Thread: subcooling and supaheat calculations??

  1. #1
    -100C Club Member
    Join Date
    Feb 2004
    Location
    australia
    Posts
    3,766

    subcooling and supaheat calculations??

    i always forget which way around things are, so i though i would get a thread started. This way I can book mark it
    is this correct.

    subcooling.
    we take the pressure measurement at the condenser and convert that to degrees F.
    we then measure the temperature of the liquid line after the condenser again in degrees F
    subcooling an example now; example (r290) 150PSIG(89F) - 82F gives 7F (what is the ideal subcooling value?)


    then i would do the same for supa heat. take the pressure and convert that to degrees F with table.

    is it the difference between the pressure/temperature valve and the evap temperature (or is it the) temperature 6" from the compressor. (i always get messed up with this bit)
    8F-12F is a good level of supaheat correct.

    the negatives seem to stuff the answer up though.
    Example: r290 at 10Hg and evap -50c and 6”from compressor is -40c.
    10Hg(-60F) - -41F= -20F ??

    and another system example: evap is -31c, 6”from the compressor is -20c, pressure 0spig
    calculation
    0psig(-43F) - -5F= -38F

    or if I do it on the evap temperature.
    0psig(-43F) - -25F= -18F

    i remember that garry (what has happened to him, hasn’t been here for months) use to teach alot about this, he said it wasn’t about the temps its about getting these figures correct to enable the phase change system to function correctly and per long compressor life etc.
    so any help i would appreciate
    Last edited by kayl; 12-12-2004 at 10:29 PM.

  2. #2
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    Subcooling is how much of a temperature drop you get after you condense your gas.

    The temperature your gas condenses at is obtained from the high side pressure reading and a chart.

    So for propane condensing at 160 psig, the corresponding temp is 34.5ºC
    Now measure the temperature at the exit of the condensor and this will tell you how much the temp has dropped after the gas has condensed.

    Say it reads 24.5ºC then the degree of subcooling is (condensing temp - condensor outlet);
    34.5-24.5 = 10º of subcooling.

    For superheat we want to measure how much of a temperature increase is exhibited by the evaporating gas, thus:

    Take the low side pressure and look up chart for corresponding temp.

    So for 0psig the evaporating temp is -42ºC (R290).

    Now measure the temp of the suction line 3-6" from compressor, say it reads -27ºC.

    Your degree of superheat is now (Suction Line Temp - Evaporating Temp);
    -27 - (-42) = 15

    If you do your calculations in ºF then you need to divide your final answer by 1.8.

    Hope this helped

  3. #3
    Registered User
    Join Date
    Aug 2004
    Posts
    21
    great info

  4. #4
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    Looking at your sums for superheat, you were subtracting the suction line temp from the evaporator temp. It should be the otherway around also use the evaporating temp from the chart at the low side pressure. So for your 2 examples;

    Example: r290 at 10Hg and evap -50c and 6”from compressor is -40c.
    10Hg(-60F) - -41F= -20F ??

    It should be;
    convert -40ºC to ºF.
    -40*1.8+32 = -40ºF
    Next;
    -40 - -60 = +20
    Next convert to ºC/Kelvin
    +20/1.8 = 11.11 degrees of superheat


    and another system example: evap is -31c, 6”from the compressor is -20c, pressure 0spig
    calculation
    0psig(-43F) - -5F= -38F

    This time we can convert the chart temp to ºC first this time;
    (-43 -32)/1.8 = -41.67ºC
    Next subtract chart temp from suction line temp;
    -20 - (-41.67) = 21.67 degrees of superheat

  5. #5
    HVAC/R Engineer
    Join Date
    Nov 2003
    Posts
    3,565
    These systems will work fine with a superheat of 8 to 12 degF and a subcooling of 5 to 8 degF.

  6. #6
    -100C Club Member
    Join Date
    Feb 2004
    Location
    australia
    Posts
    3,766
    thanxs guys this is exactly what i want and some great examples
    cheers.
    so me rotary 1HP running bbq r290 runs sweet at 10Hg
    and the other will need a capillary tube shortened.
    Last edited by kayl; 12-13-2004 at 05:09 PM.

  7. #7
    Xtreme Hardware Killer
    Join Date
    Jan 2004
    Location
    Behind you
    Posts
    1,265
    chilly1 think we can get a thread stickied about this math stuff?
    Level 80 UD Death Knight on Murmur (Beta)

  8. #8
    HVAC/R Engineer
    Join Date
    Nov 2003
    Posts
    3,565
    I is already in the stickins isn't it?

  9. #9
    Xtreme Member
    Join Date
    Nov 2002
    Location
    Sierra Nevada Mountains (not my Beer)
    Posts
    472
    Quote Originally Posted by chilly1
    I is already in the stickins isn't it?
    Soooo ... Good sticky! What do ya think?