    Are you sure your not having a problem getting r290? Sounds almost like your adding air to the system.


    If you have a cooling question or concern feel free to contact me.

  2. #502
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Adam give me a break

    No I verified that I was getting liquid propane spurting out of the cylinder when held upside down. And I charged it into my evacuated 3x9 addition tank using an electronic scale, being sure to purge the lines with propane to get rid of any air. Also had a brand new supco filter dryer inline to absorb any water that might have been in the propane. Stuff was getting cold past the first phase separator, and I'm sure that if I had added more that I could have seen the temperatures drop in the first stage, but unlike the R123/R22 combo, the R600/R290 combo tends to reflect the pressure of the R290, which can get quite high when a saturated liquid is present (the R123 actually reduces the pressure of the R22 or R410a when mixed). This wouldn't leave me much room to add the other gases.

    I will leave it up to others to puzzle the HC mystery.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  3. #503
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Heh thats odd indeed, I'll have to get back to testing my autoc once I get more time.


    If you have a cooling question or concern feel free to contact me.

  4. #504
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Heh thats odd indeed, I'll have to get back to testing my autoc once I get more time.
    So you have been making progress on this project. I was beginning to wonder. Pretty stealthy I'd say... NOLTECH = AREA 51

    Any more details you can divulge?
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  5. #505
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Not going to use a rotary


    If you have a cooling question or concern feel free to contact me.

  6. #506
    Xtreme Addict
    Join Date
    Oct 2005
    Location
    England, Northwest
    Posts
    1,219
    Quote Originally Posted by n00b 0f l337 View Post
    Not going to use a rotary
    My god, the flood of detail is going to drown me.

  7. #507
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Quote Originally Posted by yngndrw View Post
    My god, the flood of detail is going to drown me.


    Quote Originally Posted by n00b 0f l337 View Post
    Not going to use a rotary
    Any reason not to? From my recent experiences, it seems like a rotary makes for an excellent pump. Twice as efficient as a reciprocating, able stand much higher static pressures, great start-up torque, and compact size. What else could you ask for?

    Perhaps you're going to use a Scroll instead?

    Hey wait a minute... AREA 51... recovered alien technology... Hmmm....
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  8. #508
    Xtreme Member
    Join Date
    Jul 2005
    Location
    Austria
    Posts
    428
    A reciproc can fit into a normal SS case. Maybe he wants to build an autocascading system in a SS case.

  9. #509
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Any reason not to? From my recent experiences, it seems like a rotary makes for an excellent pump. Twice as efficient as a reciprocating, able stand much higher static pressures, great start-up torque, and compact size. What else could you ask for?

    Perhaps you're going to use a Scroll instead?
    Well, simply put, height, though not so much in this case, but also noise. Rotary's are lovely and all, however though this version will be much too big for a single stage case, I do want to get it down to that sort of height.


    If you have a cooling question or concern feel free to contact me.

  10. #510
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Damn lost the auction on that Danfoss SC12CLX... Maybe rotary will occur in this build after all.


    If you have a cooling question or concern feel free to contact me.

  11. #511
    Xtreme Mentor
    Join Date
    Feb 2007
    Location
    Victoria, British Colombia
    Posts
    2,677
    what was your highest bid and how long left?
    mentally confused and prone to wandering

  12. #512
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Um bid at $45, someone took at $52.50, both with 4 seconds or so left?


    If you have a cooling question or concern feel free to contact me.

  13. #513
    Xtreme Mentor
    Join Date
    Mar 2006
    Location
    Redvers, Sask, Canada.
    Posts
    2,974
    Bumping thread due to sheer awsomnes of it!
    Bring back natural selection! No more warning lables!

    The one and Only MG Pony

  14. #514
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Thanks MG

    This also served to remind me that I still need to post an update on this project.

    What's been happening:
    I did quite a few tests with R410a, until I finally decided that it just isn't anywhere as good a refrigerant as R22 (of course I kinda suspected this all along, but now I'm completely convinced). Although I did get some interesting results by eliminating the argon, and boosting everything else (almost got it to do -90C at 225 watts).

    Anyway I shelved it for quite a while, having other projects needing my attention. But as of last week, the AC-2 unit now has a Sub-Cooler, and is undergoing tests to see how cold it'll run (as of today; -139C under a non-loaded condition, and about -115C with 50 watts applied --- probably close to the maximum load). It wont suit a PC cooler application, but it'll do just fine for use as a water vapor cryo-pump on our shop's helium mass spectrometer (5-10 watt load).

    I'll be putting the finishing touches on the case, adding a front panel, and basically wrapping up this project over the next 2 weeks. It was great fun building this little pup, and I hope you guys enjoyed it as well. I'll be posting pics and specs in a few days, and will also show you the final form in a couple of weeks.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  15. #515
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    That we did, that we did.


    If you have a cooling question or concern feel free to contact me.

  16. #516
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819

    Sub-Cooler No Load Test

    I think I am done with the refrigerant charge tweaking.

    Here is the Cool-No-Load results:
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	AC-2_SubCooler_Test_8-9-08.jpg 
Views:	672 
Size:	84.8 KB 
ID:	83320  
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  17. #517
    Registered User
    Join Date
    Jun 2008
    Posts
    75
    So Michael why is it you still use R22 instead of R290, is it because oil return isn't an issue or the flammability of propane?
    Last edited by Raadster; 08-10-2008 at 09:21 PM.

