2. On the subject of Water In temps it would be useful to know what this value was as a check against energy dissipated by the radiator, for example in Martin's test of the MCR220 (
http://martin.skinneelabs.com/Swifte...20-Review.html) when using 1000rpm fans the drop in water temperature over the rad is 0.43°C, flowrate was 1.5gpm, and the water temperature was ~40°C (need this for a density calculation).
To calculate the watts dissipated the following equation must be solved,
KiloWatts Dissipated (kJ/s) = Mass Flowrate (kg/s) * Specific Heat (kJ/kg.K) * Temp. Change (K)
So for Martin's scenario,
Mass Flowrate = 1.5 gpm = 5.68 L/m = 0.095 L/s = 0.094 kg/s (Density @ 40°C = 992 kg/m³)
Specific Heat = 4.1813 kJ/kg.K
Temp. Change = 0.43 K
Kilowatts = 0.094*4.1813*0.43 = 0.169 kW = 169W
Martin states that the applied heat load is 302W for that much energy to have been dissipated a temp difference of 0.77 K would be required.
When the fan speed is increased to 3000rpm the temp difference rises to 0.61°C this equates to a heat dissipated of 240W much closer to the applied value of 300W.
I assume that this is an artefact of heat loss from the reservoir, tubing and other equipment in the loop which is amplified as the water temperature in the loop increases, of course what it does mean is that the C/W values are off as the rad is actually not dissipating as much energy as was assumed.
Without Water In temps for your tests I can not compare the different fan speeds to see if your testing follows the same trend, I also have not yet completed my thinking on the ramifications for what it means in terms of calculating C/W we will know how much heat was actually dissipated by the radiator but this is effected by the heat loss in the rest of the loop.
Perhaps insulating all tubing, reservoirs etc would make for a more controlled system in terms of radiator performance.