Thread: Morphing Air Conditioner into Autocascade System

  1. #376
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Quote Originally Posted by Polizei View Post
    What do you mean you wonder if the compressor can start without drawing too many amps? Haven't you run it already?

    Yes I have run it (how else would I have gotten the data), but the system was originally started up day before yesterday with a lower static BP of 154 psig. I then boosted up its charge while running, in order to tune it for 150 watt operation, and then incrementally reduced the applied load to obtain the load profile curve you saw above.

    I shut it down, and watched its pressure build while also observing the temperatures of the stack TC's. When it got to nearly 0C and was just approaching 200 psig, I was satisfied that it was tracking with what I had estimated the additions should increase it by. When I get a chance today, I'll try a re-start and see what happens. I'll also verify what the warmed up BP is as well.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  2. #377
    Xtreme Cruncher
    Join Date
    Nov 2006
    Location
    'burb of Cleveland, Ohio
    Posts
    2,871
    Oh... so you haven't run it since you initially charged it.

    I was going to say...

  3. #378
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Quote Originally Posted by Polizei View Post
    Oh... so you haven't run it since you initially charged it.
    Yes I have run it. I just haven't re-started it from a warmed up state.

    As I said earlier, I made refrigerant additions while it was running and cold. Just haven't verified how these additions will ultimately add up, or how they will affect the start up capability of the unit.

    Edit: I think we are of the same understanding... just saying it in different ways.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  4. #379
    Xtreme Cruncher
    Join Date
    Nov 2006
    Location
    'burb of Cleveland, Ohio
    Posts
    2,871
    Oh. Cut me some slack... I was up early for an extremely boring C++ programming class this morning.

    My reading comprehension went back to bed.

  5. #380
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Quote Originally Posted by Polizei View Post
    Oh. Cut me some slack... I was up early for an extremely boring C++ programming class this morning.
    OK you win But when I turn 70 and the alzheimer's begins to kick in, I'll be expecting the same
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  6. #381
    Xtreme Cruncher
    Join Date
    Nov 2006
    Location
    'burb of Cleveland, Ohio
    Posts
    2,871
    Quote Originally Posted by mytekcontrols View Post
    OK you win But when I turn 70 and the alzheimer's begins to kick in, I'll be expecting the same
    Sounds fair.

  7. #382
    Xtreme Member
    Join Date
    Jul 2005
    Location
    Austria
    Posts
    428
    He means that he is wondering if the Amps drawn by the compressor at startup will exceed its maximum rating or if it will be within specifications.

  8. #383
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Quote Originally Posted by godmod View Post
    He means that he is wondering if the Amps drawn by the compressor at startup will exceed its maximum rating or if it will be within specifications.
    This is what I still need to find out. Hopefully it will be within specifications, or can be persuaded to by allowing the discharge to bypass into the expansion tank immediately upon start-up. I figure opening a solenoid valve between the compressor discharge line and the expansion tank for maybe the first few seconds would probably do it.

    The LG QA090C's motor current rating is 5.2 amps @ 115V, exceeding this by as much as 1.25% (6.5 amps) for a short period of time should do no harm, and is considered acceptable. Going much over this could cause a premature failure.

    So I'll see what happens later today.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  9. #384
    SSD faster than your HDD
    Join Date
    Feb 2005
    Location
    Kalamazoo, MI
    Posts
    2,627
    Stunning work Michael, top notch stuff. -100 at 25W+ over your initial goal. You must be pretty happy

  10. #385
    Xtreme Member
    Join Date
    Jul 2005
    Location
    Austria
    Posts
    428
    Quote Originally Posted by mytekcontrols View Post
    The LG QA090C's motor current rating is 5.2 amps @ 115V, exceeding this by as much as 1.25% (6.5 amps) for a short period of time should do no harm, and is considered acceptable. Going much over this could cause a premature failure.
    5.2A + 1,25% = 6.5A ?
    Does not work for me
    (It would be 25%)

  11. #386
    SSD faster than your HDD
    Join Date
    Feb 2005
    Location
    Kalamazoo, MI
    Posts
    2,627
    I am sure he meant 25%, which you would multiply by 1.25

    Just a % sign in the way of a perfect calculation

  12. #387
    Xtreme Member
    Join Date
    Jul 2005
    Location
    Austria
    Posts
    428
    Quote Originally Posted by RyderOCZ View Post
    I am sure he meant 25%, which you would multiply by 1.25
    Just a % sign in the way of a perfect calculation
    You are right
    ...like double negation

  13. #388
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Yep, I did mean 1.25 x 5.2 amps, or 25% over spec. Sorry
    (damm... Alzheimer's kicking in already)

    Quote Originally Posted by SoddemFX View Post
    You can use a solenoid valve on the compressor suction return, in parrallel with which is restrictive length of tubing.

