Just noticed this thread, and I must say it's always a bit amusing when the discussion gets personal and people are called stupid, and the consensus is wrong.
So first of all, you're not going to get a correct opinion on a chiller unless you post in the chiller or phase sections where us phase guys hang out.
Secondly (drum roll please) you CAN move more heat with a chiller than it pulls from the wall! In the refrigeration industry we call it COP (Coefficient of performance) and sometimes EER or SEER in the US (which are goofy, so I'm not going to explain).
COP = Power Moved / Power Consumed = (Watts)/(Watts) i.e. dimensionless
So, as an example the COP of a Danfoss Universal Compressor SC10G (ASHRAE conditions):
@-30C = 0.53
@-20C = 1.02
@-10C = 1.57
@ 0C = 2.16
@ 10C = 2.78
(I'm looking at the datasheet for a Danfoss SC10G 50Hz compressor @ danfoss.uk because they use Watts for both cooling power and electrical power)
@0C, this compressor will move 764 Watts, and consume 353 Watts. It's not creating energy, it's moving it like a pump. It flows into the evap (764 Watts of it) from the water, which of course cools the water down in the process. The condenser then has to reject all of the power as heat (minus comp shell cooling) so ~1000 to 1100 Watts.
Hilarious! that you guys have talked/bullied yourselves into believing that a chiller is a scam! I have no idea about the particular chiller in this discussion, but $400USD is much more than the parts would cost even buying single parts (no volume discounts) from a refrigeration supply store.