When is a Receiver needed for a cascade and where in the loop is it placed?
When is a Receiver needed for a cascade and where in the loop is it placed?
Never empower an idiot with a response....
http://en.wikipedia.org/wiki/Troll_%28Internet%29
Seller/Buyer Reputation:
Heatware: http://www.heatware.com/eval.php?id=50905
Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
iTrader: http://www.blazingpc.com/forum/itrader.php?u=28
In a cascade the only stage a receiver would be used in is the first stage, and you put the receiver after the condensor like in any single stage.
The only time the receiver is used in a higher stage is when you plan an explosion.
Good point, marru. One should use recieved only on the high stage (by high stage I mean high temperature stage -> 1st stage of the cascade), e.g. before the metering device (TXV, AEV = CPEV). Cap tube systems does not require liquid reciever.
It's also not needed if you use large enough condenser and a properly sized / oriented tubing.
EK Water Blocks R&D
ekwb.com
Hobby: Rotary SS bench unit (LPG/R-507) | -75°C Auto-cascade (R-600/R-290/R-744) | Plate HX water chiller (1kW cooling power) | My 2nd cascade MP14FB R-507/R-1150 | Mini cascade R-507/R-1150 | GPU single-stage | Mach I restoration mod -> -38°C @ 230W
Milestones: 7.12GHz P4 | 6.84GHz K10.5 | 6.45GHz Ci5 | 3.31GHz K7
3DMark2001SE -> Favourite Game!
#1
Pentium D805 @ 3.4Ghz on GA-945P-S3
2Gb OCZ Gold 800 with XP Professional SP3
Ati X1800XT
550W Antec TruPower in Antec Sonata II
#2
Core 2 Quad Q9550 on GA-EP45-UD3P
4Gb Corsair Dominator 1066 with Vista Ultimate SP1
Asus 4850 TOP
750W PC Power & Cooling in ????
There is not enough electrical oulets in my room.
Best TF2 Quote:
"tomtom92 : wtf the enemy has a base IN our base"
but this is not called receiver.
i think he means an expansion tank
Cool so I shouldnt be concerned with adding a seperate reciever...for my 2 stage
Never empower an idiot with a response....
http://en.wikipedia.org/wiki/Troll_%28Internet%29
Seller/Buyer Reputation:
Heatware: http://www.heatware.com/eval.php?id=50905
Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
iTrader: http://www.blazingpc.com/forum/itrader.php?u=28
I meant upper stage (eg. 2nd, 3rd stage) and i was ironic .
Consider the situation when you would charge a second stage up to the point of filling up or partially filling up a liquid receiver (which could only be done while cascade is running btw). At this point when you turn off the cascade the low boiling refrigerant would warm up, pass the critical temperature point and go well beyond the 100bar pressure.
Bada Bing Bada Bang
Last edited by marru; 06-29-2009 at 10:53 AM.
sd imo you dont need one evocade dont use one and when i did it made no diffrence to the way it ran idle and load
hey paul what size exspantion tank you got ?
also i would of thougth if it ever got to 300psi static what ever the ambent temp i say it was over chargerd
with a 2l exspntion tank and 26c ambent i get a 175psig static and 175psig running pressure
nm you edited
was gona say yes if you had like 3kg of r1150 in the system :0
I LOVE LAMP!
I dont see an oil return on this does it not trap oil?
Last edited by sdumper; 06-29-2009 at 03:40 PM.
Never empower an idiot with a response....
http://en.wikipedia.org/wiki/Troll_%28Internet%29
Seller/Buyer Reputation:
Heatware: http://www.heatware.com/eval.php?id=50905
Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
iTrader: http://www.blazingpc.com/forum/itrader.php?u=28
If you're going to use it as an expansion tank then block of one side and run a cap tube to the other from the suction side of your compressor, when the compressor is switched off it will drain some of the refrigerant into the expansion tank slowly, when you switch the compressor on it will draw the refrigerant slowly back into the loop.
In this picture you can see two rotolock valves on each expansion tank and two hennery shut off valves in line from the compressor, this will allow me to shut and open different valves which will allow me to recover most of the refrigerant into the expansion tanks if any work is need at all like adjusting cap tubes ECT.
Last edited by sdumper; 06-29-2009 at 12:38 PM.
