    What are the chances of someone testing a pair of compressors on a system with a micron guage?
    Before wdrzal tried it I would have said low. People who have a micron gauge don't use compressors to vacume a system, and people who use a compressor as a vacume don't own a micron gauge.

    Then by trying to remove just a few drops of water fro the bottle on the other side of system.
    I'm not too keen on the idea of putting a glass bottle on the high side of the pump, but I was thinking of putting volume marks on the bottle and measuring the rate of evaporation.

    As far as figuring out how much of a vacume my pump can pull, I was thinking of trying to boil water at lower temperatures. At 20 degrees the pressure needs to be lowered to 2.339 kPa, which my pump was able to do. At 0.01 degrees the pressure must go down to 0.6113 kPa, or about 4600 microns. If my junkyard compressors can do that, I will be thoroughly impressed.

    Here's a question though, why do you need to pull such a deep vacume? I understand the need to evaporate the water from a system and remove most of the gases, but why do you need to pull the vacume so deep? At what pressure/temperature would the compressor oil start to evaporate?
    2600-M @ 226*11.5 = ~2.6ghz
    IQYHA 0429 SPMW, NF7-S
    2x512 KHX BH-5, 2-2-2-11
    6800 GT, 465W Enermax
    2-Seagate120GB SATA 7200.7 RAID-0
    Modified Tt aquarious II, 41 degrees load

  2. #52
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Just outside London
    Posts
    404
    What do you define as low vac?
    100micron is a normal figure in my field.
    Pulling this sort of vac level gives me peace of mind that all moisture/air in the system has pretty much gone thus reducing the chance that the equipment will breakdown/wear out prematurely, it also helps me sleep at night because if it does breakdown at 3am guess who has to be there by 4am to fix it??
    Also, by pulling a deep vac or trying to a micron guage will tell you a little more about the condition of the system, it will indicate the tinyest of leaks and also give you a tiny hint into moisture levels. There have been so many times I have leak tested a system to 300psi and it's held the charge overnight only to find I can't pull a vac due to tiny, tiny leak the next day.
    A few effects of moisture and air in systems...
    blocked expansion devices or a partial blockage reducing perfromance and wasting electricity, copper plating that ruins compressors, the breakdown of compressor oils... all very important.
    I reall am going to sit on my boat here, basically, if you cant pull and maintain a low vac the systems only half good.

  3. #53
    I am Xtreme
    Join Date
    Mar 2005
    Posts
    4,849
    put the bottle on the high side of a refrigeration loop,while vacuum is connected to the low side.This way you will be pulling vacuum thru the entire system.

    Not the high side of the compressor.

    by a fast rise in a micron gauge you have a leak.if the pressure rises slowly you still have some moisture in the system.

    the reason for such a deep vacuum is that at any pressure above 1 micron there is unwanted gas/air in the system the deeper the vacuum the more that is removed.

    A often held misconception is that once you get below 0 psig and read a vacuum there in nothing inside the system, the system is in vacuum, this couldn't be further from the truth, the system is not completly empty until you reach 29.92 "HG of vacuum.

    being at 1"hg vacuum just means you are 1" hg below atmospheric pressure not that ther is no pressure present.once you understand the difference between psig(gauge) and psia (absolute)its easy to understand.


    you can do your test by boiling the water then put the bottle in a ice bucket, as soon as the boiling stops, note the temperature of the water. We can determine the pressure from this.

  4. #54
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Just outside London
    Posts
    404
    That was very well put.

  5. #55
    Xtreme Member
    Join Date
    May 2005
    Location
    Vancouver Canada
    Posts
    109
    Well I tried vacuming water at 0 degrees C and it worked. I half filled a bottle with crushed ice and stuck some water in with it to fill the gaps. I connected this to my vacume pump made of two old compressors, and it was able to make the water boil. With room temperature water there are a few very large bubbles, with this ice water there are hundreds of smaller bubbles from everywhere. I guess all the surface area of the ice changes how the bubbles form or something. In any case, I have figured out that my vacume pump can pull at least a 4600 micron vacume.
    2600-M @ 226*11.5 = ~2.6ghz
    IQYHA 0429 SPMW, NF7-S
    2x512 KHX BH-5, 2-2-2-11
    6800 GT, 465W Enermax
    2-Seagate120GB SATA 7200.7 RAID-0
    Modified Tt aquarious II, 41 degrees load

  6. #56
    Xtreme Member
    Join Date
    Aug 2003
    Posts
    203
    nicely done matt


  7. #57
    I am Xtreme
    Join Date
    Mar 2005
    Posts
    4,849
    yellow jacket came out with a model that reads from .5 microns to atmospheric pressure last year. if some has one of those we could get a accurate reading. all the ones I own only read below 2000 microns . other companys also make micron gauges like tif, supco, robinair.

    In any case very good work Matt !!!! now you need to buy a gauge to show just "how Loooow you can go" LOL

    While 4600 microns isn't ideal,I think its Super for 2 compressors, I think thats low enough with using a heat gun you can do a very good evacuation on a system.

    I wondering if adding a check valve will improve performance even more?

  8. #58
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Just outside London
    Posts
    404
    Well done on the mission to proving to some degree a compressor or two will do something worth while
    boy compressor technology has changed.

    I think that now you have the task of removing moisture contaminated oil from the compressors. now a vac pump has a little sightglass so you can see the oil and a very handy little drain screw on the bottom, so much easier.
    Sorry, I whill shut up about vac pumps now

  9. #59
    Xtreme Member
    Join Date
    May 2005
    Location
    Vancouver Canada
    Posts
    109
    I'm not sure if I really have to worry about water contaminating the oil. Every time I turn it on it spits out a little oil, so I think I will just have to continually throw a little oil down the low side.