    At startup the solenoid valve is closed, causing the return gas to flow through the restriction. The restriction causes a pressure drop between the suction line and compressor suction port.

    The developed pressure drop reduces the motor loading on the compressor, because the compressor is doing less work.

    When the system has become stable the solenoid is opened and the system opperates as normal.
    Interesting idea, and yes I see how this could work (I'll have to write this down)

    But not to dismiss it, I will probably do the buffer valve thing I mentioned, for the simple fact that I have used this before in autocascades with great success. Although it does depend on small pressure drop to be effective, where as your idea doesn't.

    Quote Originally Posted by RyderOCZ View Post
    Stunning work Michael, top notch stuff. -100 at 25W+ over your initial goal. You must be pretty happy
    Yes I am!
    Thanks for the kudos.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  14. #389
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Basically the same as an idle load switch in a way. Just a way to connect high and low with little to no restriction. Plumb it into the expansion tank and let the restriction between there and system to equalize and then close the valve once compressors going.


    If you have a cooling question or concern feel free to contact me.

  15. #390
    Xtreme Enthusiast
    Join Date
    Jul 2004
    Location
    The Netherlands
    Posts
    985
    Quote Originally Posted by mytekcontrols View Post
    Thanks Chris. I too am amazed at what this little sub 10cc compressor can do


    Wait no longer, here they are:
    Coil outlet is Evap inlet, in the graph Shouldn't it be Evap outlet?

    Anyway 150 Watts! Nice!
    Not too shabby!

  16. #391
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Some thoughts...

    I have been doing some thinking on why the R-600, R-170, R-14 charge did not work as expected. It appears to all come down to how effective is the separation in my home brew phase separators. I had assumed it would be simply adequate, but not phenomenal, especially in the later stages. But now I'm not too sure about this.

    Remember the 3600 Watt "Big Brother" unit I showed in a previous photo? A unit similar to this was my first test bed for an R-600 charge. It worked unbelievably better, and with only half the liquid (R-600) than the previous R123/R22 combo. So I just assumed that I would see similar results with my AC-2 unit when using R-600. Why didn't I? well I think that proportionally speaking, all my phase separators are much much larger then what is used on the "Big Brother" unit. How much larger? At least 13 times the volume (based on compressor mass flow differences).

    So it would stand to reason that the AC-2 unit would be far superior in its ability to separate the liquids from the gases at each phase separation point. Having poor phase separation allowed the "Big Brother" unit to get by without a mid-carrier refrigerant between R-600 and R-170 (80 degree C difference in boiling points).

    But the AC-2 unit with its superior phase separation, ended up disconnecting between the lower and upper stages, mainly due to excessive amounts of R-170 being dissolved into the R-600 and robbed from the downstream stages. And later as the lower stage got even colder due to it's isolation from upper stage loads, the temperature dropped to the level that even R-14 was being gobbled up as well. Probably the best way to over come this would have been to add a mid-carrier refrigerant such as R-290 or R-22. Another way was by using brute force, and adding excessive amounts of R-170 and R-14 in order to compensate (this is what I did on my first tests). But from a thermodynamic aspect, this probably just ends up making 3 phase separated autocascade, into something that acts more like 2 phase separated design due to inter-stage flooding.

    R-600 should still be better at moving heat then an HCFC. So perhaps I'll try a future test with an R-600/R-22 combination to see what happens. If I had R-290 I'd try that as well.

