Been awhile, but have been busy, cutting, changing captubes, I think I learnt some aspects of the influence the cap tube has. Also changed some pipe work, some for better and some I need to change Lp take off freezes the guage.
Anyway a few pics then the test data. Managed a 10minute plus at 270watt and held at -22C so it looks like were now going in the right direction
Captube .09mm length approx 3.5mt
Static 7barg, Ambient 9C
Started up and ran idle for 5minutes:
SH= -32.5C, temp measured 6” from bulb (not sure if this is sh but people measure this).
Evap = -40.5C
Pipe = -42.5C (this the suction pipe 20mm from evap)
HP = 9 barg
LP = .2barg
Loaded heat loader to 180watt
Temps took every minute for ten minutes: temps are negative unless preceded with a +
1 =31.0
2 = 29.8
3 = 30.8 HP 10barg, LP .4barg
4 = 30.6
5 = 31.3
6 = 30.4 ( SH= 31.2c)
7 = 27.7 HP 10barg LP .6barg
8 = 26.8
9 = 26.4
10 = 26.4
End of test readings: HP=10bg, LP=.6bg,SH=29.2C, Pipe=33.3C
Bulb completely frosted.
Turned up load to 235watt:
1 =25.1
2 = 24.7
3 = 24.3
4 = 24.2 HP 11barg, LP .7barg
5 = 23.9
6 = 23.9
7 = 24.0
8 = 24.0
9 = 23.9
10 = 24.0
End of test readings: HP=11barg, LP=.8barg, SH=26.1C, Pipe =31.6C
Bulb still completely frosted.
Having got through this test decided to go full load 275Watts
1 = 23.6
2 = 22.7
3 = 22.5
4 = 22.8
5 = 22.4
6 = 22.8
7 = 22.5
8 = 22.5
9 = 22.5
10 = 22.5
End of test readings: HP=11barg, LP=.8barg, SH=25.1C, Pipe =31.4C
Bulb still completely frosted.
Some questions:
The HP seems low compared to pics seen here, I will add more captube to give more vacuum then add more gas, ? more HP.
Superheat, I understand how it works with steam! But not with refrigeration, could some explain with the figures above if possible, I read that superheat needs to be 4 – 12c how/ why and where.
Await your comments, and thanks for the help.