Refilling R600a fridge (Urgent).
hello
That was topic about filling A/C in car but I didn't find anything about refilling fridge .
So I must refill R600a fridge made by Whirpool, looking like this : (it's fridge/freezer) :
I have R600a . Shrader is already brazed to suction port . On label there is 0.054kg of gas wrote . What suction pressure should have freezer when it's tunned properly ? What are other factors saying that fridge is tunned well ?
That's bit urgent ..today evening I must refill it
Thanks for all help !
Regards
|
|
|
10-19-2009, 03:55 AM
|
#2
|
|
Xtreme Addict
Join Date: Oct 2005
Location: England, Northwest
Posts: 1,016
|
Can you not just weigh the gas in ?
__________________
|
|
|
10-19-2009, 05:25 AM
|
#3
|
|
-100c Club
Join Date: Jun 2005
Location: Slovenia, Europe
Posts: 1,399
|
Borrow a 2000g 1g scale laboratory grade weight (cheap, around 20-30€), place the container with R600a on it, calibrate it to 0 and charge to -54g.
|
|
|
10-19-2009, 05:55 AM
|
#4
|
|
Xtreme Member
Join Date: Jul 2008
Location: Poland
Posts: 297
|
Even standard electronic kitchen scale will do the job. My is up to 5kg, 1g step.
|
|
|
10-19-2009, 06:00 AM
|
#5
|
|
-100c Club Member
Join Date: Mar 2005
Location: Poland
Posts: 1,096
|
I don't have any electronic weight, plus not all refrigerant is out of system (frigde have very tiny leak, gas leaks throught 4 years to stop working of fridge) . So I must find another way of tuning it..
|
|
|
10-19-2009, 06:42 AM
|
#6
|
|
Registered User
Join Date: Oct 2006
Location: Germany
Posts: 65
|
did you thought about that R600a is flammable/ explosive? Just Refilling is bad way, maybe leak is on suction side. Those freezers are at low suchtion pressure/ maybe in vacuum and O2 can get in system  .
Getting this system leak free, testing with nitrogen and then a good vacuumpump is required. But when leak is in evaporator, you simply throw it away
|
|
|
10-19-2009, 08:31 AM
|
#7
|
|
-100c Club Member
Join Date: Mar 2005
Location: Poland
Posts: 1,096
|
OK I know August, but can You tell me way how to refill it without having weight ?
|
|
|
10-19-2009, 09:39 AM
|
#8
|
|
Xtreme Enthusiast
Join Date: Feb 2007
Location: London ont. Canada
Posts: 729
|
just do it the same as one of the single stages we build. there should be a 4c to 12c superheat but subcooling will be different if it is a static cooled condensor if it is not then just charge the same as a single stage system. this is how i have done fridges before but like august said u should really try and find the leak
|
|
|
10-21-2009, 05:24 PM
|
#9
|
|
-100c Club Member
Join Date: Mar 2005
Location: Poland
Posts: 1,096
|
Finally I rent weight from neighbours (electronic) and put a 54 grams of R600a like sticker says . But that time pulldown time was really slow, and from fridge was comming not nice sounds (hissing, buzzing) ...just like too little refrigerant . So I add 10 grams more and till now all works fine  .
Thanks for help.
|
|
|
10-25-2009, 04:37 AM
|
#10
|
|
-100c Club Member
Join Date: Mar 2005
Location: Poland
Posts: 1,096
|
Hi
After 3 days fridge is out of gas again so I guess leak is not small ...
Till now I've found one small leak :
Can anybody have an idea if I can throw away that piece of alu pipe which is comming inside fridge (I think yes) wall and connect condensor outlet directly to drier ?
Because I don't know in what way I should braze steel to alu, if I throw away that alu I'll connect steel condensor with cooper drier using cooper pipe .
Am I right ?
|
|
|
10-25-2009, 05:14 AM
|
#11
|
|
I am Xtreme
Join Date: Mar 2005
Posts: 4,912
|
The places where you need to remove/repair the aluminum ,use a double flare on the aluminum to reconnect.
__________________
http://xtremespeakfreely.com/forum/
Register today .
The Laws of Thermodynamics say:
Zeroth Law: "You must play the game."
First Law: "You can't win."
Second Law: "You can't break even."
Third Law: "You can't quit the game."
Do you wanna Play Thermodynamics ????????  I forgot "you must"
|
|
|
10-25-2009, 05:51 AM
|
#12
|
|
Registered User
Join Date: Oct 2006
Location: Germany
Posts: 65
|
maybe some sort of slhx inside fridge/freezer?
|
|
|
10-25-2009, 10:39 AM
|
#13
|
|
Registered User
Join Date: Aug 2009
Posts: 17
|
I thinks is not aluminium is a steel juste remake a braid , is not slhx , this tube going under your fridge or in the side is a sort of desuper .... I thinks that you little to connect(bind) the condensseur with the dezydrateur directl (reverso translate sorri ^^ )
Last edited by tanguintel; 10-25-2009 at 10:43 AM.
|
|
|
 |