    Cap tube sizing rule

    I would like to propose a rule for sizing cap tubes (single stage systems). Based on what I have been seeing in the forums, I would propose the following:

    For R404A/R507:

    Using a center point of 150 watts load I would guestimate 10 feet (3 M) of .028 inch (.7 mm) cap tube.

    For each increase of 15 watts, I would shorten the cap tube by 1 foot (30 cm).

    For each decrease of 15 watts, I would lengthen the cap tube by 1 foot (30 cm).

    Then for R22/R290 (propane) shorten 1 foot (30 cm).

    For .026 cap tube, multiply by .7.

    For .031 cap tube, multiply by 1.6.

    It is best to stay between 5 feet (1.5 M) and 16 feet (5 M), with center range of 10 feet (3 M) being ideal.

    Does this sound about right?


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  2. #2
    Xtreme Enthusiast
    Join Date
    Aug 2003
    Location
    Netherlands
    Posts
    507
    MOOOOODDDDD ?!?!?!

    Please make this one a sticky
    Pifast:
    Socket 754 3700+ Clawhammer action:
    39.64sec 11*285 2.5-3-3-7
    Now Pifast @ 3306MHZ !!! 37.72sec World record!
    Now SuperPi 1M @ 3306mhz 26.922sec World record!

    Ministry of Overclocking Contests

  3. #3
    Xtreme Member
    Join Date
    Oct 2003
    Location
    The Netherlands
    Posts
    472
    Hoho, let Bowman and the others say that the old man is right

  4. #4
    Xtreme Enthusiast
    Join Date
    Aug 2003
    Location
    Netherlands
    Posts
    507
    Yeah well

    Whether or not it is true, the correct "rules" will be posted in this topic anyway. So a sticky wouldn't hurt


    btw, just mounted my 172w pelt on a GF2 dangerden block. Home made coldplate and insulation ofcourse. Pics will be online soon (as soon i can get some1 to take pics :P)
    Pifast:
    Socket 754 3700+ Clawhammer action:
    39.64sec 11*285 2.5-3-3-7
    Now Pifast @ 3306MHZ !!! 37.72sec World record!
    Now SuperPi 1M @ 3306mhz 26.922sec World record!

    Ministry of Overclocking Contests

  5. #5
    Xtreme Addict
    Join Date
    Aug 2002
    Location
    Melbourne Aus
    Posts
    1,219
    Does anyone know the exact length of the Mach I and Mach II capillary tube length?

  6. #6
    Xtreme Enthusiast
    Join Date
    Jan 2003
    Location
    USA
    Posts
    733
    this definitely needs to become a sticky -- right now you have to dig thru a ton of threads to find the info on cap tube sizing for different refrigerants and different cap tubes.

    on the one for R22, I think that is damn close to being right - I am still tweaking my latest R22 .028 direct die system but those numbers are looking pretty close to what I expect to end up using for it...

    great thread gary
    Counting bodies like sheep to the rhythm of the war drums.
    go to sleep
    go to sleep
    go back to sleep.

    carpe noctem.

  7. #7
    Registered User
    Join Date
    Jan 2004
    Location
    Boernicke, Germany (right now Darwin Australia)
    Posts
    11
    Yeah great topic to pick up Garry!
    It's always a very welcomed issue I believe. Would be nice to just use your rules to adjust captube length without having to annoy others for their help!
    I feel the Minute of Decay!

  8. #8
    Xtreme Member
    Join Date
    Oct 2003
    Posts
    165
    Wise words from a wise man.
    But i still want my expansion-valve. ( THX ?? )
    Fooled death 13 august 2006

  9. #9
    HVAC/R Engineer
    Join Date
    Nov 2003
    Posts
    3,565

    Re: Cap tube sizing rule

    Originally posted by Gary Lloyd
    I would like to propose a rule for sizing cap tubes (single stage systems). Based on what I have been seeing in the forums, I would propose the following:

    For R404A/R507:

    Using a center point of 150 watts load I would guestimate 10 feet (3 M) of .028 inch (.7 mm) cap tube.

    For each increase of 15 watts, I would shorten the cap tube by 1 foot (30 cm).

    For each decrease of 15 watts, I would lengthen the cap tube by 1 foot (30 cm).

    Then for R22/R290 (propane) shorten 1 foot (30 cm).

    For .026 cap tube, multiply by .7.


    For .031 cap tube, multiply by 1.6.

    It is best to stay between 5 feet (1.5 M) and 16 feet (5 M), with center range of 10 feet (3 M) being ideal.

