    Quote Originally Posted by Nyx
    I might be wrong. But from his last post, the designs are not far from what we have. I think it is the type of refrigerant he uses for his autocascades.which most of us could not have access to, or do not have enough knowledge on the purpose of it. For example R123 was used in most of his autoc but most of the autoc in XS do not use such refrigerant.Maybe because we do not know its properties enough.
    But still i would like to know how far his designs are from those in XS but i would be more interested to know the use of some of his unusual refrigerant like R123.

    im interested in direction of flow on the hxs.
    ie cc1 cc2 and coaxial hx
    ie evap bottom up with high stage entering top exit bottom.
    i cant confirm but it looks like one of the cc's flows high stage entering bottom??
    Last edited by kayl; 04-27-2006 at 04:22 AM.

  2. #127
    Phenom™
    Join Date
    Sep 2002
    Posts
    5,163
    Ummm, I'm not sure that everyone understands that this unit wasn't built by Cryo-tek (although he can and does build units of his own). This particular unit was built by Polycold and therefore the schematic would be under NDA. Here's a basic diagram of a 3 stage autocascade. If you can't figure it out, then you shouldn't be building an autocascade yourself


  3. #128
    Xtreme Enthusiast
    Join Date
    Jul 2004
    Location
    The Netherlands
    Posts
    985
    i always thought it was called a metering device,
    cuz i've never seen a captube expanding

    But the schematic looks reasonable, 4 metering devices, 4 evap+suction / liquidline HX, 3 phase seperators
    I'm just amazed that it actually works

  4. #129
    Xtreme Enthusiast
    Join Date
    Feb 2004
    Location
    Netherlands
    Posts
    757
    we need to find out what is happening with the argon, now it just doesn't make sense. The pressure/temperature just isn't the way it should be with argon. When we understand what is going on with the argon, we might be able to build cascades that will hold a load at -140*C or something. wish I had those gasses.

    btw cryo-tek, any idea what kind of oil is in the system? Since you got r14 in it succesfully and people here had oil issues between r14 and POE. Could you please answer a few of our questions?
    Last edited by Unknown_road; 04-25-2006 at 12:08 AM.

  5. #130
    Xtreme Enthusiast
    Join Date
    Jul 2004
    Location
    The Netherlands
    Posts
    985
    Quote Originally Posted by Unknown_road
    we need to find out what is happening with the argon, now it just doesn't make sense. The pressure/temperature just isn't the way it should be with argon.
    At that evap temp you should be having a pressure of about 45 bar!

  6. #131
    -100c Club Member
    Join Date
    Apr 2003
    Location
    Riverside, California
    Posts
    4,740
    Well have all gases except... R123... I just can't bring myself to buy 100lbs of it... anyone in US care to split (with proper license?)? It's pretty cheap per pound but only thing I see is 100lbs and 200lbs drums... bleh.
    I do have r22, R23, R116, obviously nitrogen and argon handy... :P Just need to learn exact purposes and what happens to really get to it.
    [SIGPIC]http://www.vapoli.com/Images/Forum/vapoli.jpg[/SIGPIC]

    Single Stage Work Logs

    Quote Originally Posted by killermiller View Post
    Those ccb's will die if you look at them wrong.

    heatware: jinu117

  7. #132
    Phenom™
    Join Date
    Sep 2002
    Posts
    5,163
    Quote Originally Posted by Unknown_road
    we need to find out what is happening with the argon, now it just doesn't make sense. The pressure/temperature just isn't the way it should be with argon. When we understand what is going on with the argon, we might be able to build cascades that will hold a load at -140*C or something. wish I had those gasses.
    Argon helps lower the partial pressure of the r14 allowing it to evaporate @ lower temps. However, one of the drawbacks of adding argon is that it will increase discharge pressures. Argon is cheap and readily available - as you probably know already, it's a sheilding gas.......*How was that Cryo-tek? I'm sounding smarter already *

    EDIT - Forgot to add: The argon itself doesn't condense....
    Last edited by s7e9h3n; 04-25-2006 at 12:14 AM.

