more low voltage TEC numbers
Ferrotec has some nice on-line curves and you can adjust to compensate for hot side temperature. I've been looking at their 9506/031/600 B which is 03160 spec.
The coefficient of performance (COP) is the amount of heat pumping divided by the amount of supplied electrical power. Max CoP for this unit at 30C hot side is 3.3, and occurs at 7.5A and .6V for a 10C differential. For only 4.5W in, it moves about 15W, which is mighty fine efficiency (but not much cooling).
That's a 55mm size, at a nice fat 4.85mm height. Efficiency drops pretty fast as current goes up, with the 50% point (CoP of 1) at 37.5A with 2.3V required, which draws 86.25W to move 86.25W.
Going to the 2.5 CoP point (15A 1V) moves 37.5W across a 10C differential at 30C hot side. So 5 of those on a 5V supply draws 75W and moves 180W. Using 5 of these with 12V PCM control and a 200W cooling design center, we draw 90W on average, and can move 450W at 12V with a total power in of about 480W. That would probably do the job for keeping even a big OC system with dual graphics nice and cool, and with good efficiency (most of the time)... but at max cooling, the hot side cooling needs to unload the power in and the power moved, close to 1000W. Need a big pump and big rad to handle that. But if we are willing to let the cold side rad do some of the cooling, which means we have to let the outlet temp rise a few degrees, we might decide to clamp PCM at the 1.5 CoP, which provides 350W of cooling for 230W in, and a total heat load of under 600W at max load. That setup does not seem totally crazy - it would maintain below ambient for all but the highest loads, and even then would only go a few degrees above ambient.
For the totally freeze crazy, with a big enough cold side setup, you could run 2 sets of 4 of these on a 12V supply. If you can keep the hot side at 40C, you can drive the cold side close to 0C while moving 360W. You will need to unload close to 1500W, but hey, formula 1 is about performance, not cost...
The graphs are fun to play with - for this TEC they are at http://www.ferrotec.com/products/the...ail.php?id=119
power curves for your TECs
Quote:
Originally Posted by
Scarlet Infidel
Just looked at those graphs, quite interesting. Its a shame none of the models they have match the ones I'm using.
What I'm interested in, is the massive spike in COP at around 1/8 of Imax. Though there's a huge disadvantage of running any lower than this magic point.
Also, at this point you'd only be pumping around 10w per element (on the type of element I'm looking at) so perhaps a slightly higher current is better in that respect (though still at the peak).
For the closest element to mine, for 20w movement at dT of 10c it will require 7w of power. This is a COP of 2.85 with a hot side of around 33c with cheap air cooling.
As I have 10 peltier modules, I'm looking at cooling 200w load with 70w power to ambient (of course this is best case, there are all the thermal interfaces etc). This seems to match nicely to my previous calculations and real world tests.
I think you said you have 12709's - you can take the 12712 curves at http://www.ferrotec.com/products/the...ail.php?id=115 and derate by 25% to get an idea of where you should go. You can do a quick double check looking at 12708 and 12710 curves, you should be right in the middle but unfortunately the nice ferrotec calculator doesn't have those values and the thermal enterprises curves are harder to read.
If your hot side is 35C, you have more options for low voltage. You can't achieve better than 2.0 CoP with a differential over 15C.
If the small sinks you describe are kind of 'OEM Standard' solid aluminum, they probably have .7 to .8 C/W rating. So using your numbers, you would be throwing off 27W per element, and would see around a 20C rise. If the sinks are a little better, like a decent sized copper base aluminum fin, you might get .4 C/W, which gets down to the 10C differential level.
Let's look at the 3.0 and 2.0 CoP points. For your units, the 3.0 point puts you at about 1.8A, which with 10C differential and 35C hot side puts you at about 3.7V per unit, pumping about 20W for 6.6W in. That's similar to what you were thinking. You coulkd do 3 groups of 3 in series off of a 12V supply and hit the voltage pretty well.
If you go to the 2.0 CoP, you need a pretty efficient sink - you can't do that CoP with over 15C differential. You'll need about 2.6A and 5.1V, pumping about 26.5W for 13.25W in. So efficiency starts to roll off but you get more transfer, and you are at a nice standard voltage. You have to unload about 40W per unit. That would raise your hot side to 15C over ambient with a .4 W/C sink.
Taking the 3.0 CoP and using the series power scheme off 12V, 9 units would move 180W with a total heat load of 243W. If that meets your cooling needs (that would drop a 1GPM flow about .6C), you might be fine.
Taking the 2.0 CoP and running off 5V parallel, 10 units would move 265W which is respectable, with a total heat load of 400W. That would drop a 1GPM flow about 1C, and if your heat in is lower than 265W, you should also be able to achieve some nice low temps.