    So in your opinion, propane to ethylene. Thats -42C to -104C. Or a 62C boiling point delta. Do you think a partial phase separator would be necesary? R600 to R170 is a 89C boiling point delta.
    I wish I could give you a definitive answer, but as you can imagine, it depends on a lot of different factors (eg; phase separator efficiency for one). Since I don't have ethylene or anything else with this same boiling point, I can't run a test. But you can
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  2. #452
    Diablo 3! Who's Excited?
    Join Date
    May 2005
    Location
    Boulder, Colorado
    Posts
    9,412
    Quote Originally Posted by n00b 0f l337 View Post
    So in your opinion, propane to ethylene. Thats -42C to -104C. Or a 62C boiling point delta. Do you think a partial phase separator would be necesary? R600 to R170 is a 89C boiling point delta.
    On a similar note, could you get away with strictly R290/R1150 or should you keep the R600 loop for compressor cooling and as a way to help purify the R1150 by having 2 loops to pull the R600/R290 components out of the mix?

    Basically R290 -> R1150 or R600/R290 -> R290/R1150 -> R1150.

    ninja-edit: Thinking about it, I'm betting the 2nd option would be better as that 1st mixture will boil somewhere close to propane, say -30C. Hopefully the 2nd mixture would boil around ethane's BP, and the final stage would be nearly pure R1150. I'm in the planning stages of my autocascade which is why I ask and I don't want to screw it up
    Last edited by [XC] gomeler; 04-13-2008 at 10:59 AM.

  3. #453
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Hahaha Michael ya should get ethylene, might be able to help you guys replace r14


    If you have a cooling question or concern feel free to contact me.

  4. #454
    Xtreme Member
    Join Date
    Dec 2005
    Location
    Rennes (france)
    Posts
    443
    What about blending 2 HC? Don't you think they will blend to form an azeotropic gas in the end? Some of you use blend on cascade (methan+propan), so why would it be different here?

    You're expecting to condense ethan or ethylen with respectively R600a or R290? Good luck

    Considering they won't blend (I'm not sure they won't...) :
    R170 is the hardest mid range second stage refrigerant (~-85°C @ 1bar like R23 and R13) to condense because of very high latent heat of vaporisation. A R600a compressor must have 65% greater displacement than needed with R12 to get the same capacity, so don't expect to remove the heat of R170 to condense it at decent pressures.

    That's worse with ethylen and propan

  5. #455
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    They will be blending, and theres also going to be saturation. And not even isobutane, we're talking about normal butane.


    If you have a cooling question or concern feel free to contact me.

  6. #456
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Quote Originally Posted by Clemmaster View Post
    You're expecting to condense ethan or ethylen with respectively R600a or R290? Good luck
    Considering they won't blend (I'm not sure they won't...) :
    R170 is the hardest mid range second stage refrigerant (~-85°C @ 1bar like R23 and R13) to condense because of very high latent heat of vaporisation. A R600a compressor must have 65% greater displacement than needed with R12 to get the same capacity, so don't expect to remove the heat of R170 to condense it at decent pressures.
    Actually I think I can condense it at reasonable pressures with only R-600 (43 suction/240 discharge):
    Quote Originally Posted by mytekcontrols View Post
    First Test Results (-102.6C @ 125 Watts)
    And with R-123+R-22 (49 suction/275 discharge):
    Quote Originally Posted by mytekcontrols View Post
    -101C @ 150 Watts Applied Load
    Quote Originally Posted by gomeler View Post
    On a similar note, could you get away with strictly R290/R1150 or should you keep the R600 loop for compressor cooling and as a way to help purify the R1150 by having 2 loops to pull the R600/R290 components out of the mix?
    I think it best to use both the R600 and the R290 for the reasons that you stated in the end.

    Edit: I'll be running my next test with R600 and R290.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  7. #457
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Oh cool made a r290 adaptor?


    If you have a cooling question or concern feel free to contact me.

  8. #458
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Oh cool made a r290 adaptor?
    Yes I did. Thanks for the idea

    Still waiting on my extra parts to arrive first, so I can implement the buffer valve feature. But soon.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  9. #459
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    No problem and not my idea, been used here for years


    If you have a cooling question or concern feel free to contact me.

  10. #460
    Xtreme Member
    Join Date
    Dec 2005
    Location
    Rennes (france)
    Posts
    443
    Quote Originally Posted by mytekcontrols View Post
    Actually I think I can condense it at reasonable pressures with only R-600 (43 suction/240 discharge):
    You're talking about condensing R170 with R600 right?

