    Project 173K: -109C first testrun

    The first testrun without any optimizations. High stage has not enough refrigerant (superheat almost 15K). The low stage has certainly not enough refrigerant; I just gave it a shot. Superheat at the compressor is more than 70K. But I admit that I must do accurate measurements. But that's something for the next session.



    Interstage is -35C. This is measured at the TEV bulb, so it is heated a bit by the incoming hot ethylene. 'real' temp is probably lower. I cannot measure pressures at the moment since I have only one meterset.

    Evaporator (unloaded) runs at -109C. This was 5 seconds before I pulled the plug. But as I said: it's a testrun.

    Low stage pressures. Discharge pressure is a bit low IMHO. But, this is with too little refrigerant.



    Next thing on the list is finishing the electrical interconnections (currently only the high pressure switch is connected, the rest is plugged directly in the wall outlets). Then, optimization of the high stage. And finally, optimization of the low stage, with load.

    edit: a system overview of a few days ago. I promise I will shoot more detailed pictures and finish the article on my website. But burning copper is more fun than writing


  2. #2
    Xtreme Owner Charles Wirth's Avatar
    Join Date
    Jun 2002
    Location
    Las Vegas
    Posts
    11,657
    Sweeet, nice job
    Intel 9990XE @ 5.1Ghz
    ASUS Rampage VI Extreme Omega
    GTX 2080 ti Galax Hall of Fame
    64GB Galax Hall of Fame
    Intel Optane
    Platimax 1245W

    Intel 3175X
    Asus Dominus Extreme
    GRX 1080ti Galax Hall of Fame
    96GB Patriot Steel
    Intel Optane 900P RAID

  3. #3
    Xtreme Member
    Join Date
    Dec 2003
    Posts
    128
    thats what im talking about baby ... great work once again

  4. #4
    Xtreme Member
    Join Date
    Oct 2003
    Location
    The Netherlands
    Posts
    472
    Static pressure was only 6 bar after equalisation. Thus, very little ethylene. No expansion tank mounted yet. The weakest low stage component has a maximum working pressure of 22 bar (and a much higher burst pressure), so I can go a long way when adding refrigerant. Still, I think I will add an expansion tank just to lower the compressor motor startup torque required.

    The only problem is where to leave it. It's already crowded on the baseplate, and it will be even more crowded when I fitted the electrics.

    I might consider putting 3-8 meters (9-24ft) of 22mm (7/8") capped copper pipe in a zig-zag pattern, and mounting that below the baseplate. The cascade is high on it's wheels, so that would not be a bad spot after all. Of course I would add a steel plate to protect the pipes.

    An old receiver is easier, but I don't have any spare ones left.

    But I have plenty of time; the high stage needs attention first.

  5. #5
    Xtreme Member
    Join Date
    Jan 2004
    Location
    Baku, Azerbaijan
    Posts
    164
    DaBit WOW! -109 at first run ! Very nice, nice and nice again !

  6. #6
    Moderator
    Join Date
    Jun 2002
    Posts
    2,440
    Very nice. I'm thinking of getting some ethylene as well as the price is about $300 for 12kg, very good pricing.

  7. #7
    Xtreme Member
    Join Date
    Oct 2003
    Location
    The Netherlands
    Posts
    472
    Very true. I paid about EUR 70,- for 3kg, excluding bottle rent and dropoff cost etc.

    But keep in mind that pressures are insane. My pressure gages only show low pressures because there is not nearly enough ethylene in the low stage.

    Make sure you can maintain -30C SCT or lower, or don't even think about using ethylene but consider ethane instead.

  8. #8
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    Aggghhh Bar!!!

    Big time congrats, you are a sick man. you are now in the top 5% of my trade, lol. you need to stop im starting to feel stupid over here..... That controler has never been happier. good job!!!! Very very impressive!!!


    you people are going to be the death of me.
    If i was an animal Id be a freezer.

  9. #9
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    Looks like all of your research is paying off, DaBit. Congrats.

    Don't worry about not having a second set of gauges. Interstage TD is about the same as TEV superheat, so once the high stage is set up, down to temp, and has the right superheat setting, then the low stage SCT should be about the same as TEV bulb temp on the high stage.

    Hope that makes sense.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  10. #10
    Xtreme Member
    Join Date
    Oct 2003
    Location
    The Netherlands
    Posts
    472
    Originally posted by captaincascade
    Big time congrats, you are a sick man. you are now in the top 5% of my trade, lol. you need to stop im starting to feel stupid over here.....
    No need to, yet
    I still haven't passed your loaded temps..

    That controler has never been happier. good job!!!! Very very impressive!!!
    and I haven't been happier with any other controller. The thing reacts damn quick on temp changes, and it seems accurate too.

    you people are going to be the death of me.
    Next idea is already brewing in my mind. I've passed the -100C mark, but not yet the 100K mark

  11. #11
    Xtreme Member
    Join Date
    Oct 2003
    Location
    The Netherlands
    Posts
    472
    Originally posted by Gary Lloyd
    Looks like all of your research is paying off, DaBit. Congrats.
    Thanks
    Research is done, finetuning begins. I bet I will need your help in the near future

    Don't worry about not having a second set of gauges. Interstage TD is about the same as TEV superheat, so once the high stage is set up, down to temp, and has the right superheat setting, then the low stage SCT should be about the same as TEV bulb temp on the high stage.

    Hope that makes sense.
    It makes sense, but I will measure this once to be sure of that.
    I expect a small difference (in the order of 2-4K) between temp @ TEV bulb and low stage SCT. With ethylene, this increases pressure quite a lot.