    I still might get even more out of the AC-2 unit
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  17. #392
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Quote Originally Posted by Jack View Post
    Coil outlet is Evap inlet, in the graph Shouldn't it be Evap outlet?
    Yes you are right It's now fixed

    Thanks Jack
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  18. #393
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Quote Originally Posted by Nol View Post
    Basically the same as an idle load switch in a way. Just a way to connect high and low with little to no restriction. Plumb it into the expansion tank and let the restriction between there and system to equalize and then close the valve once compressors going.
    Adam... Yep you got it!
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  19. #394
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    R290 is insanely easy to get in decently high purity. Hop to homedepot, blue bottles from bernzomatic, like $2 a pop. Then pickup a $10 propane soldering/brazing torch, cut off the end of the torch, and braze an access valve to the bottle attachment side. Tada R290


    If you have a cooling question or concern feel free to contact me.

  20. #395
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Quote Originally Posted by Nol View Post
    R290 is insanely easy to get in decently high purity. Hop to homedepot, blue bottles from bernzomatic, like $2 a pop. Then pickup a $10 propane soldering/brazing torch, cut off the end of the torch, and braze an access valve to the bottle attachment side. Tada R290
    Great idea! And so simple.

    How pure do you think it is?
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  21. #396
    Xtreme Enthusiast
    Join Date
    Jul 2004
    Location
    The Netherlands
    Posts
    985
    Quote Originally Posted by mytekcontrols View Post
    I figure opening a solenoid valve between the compressor discharge line and the expansion tank for maybe the first few seconds would probably do it.
    I know that with huge ammonia chillers they use pretty much the same thing.
    There's a pipe going from the the top of oil separator the the suctionline, just before the compressor. That pipe has a valve which opens for 1,5 minutes after start-up. After the 1,5 minutes the compressor has reached enough rpm to overcome the static charge.

  22. #397
    Xtreme Member
    Join Date
    Jul 2005
    Location
    Austria
    Posts
    428
    Technical Propane has got a purity of 95%.
    The 5% are unknown, other HCs, Water.

    I can tell you for Propane 2.5:
    Purity 99.5%
    O2 max. 100 vpm
    CO + CO2 max. 10 vpm
    H2O max. 12 vpm
    KW C1,C2,C4 max. 0,7 Vol%

  23. #398
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Bernzomatic is 97.5% according to them, other stuff is HC's and air in small quantities. Run through a filter on the way in. I use that and its more then pure enough to run full singles and cascades on 290 only.


    If you have a cooling question or concern feel free to contact me.

  24. #399
    I am Xtreme
    Join Date
    Mar 2005
    Posts
    4,849
    Quote Originally Posted by n00b 0f l337 View Post
    Bernzomatic is 97.5% according to them, other stuff is HC's and air in small quantities. Run through a filter on the way in. I use that and its more then pure enough to run full singles and cascades on 290 only.

    How about a explanation of the law in the USA of using propane in refrigeration systems..........or pure HC's. It's actually illegal to modify(say a torch) to use it other than for it's intended purpose.


    Are refrigeration units being designed/built to satisfy all the regulatory bodies,Or are potential bombs being built.

    Even systems designed with every safety precaution possible/thinkable occasionally things still go boom "$hit happens" doesn't get you a "Get out of jail free card".

    I don't know......... Once you start selling/shipping units you just opened yourself up to exposure from all government regulations.


    What do you guy's Think ??????
    Last edited by wdrzal; 04-09-2008 at 01:03 PM.
    The Laws of Thermodynamics say:

    Zeroth Law: "You must play the game."
    First Law: "You can't win."
    Second Law: "You can't break even."
    Third Law: "You can't quit the game."

    Do you wanna Play Thermodynamics ???????? I forgot "you must"

  25. #400
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    I never sell units charged with propane Walt. Don't be jabbing at me. What do you think ethylene is? And no its not illegal to modify tools for other purposes. And from tests, and after seeing window ac's explode (see thread still available to read in first two pages here in vapor phase forum), impinged and "atomized" oil in refrigerants is much more deadly.

    And what about hydrocarbons in other refrigerants? Many have r290 in them. And autocascades, mytek would you like to explain the legality of using butane? I don't see a problem.
    Last edited by n00b 0f l337; 04-09-2008 at 01:08 PM.


    If you have a cooling question or concern feel free to contact me.