    Does this sound about right?
    Simply stated this is true...

  10. #10
    XIP - can sit on his hair
    Join Date
    Jun 2002
    Location
    Wakefield, West Yorkshire, UK
    Posts
    3,290
    Handy as all my parts arrived today... at LAST i can get this MkII over to 404!!

  11. #11
    Registered User
    Join Date
    Jan 2004
    Posts
    34
    Gary, is there a standard (or somethin close to it) for r-12?
    the early bird gets the worm and the second mouse gets the cheese...

  12. #12
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    For R12, I would shorten by about 3 feet.

    For R134a, I would shorten by about 4 feet.

    Keep in mind that all of these are educated guestimates, based on numbers and performance seen in these forums, along with interpolations of several online charts. I think they are pretty close.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  13. #13
    Registered User
    Join Date
    Jan 2004
    Posts
    34
    ok so on a single stage, single evap on r-12 using .028 i would start @7 feet? i know this is just a guestimate and just want to make sure im reading it right. thanks
    the early bird gets the worm and the second mouse gets the cheese...

  14. #14
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    How many watts heat load?


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  15. #15
    Registered User
    Join Date
    Jan 2004
    Posts
    34
    heat load should be 95-100 watts. gonna keep it conservative
    the early bird gets the worm and the second mouse gets the cheese...

  16. #16
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    Starting with 7 feet for a 150 watt load, we add 1 foot for each decrease of 15 watts. We end up with 10 feet of .028 for a 105 watt heat load.

    Actually I'm being conservative with this. You could probably add another foot, this being R12.
    Last edited by Gary Lloyd; 02-25-2004 at 10:53 PM.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  17. #17
    Registered User
    Join Date
    Jan 2004
    Posts
    34
    thatll work great, thanks again
    the early bird gets the worm and the second mouse gets the cheese...

  18. #18
    Xtreme Enthusiast
    Join Date
    Jan 2003
    Location
    USA
    Posts
    733
    any guess for 66% R-134a, 22% R-22, 12% R-290??

    hehe...found it on the charge plate for the high stage of a cryofreezer cascade system.
    Counting bodies like sheep to the rhythm of the war drums.
    go to sleep
    go to sleep
    go back to sleep.

    carpe noctem.

  19. #19
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    I wonder if they are autocascading. That's not even close to an azeotropic blend.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  20. #20
    HVAC/R Engineer
    Join Date
    Nov 2003
    Posts
    3,565
    I bet that blend lands right around R500 about 5 deg colder than R12

  21. #21
    Xtreme Enthusiast
    Join Date
    Jan 2003
    Location
    USA
    Posts
    733
    Originally posted by chilly1
    I bet that blend lands right around R500 about 5 deg colder than R12
    hmmm....it would be one helluva lot cheaper than R500. R500 is about $480 for a 30lbs cylinder from the webpricing I have seen.
    might have to try that mix.
    Counting bodies like sheep to the rhythm of the war drums.
    go to sleep
    go to sleep
    go back to sleep.

    carpe noctem.

  22. #22
    Registered User
    Join Date
    Jan 2003
    Posts
    78
    Ok just to confirm before I put it all together,

    According to Sisoft sandra my cpu is putting out 178W (2.5 barton mobile 12 X 218 at 2.15 Vcore)

    I am going to use propane or if possible Propylene with 0.31 cap tube.

    So I get about 11.5 feet of .031 cap according to Gary Lloyd figures.

    sound about right?

  23. #23
    Xtreme Addict
    Join Date
    Jun 2002
    Location
    usa,va.
    Posts
    2,007
    Originally posted by DaBit
    Hoho, let Bowman and the others say that the old man is right
    well it is close enough....for goverment work i would say...



    but there is no excate lenght....you see i get tons of pms on this ...and i tell everyone tha same thing....i can get you close..but you will have to fine tune and adjust to get the best temps at load....there are tons of varables..that cannt be figured...fine tuning is the only way.but problem today is people either can not or will not take time to fine tune.

    garys formula is the best way i have seen to explain how to get close.

  24. #24
    Banned
    Join Date
    Jan 2004
    Location
    Scotland
    Posts
    277
    so 6ft of .28 would be what ya want for a 200w+ heatload hu??

  25. #25
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    garys formula is the best way i have seen to explain how to get close.
    See... The old man isn't as dumb as he looks. (Actually, nobody is.)

    so 6ft of .28 would be what ya want for a 200w+ heatload hu??
    That's .028, not .28, and it depends on what refrigerant we are talking about.