    Building my first Single Stage

    After 10 years of inactivity I decided to come back.

    I had an old Single Stage made by "Unseen" in the basement that was not working any more because of a leak.

    I decided to try building my own Single Stage

    I used:

    Danfoss 1/3 hp with R404a
    Condenser 140x140x90mm
    Evaporator Asetec Vapochill LS
    Desuperheater Coil
    High Pressure Gauge
    Filter/Drier
    15ft captube

    Case, I used an Freezepack made by Unseen back in 2008.

    That was the compressor, condenser and evaporator in the old Single Stage...



    This is the final result










    As regards temps, idles at -55 C and with Pentium E5800 @5.0GHz at 1.7v after 27min of load keeps - 47 C.

    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	IMG_20190706_152755.jpg 
Views:	386 
Size:	401.7 KB 
ID:	132544   Click image for larger version. 

Name:	IMG_20190706_152549.jpg 
Views:	329 
Size:	424.7 KB 
ID:	132545  
    Last edited by Obijuan83; 07-06-2019 at 06:24 AM.

  2. #2
    Xtreme Owner Charles Wirth's Avatar
    Join Date
    Jun 2002
    Location
    Las Vegas
    Posts
    11,653
    Welcome back and good to see you got it running. If you need cadd files to cut new mounting I might be able to help with some measurements.
    Intel 9990XE @ 5.1Ghz
    ASUS Rampage VI Extreme Omega
    GTX 2080 ti Galax Hall of Fame
    64GB Galax Hall of Fame
    Intel Optane
    Platimax 1245W

    Intel 3175X
    Asus Dominus Extreme
    GRX 1080ti Galax Hall of Fame
    96GB Patriot Steel
    Intel Optane 900P RAID

  3. #3
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    Quote Originally Posted by Charles Wirth View Post
    Welcome back and good to see you got it running. If you need cadd files to cut new mounting I might be able to help with some measurements.
    Thank you, my next goal is to make a new evaporator and new mounting clip

  4. #4
    Xtreme Member
    Join Date
    Aug 2002
    Location
    Washington
    Posts
    365
    Very nice, looks so very sexy! So good to see someone actually doing some refrigeration on here.

  5. #5
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    Βecause of high ambient temps (37 C) and room temperature (30 C) efficiency of Single Stage suffers.

    Without load idles at -32.5 C
    High Pressure at 275psi / 48 C

    Suction freezes till compressor



    So I tried to cool the high pressure vapor with a chiller 1/8HP. I used the desuperheater coil to cool the 2 stage.

    The temp now at evaporator is -47.5
    High pressure is 180psi / 32 C

    Suction doesn't freeze till compressor.

    My question is, at that situation, I need to add refridgerant?



    Last edited by Obijuan83; 07-09-2019 at 01:13 AM.

  6. #6
    Xtreme Member
    Join Date
    Aug 2002
    Location
    Washington
    Posts
    365
    Sounds like it's overcharged. Your head pressure shouldn't be that high. I'm thinking the cap tube is too restrictive so you overcharged trying to get more capacity.

  7. #7
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    I asked if its undercharged at the situation with the added cooling.

    The head pressure its only 180psi /32C and the suction doesn't freeze.

    The cap tube is about 12 feet long and 0.031"
    Last edited by Obijuan83; 07-09-2019 at 01:39 AM.

  8. #8
    Xtreme Member
    Join Date
    Aug 2002
    Location
    Washington
    Posts
    365
    I was talking about your first pressures. Same situation though, I think your cap tube is too restrictive.

  9. #9
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    Ambient temperature doesn't matters?

  10. #10
    Xtreme Member
    Join Date
    Aug 2002
    Location
    Washington
    Posts
    365
    Ambient temperature matters, but if you were at 275 psi without the chiller/cascade/desuperheater that's indicative of an overcharge condition or the condenser isn't very efficient. Although I wasn't sure what you meant by 37c and 30c ambient and room temp since ambient and room temp is the same thing. A good thing to know is the air temp entering the condenser and the temperature exiting the condenser to find a Delta T. Finding the superheat and subcooling would be even better.

  11. #11
    Xtreme Member
    Join Date
    Aug 2002
    Location
    Washington
    Posts
    365
    Can you give the high and low side pressures? I would like to know the pressures you were getting before using the chiller on the desuperheater. Such high pressures on high side with somewhat high temps on evap and frost on compressor suction return has me wondering about the valveplate in the compressor.

  12. #12
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    Here in Greece the outside temps are 37-40C but we try to keep lower temps inside home!

    Propably the Condenser isn't that efficient at that ambient temps ~30 C but my question is when I use the first stage to cool the second stage , am I low on refridgerant at the second stage? If I add will I have better temps?

    I asked that because one and a half month ago with 20 C ambient and head pressure 215psi /20 C, it achieved -55 C at no load
    Last edited by Obijuan83; 07-09-2019 at 02:12 AM.

  13. #13
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    Quote Originally Posted by aenigma View Post
    Can you give the high and low side pressures? I would like to know the pressures you were getting before using the chiller on the desuperheater. Such high pressures on high side with somewhat high temps on evap and frost on compressor suction return has me wondering about the valveplate in the compressor.
    Its difficult to measure low pressure atm but what makes you think that there is problem with valveplate? When I cooled enough the refridgerant at 175-180psi the evaporator temps are better (-47.5 C) that means low side pressure at 0psi and below I think.
    Last edited by Obijuan83; 07-09-2019 at 02:19 AM.