  8. #133
    Phenom™
    Join Date
    Sep 2002
    Posts
    5,163
    Quote Originally Posted by Jack
    At that evap temp you should be having a pressure of about 45 bar!
    Evap temp @ -162C = 180psi discharge

  9. #134
    Xtreme Enthusiast
    Join Date
    Feb 2004
    Location
    Netherlands
    Posts
    757
    Quote Originally Posted by s7e9h3n
    Argon helps lower the partial pressure of the r14 allowing it to evaporate @ lower temps. However, one of the drawbacks of adding argon is that it will increase discharge pressures. Argon is cheap and readily available - as you probably know already, it's a sheilding gas.......*How was that Cryo-tek? I'm sounding smarter already *

    EDIT - Forgot to add: The argon itself doesn't condense....
    Sorry but I don't buy that, partitial pressure doesn't reach anything in the range of -140 with r14. just look at a PT-chart of it.

  10. #135
    Phenom™
    Join Date
    Sep 2002
    Posts
    5,163
    Quote Originally Posted by Unknown_road
    Sorry but I don't buy that, partitial pressure doesn't reach anything in the range of -140 with r14. just look at a PT-chart of it.
    Ok...well, I'm just repeating what cryo-tek's told me. What is your theory to what is happening here? It would be interesting to hear

  11. #136
    Gigabyte Champion USA
    Join Date
    Jan 2005
    Posts
    507
    Wow! I hate this smilie, but this is the thread it was put here for


  12. #137
    -100C Club Member
    Join Date
    Feb 2004
    Location
    australia
    Posts
    3,766
    Quote Originally Posted by s7e9h3n
    Evap temp @ -162C = 180psi discharge
    that is just amazing

  13. #138
    -100c Club Member
    Join Date
    Apr 2003
    Location
    Riverside, California
    Posts
    4,740
    Lemme think clearly for a moment at 3:36 AM in the morning.... (had a customer unit i had to finish... he was here )
    So...
    Argon takes volume in chamber... but doesn't condense or evaporates...
    it certainly doesn't condense anywhere in loop, and is non condensable.
    Obviously high side pressure do go up with this. With the artificially developed high side pressure, we see higher pressure differential than normally would have seen considering we still have same amount of gas without argon. All the evaporating happens same thus as in amount of refrigerant but the differential aids in creating more flow of liquid...or I think it should within reason. But as restriction didn't really change -captubing- we have condition in evap which refrigerant can expand better (well argon doesn't really expand unlike refrigerant obviously around temp we are dealing with)...? better temp is always lower suction pressure after all. so it must also translate the other way in this case... (gotta love how gas laws always goes hand in hand).
    I think I am rambling off...
    Now care to explain why nitrogen (other than it's boiling and melting point) is not a good candidate for this reason? Or is it...?
    [SIGPIC]http://www.vapoli.com/Images/Forum/vapoli.jpg[/SIGPIC]

    Single Stage Work Logs

    Quote Originally Posted by killermiller View Post
    Those ccb's will die if you look at them wrong.

    heatware: jinu117

  14. #139
    I am Xtreme
    Join Date
    Mar 2005
    Posts
    4,849
    better temp is always lower suction pressure after all.

    wrong.
    The Laws of Thermodynamics say:

    Zeroth Law: "You must play the game."
    First Law: "You can't win."
    Second Law: "You can't break even."
    Third Law: "You can't quit the game."

    Do you wanna Play Thermodynamics ???????? I forgot "you must"

  15. #140
    -100c Club Member
    Join Date
    Apr 2003
    Location
    Riverside, California
    Posts
    4,740
    Quote Originally Posted by wdrzal
    better temp is always lower suction pressure after all.

    wrong.
    Yeah... hmmm
    I just thought about it and, realized... what is SUCTION pressure in this case... lol.
    after what stage? I think that 20psi is combined suction pressure right before or inside compressor.... so it might be running well into vacuum for evap stage.
    [SIGPIC]http://www.vapoli.com/Images/Forum/vapoli.jpg[/SIGPIC]

    Single Stage Work Logs

    Quote Originally Posted by killermiller View Post
    Those ccb's will die if you look at them wrong.

    heatware: jinu117

  16. #141
    Xtreme Enthusiast
    Join Date
    Oct 2004
    Location
    Athens,Hellas
    Posts
    810
    Quote Originally Posted by s7e9h3n
    Ummm, I'm not sure that everyone understands that this unit wasn't built by Cryo-tek (although he can and does build units of his own). This particular unit was built by Polycold and therefore the schematic would be under NDA. Here's a basic diagram of a 3 stage autocascade. If you can't figure it out, then you shouldn't be building an autocascade yourself

    thats a nice diagram, anyone wanna trial and error captube length on such a system??
    if this is your first night in xtremesystems,
    you have to overclock.

