Originally Posted by
wdrzal
in a single stage there is about 1/8 to 1/4 cubic foot of internal volume ,Im just guesing I didn't do the calculations, but a 1 cfm pump would lower the pressure in about 15 to 45 seconds.. you just need to lower the pressure and KEEP it there and let it pump until all the moisture is removed. I use a 6 cfm pump on systems from 250,000 to 500,000 btu's and it does just fine .do you really think you need a 6 cfm for 600 btu's., NOT. its the pumps abilty to reach and maintain a low micron readind that is important.
want to add on these small systems a 10cfm pump won't evacuate a system any faster than a 1 cfm. What is important is to remove restrictions as that pressure loss is critical at very low pressures. Use the largest diameter hose of the shortest length for dehydrating.I all ways remove the valve core also ,that is a major restriction that lengthens evac times substantully.