  11. #461
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Yes he is, butane will boil much lower then its normal BP as it absorbs and saturates with ethane.


    If you have a cooling question or concern feel free to contact me.

  12. #462
    Xtreme Member
    Join Date
    Dec 2005
    Location
    Rennes (france)
    Posts
    443
    How do you know where it will actually saturate?

    Ethane involve a very high condensing rejection so you must have a good displacement to carry such load on first stage...

  13. #463
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    It will saturate everywhere... Dunno what you mean by that? The auxillary condenser before the first phase separator will lower refrigerant temps and boost saturation as well.


    If you have a cooling question or concern feel free to contact me.

  14. #464
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Clemmaster, When I made the statement:
    Actually I think I can condense it at reasonable pressures with only R-600 (43 suction/240 discharge)
    I really meant to say "I know" instead of "I think". The reason I say this is, that I know beyond a shadow of a doubt, that the only way I could have obtained -100C or colder with a charge based on R-600, R-170, R-14 -and- with a 240 psig condensing pressure -while- evaporating into a 43 psig suction, would be by condensing at least the R-14, which would have minimally required condensing and evaporating the R-170.

    My questions to you are: Have you studied, or have been working with autocascades? Do you understand that an autocascade is not the same as a standard multi-compressor cascade, and that in an autocascade a mixture of refrigerants are fractionated out and used to cool successive stages? If not, then this may be the source of your dilemma about why I was able to condense R-170 (and R-14 which has a much lower boiling point), while using only one other refrigerant (R-600).

    One last question for you: Have you read through this entire thread? If not, then I would highly recommend that you do so, since much has been covered on the topic of autocascades and how we think they work.

    I'll be the first one to admit that there has been much theorizing on the subject, and I'm sure you'll find that some of the later posts will be in conflict with what had been thought to be fact in earlier ones. But overall I believe it has been a very productive effort, and hopefully is allowing others to have the knowledge to build their own autocascades, and have their own successes at condensing R-170, and/or R-1150, and/or R-14.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  15. #465
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Mytek if you need a rotary cascade as you were thinking from the r22 problem thread, send me an email I have a large inventory at the moment.


    If you have a cooling question or concern feel free to contact me.

  16. #466
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    I just read over my response to Clemmaster's questions, and although I didn't mean to come off as and over bearing know-it-to-all, I think it could possibly be perceived that way. My apologies go out if it felt this way to you as well Clemmaster

    Anyway the point I was really trying to make is, that there is a tremendous amount of information on autocascades already covered by this thread. So to keep from being redundant (by going over what has already been discussed), it is best to start at the beginning, and read it through to the end. That way we can try to keep this from getting into a 1000+ postings, which to say the least, gets a bit unwieldy.

    However, I am always happy to try and answer the questions, and try to do so as accurately as I can.

    Also... to this thread.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  17. #467
    Xtreme Member
    Join Date
    Dec 2005
    Location
    Rennes (france)
    Posts
    443
    Quote Originally Posted by mytekcontrols View Post
    Clemmaster, When I made the statement:

    I really meant to say "I know" instead of "I think". The reason I say this is, that I know beyond a shadow of a doubt, that the only way I could have obtained -100C or colder with a charge based on R-600, R-170, R-14 -and- with a 240 psig condensing pressure -while- evaporating into a 43 psig suction, would be by condensing at least the R-14, which would have minimally required condensing and evaporating the R-170.

    My questions to you are: Have you studied, or have been working with autocascades? Do you understand that an autocascade is not the same as a standard multi-compressor cascade, and that in an autocascade a mixture of refrigerants are fractionated out and used to cool successive stages? If not, then this may be the source of your dilemma about why I was able to condense R-170 (and R-14 which has a much lower boiling point), while using only one other refrigerant (R-600).

    One last question for you: Have you read through this entire thread? If not, then I would highly recommend that you do so, since much has been covered on the topic of autocascades and how we think they work.

    I'll be the first one to admit that there has been much theorizing on the subject, and I'm sure you'll find that some of the later posts will be in conflict with what had been thought to be fact in earlier ones. But overall I believe it has been a very productive effort, and hopefully is allowing others to have the knowledge to build their own autocascades, and have their own successes at condensing R-170, and/or R-1150, and/or R-14.

