    Chiller for positive Temps and no condensation

    hi guys,

    i´ve build a chiller in the past month.

    specs:
    danfoss sc12g
    big condenser around 2,5kw?
    danfoss ten2 r134 txv 01 orifice
    20 plates hx
    10l water reservoir
    carel controller with ntc probes

    500 watts at 0°C to 1°C are possible
    more load at higher temps are no problem for this monster.
    i did some testing. my results:
    water temp between 15°C and 23°C with 250 watts:
    the chiller needs 9 minutes to cool the water down
    and the water needs 21 minutes to warm from 15°C to 23°C

    water temp between 15°C and 23°C with 500 watts:
    the chiller needs 17 minutes to cool the water down
    and the water needs 11 minutes to warm from 15°C to 23°C

    pics:









































  2. #2
    Xtreme Member
    Join Date
    Dec 2007
    Posts
    132
    Looks like German Quality build =)

  3. #3
    Administrator
    Join Date
    Nov 2007
    Location
    Stockton, CA
    Posts
    3,569
    Very nice unit Patrick

    You do very clean well thought out work.

    In your first picture what is the unit in the back ground ?

  4. #4
    Xtreme Addict
    Join Date
    Jul 2007
    Location
    Arizona - USA
    Posts
    2,200
    Looks amazing Patrick. Well done!
    //RETIRED-o00o--°(_)°--o00o-OVERCLOCKER//


  5. #5
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Germany
    Posts
    401
    thanks.
    tha fan of the chiller has a dimmer to make it more silent than the compressor.

    the unit in the back of the first pic was a normal 2 stage cascade with r404a in the 1st and r1150 in the second stage.

  6. #6
    Administrator
    Join Date
    Nov 2007
    Location
    Stockton, CA
    Posts
    3,569
    Quote Originally Posted by Patrickclouds View Post
    normal 2 stage cascade
    Oh just a normal 2 Stage Cascade
    If you made it its far from normal I bet

  7. #7
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Germany
    Posts
    401
    i did another load test today.

    this time i used a stronger waterpump.

    with 500watts it was possible to achieve "water" temp of -5°C

    then i tested with 750watts and achieved +4,5°C

  8. #8
    -100c Club
    Join Date
    Jun 2005
    Location
    Slovenia, Europe
    Posts
    2,283
    Great stuff Patrick!

    Personally I'd go for R-507, it's possible to achieve around 1kW at 0°C - condensation issues aside - as I did with my chiller build.