A Comparison: AC-2 vs. Polycold P-75
This pic shows a very good physical comparison of a commercially made product (Polycold P-75), and what can be done with a Home Depot purchased AC unit. Now obviously the P-75 is missing its panels, but if nothing else, it shows the tremendous reduction in size that was achieved (not to mention, 1/2 the power consumption).
1 Attachment(s)
AC-2 Under High Vacuum (10-6 Torr range)
Here are my results with the AC-2 unit under actual operating conditions at High Vac (approximately 2x10-6 Torr).
- Comp Suction Pressure = 26 psig
- Comp Discharge Pressure = 148 psig
- Comp Discharge Temperature = 67.1C
- Condenser Air Temperature = 21.8C
- Compressor Suction Temperature = 0.5C
- Veeco MS-17 Cold Probe = -139.6C
I had to boost up the refrigerant charge to completely work the cold probe (forgot about radiant heat load coming from the walls of the cold probe vacuum chamber). Here is my estimate of the present charge:
- 7oz R123
- 4oz R22
- 85psi R170
- 85psi R14
- 45psi Argon
The 1oz boost in the R22 really helped to make a better connection between the low and the high stages of the autocascade, and can also be seen in the moderate pressures, even though more gases were added.
If I get a chance I'll try to do a complete recharge with this new charge to verify repeatability under the same conditions. Judging by the compressor pressures, it appears that there may still be room for more Argon and even lower temps.
1 Attachment(s)
AC-3 (AKA CryoBUG) HXC Stack
Although I can't reveal the exact details on this project, never the less I thought you guys might like to see my new Heat Exchanger Stack aimed at producing -150C or colder.
The photo below shows the "layered" approach being used in this latest autocascade design, yielding over all dimensions of 10.5" high x 6.5" footprint. And of course there are all kinds of goodies stuffed down the center (no wasted space in this baby :up:).
Outer coil is 5/16" od inside of 1/2" od, inner coils are 3/16" od inside of 3/8" od.
The inner coil is broken in a few spots for insertion of tees (not visible -- on back side), and was wound in one operation following brazing of these parts.
The bullet strainer shown, is feeding both the final and subcooler captubes (yes the final part of the 3/8" coil winding is the subcooler).
3 Attachment(s)
AC3 (aka CryoBUG): Preliminary Assembly Has Begun
My Base Pan arrived late last week, so I have begun the initial assembly phase.
Below are a few images of some of the main components bolted in place, and the De-Superheater/HXC connected between the compressor discharge and the condenser (I call this my Regenerative HXC, it'll be used to create an oil free Hot Gas source for Defrost).
The HXC Stack is just sitting on the base pan to show its basic area of residence, although in the final process it will be insulated from the pan.
The frame and HXC Stack insulation box utilize what is called T-Slot framing members for the main structural supports. The final assembly will use polycarbonate plastic sheets slid into the T-Slot channels, to create a box around the HXC Stack. And there will be aluminum panels bolted around the outer perimeter to form the unit's enclosure.