    My Cascades first run...

    Hello

    Ive just mounted the system for some testing (i wanted to test the HX's performance) and bah... smth is SERIOUSLY wrong...

    The system:
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	dsc00949.jpg 
Views:	360 
Size:	143.3 KB 
ID:	4992  

  2. #2
    Xtreme Legend
    Join Date
    Feb 2003
    Location
    Warsaw, Poland
    Posts
    1,648
    Ok, some more info

    I stage:
    10k btu/h tecumesh compressor
    R22
    -39C SST; -36 to -37C evap temp
    ~35C condenser outlet temp, dunno the SCT but the TXV is feeded all the time (can hear it)

    Im really in some panic, i cant think clar cause i get 10C SCT in the II stage with R22 ! With -35C sst temps on the I stage...

    Could i ask for some help, right now i cant think clear, the firt thing ill try to do is give you guys as much data as i can

  3. #3
    Xtreme Member
    Join Date
    Apr 2003
    Location
    dallas, tx
    Posts
    280
    what is the temperature of the liquid coiming from the ishx on the 2nd stage. i would trust that way more than the sct temperature.
    electrical engineering lab rat

    As always, there are three important questions involved:

    What is the heat load?

    How cold do you want it?

    Will that be Visa, MC, or Discover Card?

    -gary

  4. #4
    Xtreme Member
    Join Date
    Oct 2003
    Location
    The Netherlands
    Posts
    472
    Are you sure it isn't overcharged? I have seen this with my system; as soon as there is too much refrigerant in the system, the interstage HX fills up and the low stage condensing pressure skyrockets. The interstage HX then acts as a subcooler only.

  5. #5
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    It sounds to me like the low stage is overcharged. The difference between the high stage SST and the low stage SCT should be about 6-8C. Another possibility would be air in the low stage system.

    Remove refrigerant until the difference is 6-8C and let's see how the low stage performs then.