2 modifications.... kind of.
#1. This was a troublesome unit. Local customer brought in not working Mach II GT. Basically he managed to snap off cap tubing and went to local refrigeration guy to get it fixed and has blown what he says 20 fuses after that. Upon inspection, compressor was making racket and further diagnose was needed. I found out the compressor has completely blown it's valve. Cause of it sever overcharge + blocked cap tube.
Compressor was replaced and cap tube was repaired once again and reduced some length of cap tube to accomodate a little more capacity.
Testing at 200w as I have no faith in this evap beyond that...
http://www.vapoli.com/Images/Forum/MachMod/IMG_0216.JPG
#2. Well, another one of reworking of custom built unit. Original unit was encased in v2000 but customer wanted ss case. Also, the tuning was done quite a bit differently than what I would have preferred/customer would have preferred. One thing I noticed was that as builder has mentioned it held the load designated in flying colors (kudos to that, first unit out of 6 builders unit I had to touch that did what it says it did). However, I can't agree on way of tuning with compressor reaching 95c....
I had to take out oil for precaution and it now has new oil in system. It's leak testing ATM and will be insulated, encased, etc when case arrives.
I've put something different again on this thing and hoping to get some good result out of this. I believe the compressor is NF11FX (can't tell with no label and some painting done on it...)
http://www.vapoli.com/Images/Forum/Revisit/IMG_0219.JPG
http://www.vapoli.com/Images/Forum/Revisit/IMG-0221.JPG