Compressor starting

Its been colder here in Atlanta lately and I had trouble starting the second compressor on a cascade i use for personal use.

I took a space heater out and warmed the second and first up a bit and it started right up but this has me a little perplexed because it wasnt that cold...maybe 46f -- 8c

Anyone know if this is normal or a symptom of something else.

My compressors are 11k rotaries...
__________________
http://valid.canardpc.com/show_oc.php?id=606830

Seller/Buyer Reputation:
Heatware: http://www.heatware.com/eval.php?id=50905
Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
iTrader: http://www.blazingpc.com/forum/itrader.php?u=28
sdumper is offline   Reply With Quote
Old 10-17-2009, 09:51 AM   #2
sdumper
-100c club
 
sdumper's Avatar
 
Join Date: Aug 2006
Location: Atlanta
Posts: 2,228
I think i have my answer....
I have a high charge in my first stage and a large charge in my second. The second has never been a problem during the summer because of the outside temp and my use of a large Parker tank for expansion. However on colder days like today my refrigerant is accumulating in my compressors because they are acting like heat sinks and this is raising my compressor pressure high enough that it wont be able to crank. So when I heat my compressors the refrigerant is moving out of my compressors lowering the pressure enough to start.


"While the system is running, there is enough heat being generated by the compressor running to keep from creating refrigerant migration from occurring. Refrigerant vapor always migrates to the coldest part of the system (the compressor). The refrigerant migrates to the compressor crankcase where it is attracted to the compressor oil. This refrigerant vapor condenses and will return to a liquid in the off cycle. On the next start of the compressor, the oil is in a watery state and washes the bearings out, which leads to locked up, frozen or totally burnt out compressors.[3] The temperature is sensed at the compressor, indoor coil, and outdoors. The sensed temperatures are compared and if the compressor temperature is not a specified amount higher than the lower of the other two sensed temperatures, then the crankcase heater is energized. When the compressor temperature rises to or is a specified amount above the lower of the other two temperatures, the crankcase heater is deenergized.[6]"




So if im right how do I get around this do i need to add crankcase heaters??
__________________
http://valid.canardpc.com/show_oc.php?id=606830

Seller/Buyer Reputation:
Heatware: http://www.heatware.com/eval.php?id=50905
Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
iTrader: http://www.blazingpc.com/forum/itrader.php?u=28
sdumper is offline   Reply With Quote
Old 10-17-2009, 10:30 AM   #3
MeltedDuron
Dothan FTW!
 
MeltedDuron's Avatar
 
Join Date: Jun 2004
Location: London, England
Posts: 896
Send a message via AIM to MeltedDuron Send a message via MSN to MeltedDuron Send a message via Yahoo to MeltedDuron
Higher rated capaitor maybe due to the high presure and load needed to crank it over. Maybe in the colder month add an electric blanket over the unit when not being used
__________________
.:Melted's Hardware:.

.:My Workstation::Sorta Done:.
.:Intel E4300@3ghz(375*8):2gb G.Skill HZ 6400@500mhz:Sapphire X1950pro:Gigabyte GA-G33M-DS2R:550w FSP Blue Storm:80gb and 160gb WD SATA2:Cheap MATX Case:.

.:Panasonic Toughbook CF-T2:.
.:Pentium M 753 (900mhz ULV):256MB:40GB:12.1" Touchscreen:. .:Not too shabby for a 2.4lbs of pwn:.

I've been using Intel ever since AMD put an end to my socket A fun. I was almost going to go back when I saw the cheap AM2 chips, but they suck Viva La Chipzilla!
MeltedDuron is offline   Reply With Quote
Old 10-17-2009, 10:52 AM   #4
NidStyles
Registered User
 
Join Date: Oct 2008
Posts: 96
Quote:
Originally Posted by sdumper View Post
My compressors are 11k rotaries...
Now I'm not too aware with how cascade's work or anything, but wouldn't you want a larger compressor on the first stage???
NidStyles is offline   Reply With Quote
Old 10-17-2009, 12:26 PM   #5
sdumper
-100c club
 
sdumper's Avatar
 
Join Date: Aug 2006
Location: Atlanta
Posts: 2,228
Quote:
Originally Posted by NidStyles View Post
Now I'm not too aware with how cascade's work or anything, but wouldn't you want a larger compressor on the first stage???
Nope
__________________
http://valid.canardpc.com/show_oc.php?id=606830