    Measuring how much vacume I can pull on my Ghetto vacume pump with a crazy expensive micron gauge just seems wrong. I will stick to ghetto measurements Maby I could try boiling some other fluids at different temps to see what it can do.
    2600-M @ 226*11.5 = ~2.6ghz
    IQYHA 0429 SPMW, NF7-S
    2x512 KHX BH-5, 2-2-2-11
    6800 GT, 465W Enermax
    2-Seagate120GB SATA 7200.7 RAID-0
    Modified Tt aquarious II, 41 degrees load

  10. #60
    Registered User
    Join Date
    Nov 2002
    Location
    Tampa,FL. USA!
    Posts
    20
    Water will contaminate the oil. In a vacuum pump application, that is what it's supposed to do. If you see the oil getting milky in a vacuum pump, then you're way past due in changing it. In a low temperature application, you only need a 1/4 of a drop of moisture in your system to clog your cap tubes. Moisture also tends to convert your refrigerant oil to a wax-like substance, also clogging your expansion device, and contributes to increasing your acidity levels in the system from chemical reaction with your hermetic compressor winding insualtion if overheated. Once the acidity level increases, it starts a vicious cycle of increasing further due to more reaction with the compressor windings and further heat due to the failing windings. Eventually the compressor burns out, and you have a very contaminated system on your hands. It's then time for a complete rebuild of your system.
    This is a worst case scenario, but not unavoidable. Oversizing your filter-driers will help a bit, and triple-evacuating your systems at least twice may help avoid the bad burnouts. In my opinion, it may be better to invest in an actual vaccuum pump, and have repeated good results in evacuating systems(and save an ass-load of time), than going through troubleshooting a system that may have moisture in it. Hell, if you don't like it, you can always sell it on E-Bay anyways..

    Just some toughts from some joker
    who does this stuff every day..
    MSI K7T266 Pro2 RU, AMD XP2200,Radeon9800 AIW128mg,Herc GTXP...

  11. #61
    Xtreme Addict
    Join Date
    May 2005
    Location
    Nova Scotia,Canada
    Posts
    1,004
    I got another used compressor at work today so i added it to my vacuum pump and now with this 3rd compressor i got in series with the other 2. So when i had only the 2 compressors on i couldn't get the water to boil just after it came from the tap because its cool but after i fired up the 3rd compressor the water start boiling right away
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	3rd compressor.JPG 
Views:	62 
Size:	126.2 KB 
ID:	33797   Click image for larger version. 

Name:	3rd compressor1.JPG 
Views:	84 
Size:	148.4 KB 
ID:	33798   Click image for larger version. 

Name:	bubbles.JPG 
Views:	64 
Size:	96.2 KB 
ID:	33799  
    My Rig:

    Q6600 2.4Ghz@2.9Ghz Custom Liquid Cooling
    ATI X1950XTX 512mb DDR4
    MSI 975X Platinum PowerUp Edition
    2gb Kingston Hyper-X DDR2 667
    Sound Blaster Audigy2
    2 IDE HDD, 2 SATA HDD
    LG DL16XDVD Writer,52X CDROM
    OCZ 520Watt PSU 33Amp +12v
    Thermaltake Xaser III case
    Logitech Z560 4.1 400watt Surround Sound

    3Dmark03-21112
    3Dmark05-12154
    3Dmark06-8054

  12. #62
    Xtreme Member
    Join Date
    Aug 2004
    Location
    Stevenage, England
    Posts
    143
    this has been a really interesting read i my self use a compressor to vacuum my system, i only do so as its cheaper and im still fairly new to all this.

    would a more powerful compressor work better as a vacuum pump, what would be the minimum for ther job ?

    whats the best way to vacuum a system with compressors ?

    MW

  13. #63
    Xtreme Addict
    Join Date
    May 2005
    Location
    Nova Scotia,Canada
    Posts
    1,004
    Quote Originally Posted by mr-white
    this has been a really interesting read i my self use a compressor to vacuum my system, i only do so as its cheaper and im still fairly new to all this.

    would a more powerful compressor work better as a vacuum pump, what would be the minimum for ther job ?

    whats the best way to vacuum a system with compressors ?

    MW
    The size of the compressor doesn't matter the only difference is the larger the quicker it will pull a vacuum.

    MW-"whats the best way to vacuum a system with compressors ?"

    set them up just i do in my pic above there in series.
    My Rig:

    Q6600 2.4Ghz@2.9Ghz Custom Liquid Cooling
    ATI X1950XTX 512mb DDR4
    MSI 975X Platinum PowerUp Edition
    2gb Kingston Hyper-X DDR2 667
    Sound Blaster Audigy2
    2 IDE HDD, 2 SATA HDD
    LG DL16XDVD Writer,52X CDROM
    OCZ 520Watt PSU 33Amp +12v
    Thermaltake Xaser III case
    Logitech Z560 4.1 400watt Surround Sound

    3Dmark03-21112
    3Dmark05-12154
    3Dmark06-8054

  14. #64
    Xtreme Member
    Join Date
    Aug 2004
    Location
    Stevenage, England
    Posts
    143
    the reason i asked was because i got told running compressors in series didnt work because the second compressor could only move what the first had removed so it didnt increase performance. then i read it was good to have one compressor on the high side and one on the low both vacuuming together ?