    Don't worry for me

    I didn't look at the pdf, and I now know the purpose of this cooling, nothing to be afraid of indeed

  18. #468
    Xtreme Member
    Join Date
    Dec 2005
    Location
    Rennes (france)
    Posts
    443
    Quote Originally Posted by mytekcontrols View Post
    I just read over my response to Clemmaster's questions, and although I didn't mean to come off as and over bearing know-it-to-all, I think it could possibly be perceived that way. My apologies go out if it felt this way to you as well Clemmaster
    No problem, that's the way I talk too I understand that it isn't personnal

    I apologize not having read the entire topic, I will, I'm sure I will find lots of information. I didn't know where the blend would saturate but as you said, It will saturate somewhere between butan and ethan point and that's the way it's supposed to be, that now make sense . I've always been thinking of "quasi-non blending" refrigerant (R290+R744 or R290+R23) not on HC mixtures and that's a part I'll we be working on!

    Thank you

  19. #469
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Quote Originally Posted by Clemmaster View Post
    I've always been thinking of "quasi-non blending" refrigerant (R290+R744 or R290+R23) not on HC mixtures and that's a part I'll we be working on!
    I like the term "quasi-non blending". In other words; a virtual refrigerant, one that exists only under certain conditions

    This is probably as good of a description as any, for what happens to the combination of refrigerants used within an autocascade as they are subcooled, and then go into solution with other nearby boiling point neighbors. Thus creating a condensate with a unique boiling point.

    I also think that the other affect that we see to lowering temperatures, is that brought on by evaporating a condensate into an environment which consists of gases that have a lower boiling point then the condensate itself (eg; R-14 evaporating into Argon rich environment). This could be compared to the effectiveness of an evaporative water cooler in a high humidity environment vs. a dry low humidity one. The low humidity environment, being of a large part composed of lower boiling point gases, allows for an increased flow of heat from the evaporation of the water. Where as the high humidity environment is less effective due to saturation.

    This is all part of the fun and magic to getting an autocascade to work properly
    Last edited by mytekcontrols; 04-17-2008 at 05:08 AM.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  20. #470
    Xtreme Member
    Join Date
    Dec 2005
    Location
    Rennes (france)
    Posts
    443
    Quote Originally Posted by mytekcontrols View Post
    I like the term "quasi-non blending". In other words; a virtual refrigerant, one that exists only under certain conditions
    Yes I don't know how to call these mixtures because two gases always start a reaction (even if it stops really quick, that's the way it is ).

  21. #471
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Yes I don't know how to call these mixtures because two gases always start a reaction (even if it stops really quick, that's the way it is ).
    This has been a problem for the engineers at Polycold for years. There was only one guy from Russia that had come up with a program that could accurately simulate a refrigerant mix for an autocascade. He had developed the program himself, and never shared it with anyone else. Unfortunately for Polycold he left, and went back to Russia, taking the program with him.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  22. #472
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819

    AC-2 Electrical w/Buffer Valve Circuit

    I received the high pressure switch yesterday (see photo below). It looks like it'll do the job just fine, and as it turns out, has the correct switch logic (Close on Pressure Rise). The Ranco Part Number is: 010-2054, and it is called a Condenser Fan Cycling Control. Range: 100 to 400 psig, Differential: 40 to 150 psig.

    I will most likely leave the differential setting at 40 psig (default), and set the cut-in to 350 psig.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Ranco PS.jpg 
Views:	890 
Size:	48.1 KB 
ID:	76745   Click image for larger version. 

Name:	AC-2 Electrical.gif 
Views:	899 
Size:	17.2 KB 
ID:	76746  
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  23. #473
    Xtreme Enthusiast
    Join Date
    Jul 2003
    Location
    Rio de Janeiro - Brazil
    Posts
    910
    Last edited by Marvin; 04-17-2008 at 07:51 AM.
    Q9550 EO @ 4.1
    Asus P5Q Deluxe
    4 Gb DDR2 Gskill
    2xVelociraptors 300 gb Raid 0
    Sapphire Vapor 4870 1Gb
    PCP&C 750w silencer psu

  24. #474
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Marvin --- those are pretty sophisticated controllers, but I think a bit more then what is really required for pressure control on the AC-2 unit.

    Below you will see an updated piping diagram showing the Buffer Valve and Pressure Control.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	AC-2 Piping Diagram with Buffer.gif 
Views:	1394 
Size:	34.5 KB 
ID:	76834  
    Last edited by mytekcontrols; 04-18-2008 at 07:25 AM.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  25. #475
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Yep thats the switch
    HPCO will cut out, a fan cycler will cut in. And they can be cheaper then that, but thats a rather high quality one