Seller/Buyer Reputation:
Heatware: http://www.heatware.com/eval.php?id=50905
Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
iTrader: http://www.blazingpc.com/forum/itrader.php?u=28
sdumper is offline   Reply With Quote
Old 10-19-2009, 06:17 PM   #6
sdumper
-100c club
 
sdumper's Avatar
 
Join Date: Aug 2006
Location: Atlanta
Posts: 2,228
Quote:
Originally Posted by sdumper View Post
I think i have my answer....
I have a high charge in my first stage and a large charge in my second. The second has never been a problem during the summer because of the outside temp and my use of a large Parker tank for expansion. However on colder days like today my refrigerant is accumulating in my compressors because they are acting like heat sinks and this is raising my compressor pressure high enough that it wont be able to crank. So when I heat my compressors the refrigerant is moving out of my compressors lowering the pressure enough to start.


"While the system is running, there is enough heat being generated by the compressor running to keep from creating refrigerant migration from occurring. Refrigerant vapor always migrates to the coldest part of the system (the compressor). The refrigerant migrates to the compressor crankcase where it is attracted to the compressor oil. This refrigerant vapor condenses and will return to a liquid in the off cycle. On the next start of the compressor, the oil is in a watery state and washes the bearings out, which leads to locked up, frozen or totally burnt out compressors.[3] The temperature is sensed at the compressor, indoor coil, and outdoors. The sensed temperatures are compared and if the compressor temperature is not a specified amount higher than the lower of the other two sensed temperatures, then the crankcase heater is energized. When the compressor temperature rises to or is a specified amount above the lower of the other two temperatures, the crankcase heater is deenergized.[6]"




So if im right how do I get around this do i need to add crankcase heaters??

Bump...

Chilly you around tonight?
__________________
http://valid.canardpc.com/show_oc.php?id=606830

Seller/Buyer Reputation:
Heatware: http://www.heatware.com/eval.php?id=50905
Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
iTrader: http://www.blazingpc.com/forum/itrader.php?u=28
sdumper is offline   Reply With Quote
Old 10-19-2009, 09:38 PM   #7
n00b 0f l337
I am Xtreme
 
n00b 0f l337's Avatar
 
Join Date: May 2005
Location: NJ
Posts: 9,734
Send a message via MSN to n00b 0f l337
Crankcase heaters are for scroll compressors.
I'm not sure whats occuring in your case, however when it's cold in that sense its refering to outside condensing units where it is colder. In your case it's across the entire system, and thus simply you have liquid occuring at the lowest points. This may be the compressor, or it may not be. However are your compressors meant to be using start capacitors? Or is there an option for start capacitors? Some rotarys require this.
__________________

Quote:
NoL: gom gom gom
Gomeler: om nom nom nom
n00b 0f l337 is offline   Reply With Quote
Old 10-20-2009, 02:36 AM   #8
barbus
Registered User
 
Join Date: Jun 2008
Location: Inside a drier
Posts: 21
Actually, crank heaters are not just for scrolls.

I have this problem with some outside condensing units, it's usually caused by liquid migrating to the coldest place, and in this instance it sounds like the comp.
I'd ad a crank heater and see how it goes.
__________________

Go placidly amid the noise and the haste, and remember what peace there may be in silence.

Avoid loud and aggressive persons, they are vexatious to the spirit.

With all its sham, drudgery, and broken dreams, it is still a beautiful world.

Be cheerful. Strive to be happy.

barbus is offline   Reply With Quote
Old 10-20-2009, 06:57 AM   #9
sdumper
-100c club
 
sdumper's Avatar
 
Join Date: Aug 2006
Location: Atlanta
Posts: 2,228
Quote:
Originally Posted by barbus View Post
Actually, crank heaters are not just for scrolls.

I have this problem with some outside condensing units, it's usually caused by liquid migrating to the coldest place, and in this instance it sounds like the comp.
I'd ad a crank heater and see how it goes.
Thanks ill give it a try and also check to see if a start cap is an option.
__________________
http://valid.canardpc.com/show_oc.php?id=606830

Seller/Buyer Reputation:
Heatware: http://www.heatware.com/eval.php?id=50905
Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
iTrader: http://www.blazingpc.com/forum/itrader.php?u=28
sdumper is offline   Reply With Quote
Reply

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -8. The time now is 03:38 PM.


Powered by vBulletin® Version 3.7.6
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
XtremeSystems