Need help for troubleshooting a SS
I have a single stage with the following parts :
Compressor : Electolux GD30MB R134A , charged with R507A
Condenser : Original from Prometeia Mach2
Cap tube : 2.5m 0.031"
Evap from Eleven .
The Compressor is 1/12HP and i'm planning to use it for cooling my X1900XTX . There is some strange behaviour that bothers me .
For heatload tester i have an 170W peltier . I put some AS ceramique on it's hot side . Next i put a cold plate & finally the evaporator .
Peltier Voltage| Pressures |Plate temp |Suction temp|
--------------+----------+-----------+------------+
0V |20/200PSI| -29C | 17C |
5V |24/215PSI| -17C | 14C |
12V |42/260PSI| +3C | 25C |
-----------------------------------------------------
Now ... if i remove some refrigerant i get the following ...
Peltier Voltage| Pressures |Plate temp |Suction temp|
--------------+----------+-----------+------------+
0V |6/190PSI | -36C | 29C |
5V |12/210PSI| -27C | 29C |
12V |36/255PSI| -2C | 29C |
----------------------------------------------------
What do you think it's wrong ??? The temperatures are 100% right.
So , when i put more refrigerant , the evap temp goes up and the suction line gets colder ...
I'm not sure but i have 2-3 things in mind ... But first i would like to read some opinions .
Thanks .