Originally Posted by
mytekcontrols
I've attached a diagram that should make it a little clearer as to how the Sub-Cooler works.
Basically it steals a fraction of the condensate passing through it, and evaporates this in the suction side counter-flow to the discharge. Since it is essentially isolated from the return path of the evaporator, it is also isolated from any returning heat. Thus it'll tend to maintain a colder temperature then the evaporator (especially under load), and help to subcool the liquid passing through it. When subcooled, there is a greater tendency for absorption of any non-condensibles passing through as well (Argon or Methane). When this condensate consisting of subcooled refrigerant and absorbed gas is later evaporated, it'll do so at a temperature somewhere between the two refrigerants boiling points. So in other words; Subcooled R14 with absorbed Argon gas will boil colder then R14 alone.
The same should tend to hold true for a combination of R1150 and R14 in your system, assuming that you can obtain temperatures below the boiling point of the R1150 within the Sub-Cooler. On the other hand this would be a mute point if you could already obtain temperatures and pressure to fully condense the R14 in the first place.
I hope that answers your question.