  17. #142
    Xtreme Enthusiast
    Join Date
    Feb 2004
    Location
    Netherlands
    Posts
    757
    Quote Originally Posted by jinu117
    Yeah... hmmm
    I just thought about it and, realized... what is SUCTION pressure in this case... lol.
    after what stage? I think that 20psi is combined suction pressure right before or inside compressor.... so it might be running well into vacuum for evap stage.
    NO! suction pressure is almost the same everywhere as long as you don't have restrictions along the way.

    cryo-tek: trow some methane in the system!
    Last edited by Unknown_road; 04-25-2006 at 05:49 AM.

  18. #143
    Xtreme Member
    Join Date
    Mar 2005
    Posts
    325
    How much argon would be required to drive the pressures up to 700 PSI at -120C which argon could turn partly liquid. If the charge is correct i believe that it will not drive the pressure up astronomically and might still help in maintaining the ultra low temps. And there is still an expansion tank, it could help slowly release the extra mix into the system if a captube is used. so this could also be a crucial point.
    Last edited by Nyx; 04-25-2006 at 06:11 AM.

  19. #144
    Xtreme Enthusiast
    Join Date
    Feb 2004
    Location
    Netherlands
    Posts
    757
    you want the system to work at 700psi??

  20. #145
    -150c Club Member
    Join Date
    Apr 2006
    Posts
    94
    Quote Originally Posted by jinu117
    Well have all gases except... R123... I just can't bring myself to buy 100lbs of it... anyone in US care to split (with proper license?)? It's pretty cheap per pound but only thing I see is 100lbs and 200lbs drums... bleh.
    I do have r22, R23, R116, obviously nitrogen and argon handy... :P Just need to learn exact purposes and what happens to really get to it.
    No 123? try 11 or 114

  21. #146
    Xtreme Member
    Join Date
    Mar 2005
    Location
    Universe #1 --> Earth --> Europe --> Austria --> 120km NW of Vienna :D
    Posts
    249
    Well ... first of all ... cryo-tek: Your units go LIKE HELL!
    I'm a fan of autocascades .... but your's beat everything I knew til now!
    REEAALLLLLLY NICE!

    Short question:
    How long does this nice unit need to come down to ... let's say .... -100°C?

    regards
    404Power

    PS: PLZ check your PMs! (I only wrote one ... not 3 or so! )

  22. #147
    Xtreme Member
    Join Date
    Mar 2005
    Posts
    325
    lol cyro all of us want to know how does the argon work in your system without having sky rocket pressures. pls explain.

  23. #148
    ln2nl
    Join Date
    Jun 2004
    Location
    The Netherlands
    Posts
    1,659
    Let the guy dont get 1000 pm's in an hour guys like stephen said... this will work not in our favor!
    *EDITed by IFMU*
    Signature Removed by XS Staff for not following XS Policies

    Forum Policies

  24. #149
    -150c Club Member
    Join Date
    Apr 2006
    Posts
    94
    Quote Originally Posted by Unknown_road
    Sorry but I don't buy that, partitial pressure doesn't reach anything in the range of -140 with r14. just look at a PT-chart of it.
    I need to get some work done but here is a quick bit. These are ROUGH ROUND NUMBERS !! Please don’t beat me up over a small % of error.

    Argon works best in the three stage units. (3 seps, 3 CCs)

    Two or is this three theories on the argon:

    1) Argon lowers the partial pressure of the R-14 in the evaporator allowing it to evaporate at lower temp.
    Evap pressure: 25psia (10.3 psig) R-14 Evap temp = -120c.
    Add the argon: 50% by pressure.
    Evap pressure: 25psia = 12.5 psia R-14 and 12.5 psia argon. Evap temp = -130c. (see your PT chart) More argon = lower temps.

    2) Argon dissolves into the liquid R-14 and lowers its evaporating temperature. (i.e. Glycol and water).
    3) All of the above.

    You guys are keeping me awake at night. CAFFINE !! I need a another Dew

  25. #150
    -150c Club Member
    Join Date
    Apr 2006
    Posts
    94
    I’m trying to answer questions and work for a living, this was in a PM so I’m posting for all to see.
    #1 behavior of r123:

    The R-123 condenses easily in the condenser and will dump large amounts of heat. The R-123 also helps with oil management in the #1 Phase Separator and compressor cooling.