MMM
Results 1 to 25 of 29

Thread: Building my first Single Stage

Threaded View

  1. #18
    Xtreme Member
    Join Date
    Aug 2002
    Location
    Washington
    Posts
    365
    Oh ok that's good you pulled a vacuum, I was just concerned there may be air in the system. After I vac my system I always close the manifold valves (low and high side valves) then disconnect the hose from my vac pump then connect it to my refrigerant tank, open my tank then crack open the line to the manifold/gauges to purge any air in the line set and tighten it back up. That makes sure there is no air in my line set.

    I was talking about your condenser, the piping direction is wrong for a condensor, it's an evaporator HX. As for subcooling it's good to wrap the capillary tube around the suction line. Even better is to solder it to the suction line somewhat close to the evap outlet.
    Last edited by aenigma; 07-09-2019 at 03:20 AM.

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •