    Quote Originally Posted by Unknown_road View Post
    6 feet is short in comparison to what? a 0.031" cap with r507?

    I don't think 8 feet will be able to hold the load anymore. but maybe start with 8 feet and work down from there.
    I agree with this, 240cm (8ft) is close to a good length of 0.028" when you use R507a or R402a. R290 likes it a little shorter. I would guess around 200cm of 0.028 would be pretty close to what will be ideal for you but to be safe you can start at around 240cm abd work your way down.

    As said before, it also depends on the compressor and evap you use, my guess is based on usage of a NL11F (220v) or NF9FX (110v)

  2. #152
    Xtreme Cruncher
    Join Date
    May 2007
    Location
    In a hell hole called Sac
    Posts
    1,754
    Can I go shorter since I'm running an accumulator?

  3. #153
    Registered User
    Join Date
    Feb 2007
    Location
    Finland, Sln
    Posts
    83
    Any idea how long captubes i need, first stage and second? Tube size is 0,79mm.

    Cascade with two 1hp rotary`s. First stage maybe r402 or r410a and second etylen.
    Töttörööö

  4. #154
    Xtreme Enthusiast
    Join Date
    Aug 2006
    Location
    Stockholm, Sweden
    Posts
    701
    for first stage you could use a tvx if you want 'cause the load is pretty stabile and big enough.

    otherwise I would start with 2,5-2,7meters of captube in both stages, maybe a little longer in second.

  5. #155
    Registered User
    Join Date
    Feb 2007
    Location
    Finland, Sln
    Posts
    83
    Hmm.. i have one Danfoss TX2 but it is only -40c and r22
    Töttörööö

  6. #156
    Xtreme Cruncher
    Join Date
    May 2007
    Location
    In a hell hole called Sac
    Posts
    1,754
    Ok again. Can I go shorter since I'm running an accumulator?

  7. #157
    Xtreme Addict
    Join Date
    Aug 2003
    Location
    Buenos Aires, Argentina
    Posts
    1,603
    Quote Originally Posted by 2long4u View Post
    Ok again. Can I go shorter since I'm running an accumulator?
    Yes you can
    Start making your own field experiences man.

  8. #158
    Xtreme Enthusiast
    Join Date
    Feb 2004
    Location
    Netherlands
    Posts
    757
    doesn't help efficiency though

  9. #159
    Xtreme Member
    Join Date
    Jul 2005
    Posts
    122
    Ok, can someone tell me why or if it would be bad to go with a shorter cap tube than needed? Seems like you have more head room the shorter your cap tube is (to a certain extent of course). I am thinking of starting a vap phase system this summer and having one of my buddy's dad charge it for me with whatever refrig is needed for my setup(evap going on either GPU or CPU)... would love to build a dual head until but that might be a bit hard for a first build.

    Thanks!!
    Gautam: "I like the black one... its 4" longer too... but its not 'high performance"
    Mobo------------Asus Commando
    CPU-------------L628B121-E6600(Apogee GTX)@ 505x8@ 1.53V Actual (Still Testing)
    Vid--------------BBA ATI X1900XTX @ 765/900@ 1.550/2.217 volts (Swiftech MCW60)
    Ram----------- 2x1024 OCZ PC2-8500
    HDD------------74GB Raptor, 2 320GB 7200.10's Matrix Raid
    Optical--------- DVDRW's- Dual Lite-On LH-20A1S
    PSU------------ Thermaltake Toughpower 1200W
    Water Cooling- PA120.2 & PA120.3 (San Ace fans), Dual DDC2's with Petra tops, 7/16" lines
    Benchies
    PCMark05: 9420 3DMark06: 7751 3DMark05: 13203 3DMark 03: 26301 SuperPi: 12.782


    Project: Clean Overkill

  10. #160
    Xtreme Enthusiast
    Join Date
    Jul 2003
    Location
    Rio de Janeiro - Brazil
    Posts
    910
    i have found a good article about refrigeration, also cap tube measures. Unfortunately it is in portuguese, but altavista can be your friend :
    http://www.trocalor.com.br/apostilas/rac_01.zip
    page 84.
    regards.
    Last edited by Marvin; 05-22-2007 at 06:42 PM.
    Q9550 EO @ 4.1
    Asus P5Q Deluxe
    4 Gb DDR2 Gskill
    2xVelociraptors 300 gb Raid 0
    Sapphire Vapor 4870 1Gb
    PCP&C 750w silencer psu

  11. #161
    Registered User
    Join Date
    Jul 2007
    Posts
    21
    First off, Great read, lots of information here. I appreciate it all

    secondly...
    Quote Originally Posted by Eightballrj View Post
    Ok, can someone tell me why or if it would be bad to go with a shorter cap tube than needed? Seems like you have more head room the shorter your cap tube is (to a certain extent of course). I am thinking of starting a vap phase system this summer and having one of my buddy's dad charge it for me with whatever refrig is needed for my setup(evap going on either GPU or CPU)... would love to build a dual head until but that might be a bit hard for a first build.

    Thanks!!
    I'm guessing it's because it's easier to make a captube shorter than longer.

    Thanks!

  12. #162
    Diablo 3! Who's Excited?
    Join Date
    May 2005
    Location
    Boulder, Colorado
    Posts
    9,412
    Yup, trimming is a breeze, splicing.. yuck

  13. #163
    Xtreme Enthusiast
    Join Date
    Feb 2007
    Location
    London ont. Canada
    Posts
    735
    so i was reading this over and if you had 10 foot of 0.028 for a 150 watt load on r404a/r507
    and if you are to get a increase of 15 watts for every foot you remove then to get 300 watts would you not have to remove all the cap tube by this rule

  14. #164
    Xtreme Mentor
    Join Date
    Feb 2007
    Location
    Victoria, British Colombia
    Posts
    2,677
    Quote Originally Posted by ruffus View Post
    so i was reading this over and if you had 10 foot of 0.028 for a 150 watt load on r404a/r507
    and if you are to get a increase of 15 watts for every foot you remove then to get 300 watts would you not have to remove all the cap tube by this rule
    which means that you shouldn't use .028 for 300 watt load eh?

    that is funnyt hough
    mentally confused and prone to wandering

  15. #165
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Its not really an accurate rule, the best way is to simply try something from someone else, then tune around that.


    If you have a cooling question or concern feel free to contact me.

  16. #166
    Xtreme Enthusiast
    Join Date
    Feb 2007
    Location
    London ont. Canada
    Posts
    735
    i use 0.031 but i seen this rule and seen this problem and thought i might say something about it

  17. #167
    Registered User
    Join Date
    Jul 2007
    Location
    California
    Posts
    49
    So I have 10 feet of .052 cap tube laying around... I am planning on about 150w load. Any way I can make this work?


    Current System Specs:

    E5300-R0 @ 4013 Mhz (321x12.5) w/ Scythe Mugen II Cooler
    ASUS p5b Deluxe
    4 x 1gb Corsair DDR2-800 4-4-4-12
    BFG GeForce 8800 GT OC2 Edition @ 742/1728/999 w/ Accelero S1
    Sony AW-G170A (Reflashed to Optiarc 7170A)
    Thermaltake V3 Case
    Enermax Liberty 500w PSU
    2xWD160ABYS, WD2502ABYS, WD3200YS and ST3400620A

    New toy, Q6600 on the way.

  18. #168
    Xtreme Enthusiast
    Join Date
    Jun 2006
    Location
    Near CeBIT-City Hannover
    Posts
    650
    Nope. Captube is cheap, buy .031 tube
    Quote Originally Posted by Xeon th MG Pony View Post
    ....and avoid being a total venting loser!

  19. #169
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    bump
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  20. #170
    Xtreme Member
    Join Date
    Oct 2010
    Location
    Southern California
    Posts
    143
    I'm not sure where I came across this article from Supco but a method is described using a balance gauge to determine if the cap tube length is sufficient of a restriction or not simply running the compressor on filtered air for just a few minutes to test, which can be done prior to charging..

    http://www.supco.com/images/pdfs/Man...g%20Manual.pdf


    I think there may be a few things wrong with the theory for our needs but what do I know, like we're testing and adjusting the cap tube with air which has very different flow characteristics then a fluid, a cold one at that! But I'm wondering if it's worth a shot?? Any ideas?
    Last edited by Ian[Frozen]; 02-03-2011 at 11:31 PM.
    My Apple is a Lemon

  21. #171
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    That was one of the few awesome articles I've read in a while. Quite good and a hand off to supco.


    If you have a cooling question or concern feel free to contact me.

  22. #172
    Xtreme Member
    Join Date
    Oct 2010
    Location
    Southern California
    Posts
    143
    I'm glad it was a worthwhile read, wasn't sure how it applies in our scenario. I'm wondering if we could use a vacuum gauge instead of a flow meter??