  18. #518
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Flammability is not an issue (already using ethane in the charge). It is more the fact that I haven't had good success with using R290 alone, or in combination with R600. Or for that matter, R600 alone.

    I figure if I've got to use R123 anyway, at least in order to obtain the best overall results, then I may as well use it in combination with R22. Yes there probably is an HC substitute for the R123, but I don't have anything on hand. And we just have a ton of R22 that was recovered from an ice skating rink for free, so I really can't beat the price.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  19. #519
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Your early charges with R600 in this thread point to good performance though, then you found a blocked captube. Is it possible that too many HC's makes purification hard? Or is R600 too low a BP? Though its only 0C, and r114 is very ideal...


    If you have a cooling question or concern feel free to contact me.

  20. #520
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819

    Final Piping Diagram with Sub-Cooler for HMS use

    I have attached what I certainly hope is the final piping diagram for this project (assuming I haven't made any errors). It is a vector pdf, since the resolution of a bit mapped image would probably not capture the detail.

    It is a modified version of earlier diagrams that I posted, and shows the AC-2 unit in its new application dress. That being a water vapor cryo-pump for a helium mass spectrometer.

    Please note that the offset as shown in the Final vs. the Sub-Cooler captube coming out of the bullet strainer is intentional. Having the SC captube slightly lower then the Final captube insures that the Sub-Cooler always gets fed some condensate, no matter how poor the quality or quantity of what is available. This makes sure that the Sub-Cooler is always trying to operate in an active mode, and thereby continues to create an environment where the Argon will dissolve into a sub-cooled R14 stream that runs through it.
    Attached Files Attached Files
    Last edited by mytekcontrols; 08-11-2008 at 10:16 AM.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  21. #521
    I am Xtreme
    Join Date
    Mar 2005
    Posts
    4,849
    Polycold wasn't purchased for 22 million dollars in 2003 for a outdated cfc/hcfc mix that's no longer usable.

    The present invention overcomes the need for using CFC refrigerant mixtures in a refrigeration system by utilizing refrigerants R14, R134a, R508a or R508b, R142b, and R740 in a component mixture. To achieve desired properties, these refrigerants may be used in a special mixture.
    Last edited by wdrzal; 08-11-2008 at 09:25 AM.
    The Laws of Thermodynamics say:

    Zeroth Law: "You must play the game."
    First Law: "You can't win."
    Second Law: "You can't break even."
    Third Law: "You can't quit the game."

    Do you wanna Play Thermodynamics ???????? I forgot "you must"

  22. #522
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Nol -- good observation.

    Come to think of it, I probably didn't explore this avenue as well as I should have, but I did do a follow up test with R600 after fixing the captube, and was still seeing some strange behaviour. At the time I attributed this to too good of separation within the various phase separators, possibly causing a starvation effect to occur in the later stages. But then again, I was also trying to make a 4 stage autocascade work more like a 3 stage at the time. Now that the unit has a sub-cooler, and I am using a much greater quantity of Argon (I'll post the final charge soon), I am obviously using all 4 stages (-140C). Perhaps R600 and/or R290 combo would work well in this situation.

    Perhaps you'll have better luck with your AutoC project.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  23. #523
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Good point Walt. But Polycold has access to refrigerants that I simply don't.

    Polycold charge as stated in their patent:
    R236fa, R125, R23, R14, Argon (EDIT: forgot to list the R23)

    Requires POE oil, and extremely good oil separators (Polycold had some gigantic ones custom made to their specs).

    EDIT: BTW; I no longer work for Polycold, and this project was not an attempt to make what they have made, it was simply meant to serve as a tutorial on autocascades (which I think it has done quite well).
    Last edited by mytekcontrols; 08-11-2008 at 09:58 AM.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  24. #524
    I am Xtreme
    Join Date
    Mar 2005
    Posts
    4,849
    Quote Originally Posted by mytekcontrols View Post

    EDIT: BTW; I no longer work for Polycold, and this project was not an attempt to make what they have made, it was simply meant to serve as a tutorial on autocascades (which I think it has done quite well).
    I realized that, and it was a great build and informative.

    Getting below -120c oil becomes a major issue. Thats why we need a new compressor design.

    Maybe a 3 stage axial oilless design......30 to 40 bar pressure differiantal @ 40,000 rpm.
    The Laws of Thermodynamics say:

    Zeroth Law: "You must play the game."
    First Law: "You can't win."
    Second Law: "You can't break even."
    Third Law: "You can't quit the game."

    Do you wanna Play Thermodynamics ???????? I forgot "you must"

  25. #525
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Interesting with r236FA, boils at -1.4C. Then a jump to R125 which is rather high pressure, almost like r410a.
    I think from a boiling point sense, they've tried to make like a r114 with r236fa, but then are skipping the r23 like refrigerant in favor of r125 saturated with r14 maybe?


    EDIT: Looking over and overlaying some charts, it would seem that R236FA is well, hell almost like butane exactly, except three times the mass, and a tendency to really mess with oil. That's odd indeed.
    Wish you had another one mytek of the AC2 to work with, could with your three phase seps, probably try r600, r290, veryyyy small amount of r170, then jump to r14, and maybe some argon.
    Last edited by n00b 0f l337; 08-11-2008 at 09:40 AM.