufacturer of this cap tube? Is it a 2mm one? What batch (serial numbers) if you still have them?

  16. #41
    Xtreme Enthusiast
    Join Date
    Jun 2008
    Location
    Chandler, AZ
    Posts
    573
    Holy Smokes great!

    Customer requested shoes too? lol.
    #1
    Pentium D805 @ 3.4Ghz on GA-945P-S3
    2Gb OCZ Gold 800 with XP Professional SP3
    Ati X1800XT
    550W Antec TruPower in Antec Sonata II
    #2
    Core 2 Quad Q9550 on GA-EP45-UD3P
    4Gb Corsair Dominator 1066 with Vista Ultimate SP1
    Asus 4850 TOP
    750W PC Power & Cooling in ????


    There is not enough electrical oulets in my room.
    Best TF2 Quote:
    "tomtom92 : wtf the enemy has a base IN our base"

  17. #42
    -100c Club Member
    Join Date
    Mar 2005
    Location
    Poland
    Posts
    1,290
    Quote Originally Posted by tiborrr View Post
    One of the best jobs I have ever seen lately - both cascade & single-stage aswell as packaging look very industrial like. Top notch!

    P.S.: Who is the manufacturer of this cap tube? Is it a 2mm one? What batch (serial numbers) if you still have them?
    Thanks

    That captube was "no-name" (that was 1.5m captube with 1/4 nuts on both sides , I don't know what diam. it have but looks like much over 2.0mm) I bet it's chineese one .

  18. #43
    -100c Club Member
    Join Date
    Mar 2005
    Location
    Poland
    Posts
    1,290
    Hi

    MOVIE SHOWING BYPASS IN ACTION :

    http://www.youtube.com/watch?v=NMo8BakJORk

    Sorry for not working photos, I hope that Lycos server will be working again soon if not ....I have a problem .

    Regards
    Peter

  19. #44
    Registered User
    Join Date
    Feb 2008
    Posts
    40
    It has a fast reaction, really nice job there

    You didn't "open" the valve fully i presume?

  20. #45
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    How much does it fully drop? Did it stop at -96 and how many whats were you loading?
    Amazing work!!!
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  21. #46
    -100c Club Member
    Join Date
    Mar 2005
    Location
    Poland
    Posts
    1,290
    Quote Originally Posted by sdumper View Post
    How much does it fully drop? Did it stop at -96 and how many whats were you loading?
    Amazing work!!!
    Sure, on movie it's very light open, once I open it more and I get around -70C, but valve still wasn't fully opened . I test cascade during load with 260W .

  22. #47
    -100c Club
    Join Date
    Jun 2005
    Location
    Slovenia, Europe
    Posts
    2,283
    Wanna see fast reaction? Old sharp's cascade with ball valve bypass (essentially an oil return valve).

    http://www.youtube.com/watch?v=0TURqnM3kLw