Never empower an idiot with a response....
http://en.wikipedia.org/wiki/Troll_%28Internet%29
Seller/Buyer Reputation:
Heatware: http://www.heatware.com/eval.php?id=50905
Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
iTrader: http://www.blazingpc.com/forum/itrader.php?u=28
The receiver let's the liquid and gas separate and the liquid drops to the bottom of the receiver. The liquid is then picked up and fed to the expansion valve. An expansion valve works at it's maximum efficiency when fed liquid only with no gas bubbles.
Cap tube system does not use receiver because you want some gas moving through the cap tube with the liquid
Now that's a cascade!!!
I don't agree with this. At the entrance of the capillary tube the refrigerant will be a sub-cooled liquid, the degree of sub-cooling depending on how the system was built.Cap tube system does not use receiver because you want some gas moving through the cap tube with the liquid
The pressure drop experienced by the refrigerant along the length of the capillary tube will cause an ever increasing percentage of refrigerant to be in gas phase, but at the entrance to the capillary tube the refrigerant will be pure liquid.
The reason for usually not using a receiver in a capillary tube system is more to do with the dynamics (for lack of a better word) of the system with regards to load -> idle transitions.
Essentially, a capillary tube system with no receiver is able to better adapt the refrigerant flow rate to the load applied to the evaporator.
Tom
"What will become of us, will we evolve"
I was under the impression that a small amount of gas would help let the system adjust to load. That's why I said that.
No doubt Tom knows the dynamics much better than myself. Thank you Tom
Imagine you have a capillary tube single stage running on a processor, the processor is idling at 100W
The single stage is running well - the evaporator exit superheat is a few degrees and at the filter drier you have a few degrees of sub-cooling.
Because of the low superheat you have a large mass of dense gaseous refrigerant in the suction line and because of the small amount of sub-cooling, only the last few inches of the condenser is filled with liquid.
The processor now goes into load with the processor putting out 250W.
The added evaporator heat load causes the suction superheat to raise dramatically, the dense gas occupying the suction line is replaced by highly superheated (and much less dense) suction gas. The mass of refrigerant in the suction line is reduced, with the displaced mass of refrigerant being moved into the condenser.
This added refrigerant condenses and fills up a much larger proportion of the condensers volume than was previously occupied by liquid. This process has reduced the condensers effective size, so in the long term the discharge pressure rises
Capillary tube flow rate is highly dependant on the pressure drop across it and the increased discharge pressure increases the mass flow though the capillary tube.
The increased flow rate is much better suited to handling the evaporator load and subsequently the suction superheat falls and the transition reaches a steady state.
If you had a receiver, you wouldn't have anywhere near as much increase in discharge pressure.
I was trying to avoid typing this as I’m tired but I realised that my previous post could have been taken as arrogant hence the explanation.
Tom
"What will become of us, will we evolve"
Thanks for the assist...Receiver added
I have never used a Reciever before and certainly not this type but I brazed the long copper pipe to my filter drier and the short exit pipe to my copper tube running to my site glass and then TXV.
Vacuuming right now and will charge at 9:00pm EST if all goes well.
Im assuming I dont need to adjust this thing and that it wont trap oil since fluid and not gas will be exiting...
Never empower an idiot with a response....
http://en.wikipedia.org/wiki/Troll_%28Internet%29
Seller/Buyer Reputation:
Heatware: http://www.heatware.com/eval.php?id=50905
Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
iTrader: http://www.blazingpc.com/forum/itrader.php?u=28
Evidently it has a valve of sorts on the bottom of the outlet ... im loosening it now because it was not feeding any refrigerant at all...
Would have been nice to have some instructions on this thing...
--edit-- Yep that was it and it made a huge difference in my required running pressure...much lower now...
Last edited by sdumper; 06-29-2009 at 07:22 PM.
Never empower an idiot with a response....
http://en.wikipedia.org/wiki/Troll_%28Internet%29
Seller/Buyer Reputation:
Heatware: http://www.heatware.com/eval.php?id=50905
Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
iTrader: http://www.blazingpc.com/forum/itrader.php?u=28
You are missing one thing. When the evaporator experiences a bigger load, the suction pressure will increase as a result of the increased discharge pressure and of the flow rate. So under a higher load, you have a bigger flow rate through the suction side@a higher pressure and you actually have a higher mass of fluid in the suction line thus a lower liquid level in the condenser.
In my point of view the existence of a receiver in a single evaporator sistem would only be justified by the lack of condensing pressure control and a very big load variation on the evaporator. This is only the case for our sistems where we cant afford the on/off termostatic control over the compressor as you find in a commercial application.