Although I have presented several schemes along this theme, my answer would be NO!
The reason being; you'll be sacrificing thermodynamic efficiency in the process. It is always better to design with the best possible phase separation, heat transfer, and minimal pressure drop. If you have to resort to partial phase separators to get your system to work properly, then you're probably sacrificing efficiency in doing so.
Of course sometimes due to the refrigerants that are available (or not available), you are left with no choice. So because of this, I think it is still important to cover the topic of partial phase separators, but it is also just as important to try to design without relying them.
2 Attachment(s)
AC-2 Electrical w/Buffer Valve Circuit
I received the high pressure switch yesterday (see photo below). It looks like it'll do the job just fine, and as it turns out, has the correct switch logic (Close on Pressure Rise). The Ranco Part Number is: 010-2054, and it is called a Condenser Fan Cycling Control. Range: 100 to 400 psig, Differential: 40 to 150 psig.
I will most likely leave the differential setting at 40 psig (default), and set the cut-in to 350 psig.
Need small reliable suction pressure gauge...
I have almost completed all the plumbing changes required for the Buffer Valve addition, and have also fabricated, and installed an access port manifold.
My problem is that the pressure gauges I was using are basically cr_p!!! The readings were off by 10 psi from when I had initially calibrated them. What I need is at least one reliable gauge (suction side) that is fairly small, and can be easily panel mounted. Anybody got a good source? :shrug:
P.S. I'll be posting some pictures of the plumbing changes momentarily (need to switch computers).
1 Attachment(s)
Access Port Manifold Drawing
Here is a drawing showing the construction details of the Access Port Manifold (Dimensions are in INCHES --- all holes are aligned to horizontal CenterLine):