  14. #14
    Xtreme Member
    Join Date
    Aug 2002
    Location
    Washington
    Posts
    365
    There are no real "stages" in this setup, so let's disregard that nomenclature. You got a much lower temp at 20c because it was cooler. Plain and simple you had a lower head pressure which means lower suction pressure. Either way knowing your inside ambient temperature, highside and lowside pressure and ideally condenser and evaporator inlet and outlet temperature would help a lot.

  15. #15
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    Ambient temp is 29-30C
    High side pressure before desuperheater is 180psi
    Refridgerant temp before desuperheater is 20 C
    Evaporator temp is 47.5 C

    The condenser was not used, I mean no fan was working because of 30 C ambient.

    The coolant that cooled the desuperheater has 16-17 C.

  16. #16
    Xtreme Member
    Join Date
    Aug 2002
    Location
    Washington
    Posts
    365
    Quote Originally Posted by Obijuan83 View Post
    Its difficult to measure low pressure atm but what makes you think that there is problem with valveplate? When I cooled enough the refridgerant at 175-180psi the evaporator temps are better (-47.5 C) that means low side pressure at 0psi and below I think.
    I only mentioned the valveplate because these compressors have reed valves which are simple spring steel "flaps" like an air compressor has and if they get too hot or withstand too much pressure they can bend, crack or break which can cause high pressures on both low and high side. It's fairly rare, but it happens.

    With R-404a you should be getting -46c with no load easily without the chiller desuperheater stuff. You saying it's difficult to check low side pressure makes me wonder if you pulled a vacuum before charging? If not then we found the problem.

  17. #17
    Xtreme Member
    Join Date
    Aug 2002
    Location
    Washington
    Posts
    365
    I looked at the pictures again and noticed you're using an evaporator heat exchanger for your condenser. The flow direction of the pipes traps refrigerant and oil. Might not be a big deal for a little system like this, but I thought I'd mention it.
    Last edited by aenigma; 07-09-2019 at 02:39 AM.

  18. #18
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    To be honest I pulled a vacuum but only for 45min. The low side gauge was at -30, not going any further. But i think that I did not fill the yellow hose with refridgerant when added the refridgerant, because I removed it from the vacuum pump and connected to the r404a bottle.Is that too bad?I mean the air inside the yellow hose.

  19. #19
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    Quote Originally Posted by aenigma View Post
    I looked at the pictures again and noticed you're using an evaporator heat exchanger for your condenser. The flow direction of the pipes traps refrigerant and oil. Might not be a big deal for a little system like this, but I thought I'd mention it.
    What do you mean? The cap tube that is wrapped around flexible suction line?

    If you mean that as evaporator heat exchange I would also like to ask if its better to wrapped it at contact to the suction line instead of the insulation of the suction line as it is now.

  20. #20
    Xtreme Member
    Join Date
    Aug 2002
    Location
    Washington
    Posts
    365
    Oh ok that's good you pulled a vacuum, I was just concerned there may be air in the system. After I vac my system I always close the manifold valves (low and high side valves) then disconnect the hose from my vac pump then connect it to my refrigerant tank, open my tank then crack open the line to the manifold/gauges to purge any air in the line set and tighten it back up. That makes sure there is no air in my line set.

    I was talking about your condenser, the piping direction is wrong for a condensor, it's an evaporator HX. As for subcooling it's good to wrap the capillary tube around the suction line. Even better is to solder it to the suction line somewhat close to the evap outlet.
    Last edited by aenigma; 07-09-2019 at 03:20 AM.

  21. #21
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    Quote Originally Posted by aenigma View Post

    I was talking about your condenser, the piping direction is wrong for a condensor, it's an evaporator HX. As for subcooling it's good to wrap the capillary tube around the suction line. Even better is to solder it to the suction line somewhat close to the evap outlet.
    I dont understand what you mean that its not condenser but its evaporator HX,what is the problem with the piping?

  22. #22
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    Quote Originally Posted by aenigma View Post
    There are no real "stages" in this setup, so let's disregard that nomenclature. You got a much lower temp at 20c because it was cooler. Plain and simple you had a lower head pressure which means lower suction pressure. Either way knowing your inside ambient temperature, highside and lowside pressure and ideally condenser and evaporator inlet and outlet temperature would help a lot.
    I used a second probe and got the following results.

    48 C Inlet Condenser Temp (that means 315 psig)
    38 C Outlet Condenser temp /Filter temp

    (-10C Delta)

    28 C Ambient temp
    38 C Exhaust Air temp from Condenser

    (+10 C Delta)

    -33.5 C Evaporator temp
    -32.5 C 1" before Compressor (that means 12.5 psig)

  23. #23
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    I can understand that at these ambient temperatures, 28-30 C , and temperature before condenser 48C, the SS seems to be overcharged.

    But, when I cool down the liquid line to 32 C before condenser (200psi) the evaporator temp is -47 and suction temp is -11C.

    That seems to be undercharged, am I right?

  24. #24
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    I tend to believe that my problem is not proper vacuum.

    I pulled a vacuum only for 45min and when I charged via the high pressure, the hose connected to r404a bottle was empty an full of air. Could that cause not proper vacuum?

    I have to add a low pressure gauge to measure superheat...
    Last edited by Obijuan83; 07-09-2019 at 02:13 PM.

  25. #25
    Registered User
    Join Date
    Jun 2007
    Posts
    86
    Finally the problem was poor vacuum.

    I did a proper vacuum procedure and now I have the following readings.

    35 C Inlet Condenser Temp (that means 200 psig)
    31C Outlet Condenser temp /Filter temp

    (-4 C Delta)

    27 C Ambient temp
    31 C Exhaust Air temp from Condenser

    (+4 C Delta)

    -44.5 C Evaporator temp
    -47.5 C /-1.5psi at low side gauge
    Last edited by Obijuan83; 07-11-2019 at 01:22 PM.