Attempting to automate something and I want to divert refrigerant flow from one pipe to another occasionally. Basically I want a normally closed and a normally open solenoid setup where the flow goes from point A to B when de-energized and when energized goes from point A to C. This is what a 3 way solenoid does, correct?
If so why for the life of me can I not find any HVAC rated 3 way solenoid valves? They all are rated for air up to 150psi or water/oil up to 60psi. Going to hit up United Refrigeration tomorrow but hoping to find one online. Do they go by another name in the industry and I'm just missing it?
__________________
Team PURE is about kickass pirates and unicorns defeating ninjas.
When is off: A->B and C->D and when is on: A->D and B->C, easier to show it in paint brush if you want
I bet there are guys with disassembled aircons that have this type of valve laying around
Your additional option is to use a NO solenoid with a relay in front of it to invert the voltage logic.
Yup thought about that also, more money and adding complexity Thanks for thinking about the problem though. Going to talk to the United Refrigeration guys when they open this morning and see if they have a compact solution for me.
__________________
Team PURE is about kickass pirates and unicorns defeating ninjas.
why are u going to use a 3 way solenoid. and for wat purpose.
In a build I am creating I would like to temporarily divert the refrigerant flow from the evaporator and send the refrigerant to another heat exchanger. I want to use this in conjunction with a PID temperature controller to control evaporator temperatures.
__________________
Team PURE is about kickass pirates and unicorns defeating ninjas.
Use a standard reversing valve,,, ranco makes them for about $100 USD you can get coils for the pilot valve in ac and dc voltages from 24 to 460V usually used in heatpumps for swiching the evaporator from inside to outside
Use a standard reversing valve,,, ranco makes them for about $100 USD you can get coils for the pilot valve in ac and dc voltages from 24 to 460V usually used in heatpumps for swiching the evaporator from inside to outside
Use a standard reversing valve,,, ranco makes them for about $100 USD you can get coils for the pilot valve in ac and dc voltages from 24 to 460V usually used in heatpumps for swiching the evaporator from inside to outside
Ditto: Easiest way to do it.
__________________
Quote:
Quoted from SoddemFX:
"I frankly have no idea what you are trying to do. I have received more comprehensible correspondence from Mr Obuwonga Mwahahu, who i believe wishes to give me a 10% share of his $12M fortune held in the royal bank of Nigeria."
So just use the reversing valve and use the two coil ports and cap the suction port. Reading up on them it appears they are made of nylon, I hope I don't get massive leaks between the two ports when the valve is subjected to -70C or so. I'll grab one from ebay to play with, thanks guys!
__________________
Team PURE is about kickass pirates and unicorns defeating ninjas.