Thread: Autocascade Discussion and build attempt

  1. #101
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    My compressor has a maximum working pressure, so I dont want to go beyond that. So if I reach an R23 SST/Evap exit difference between 5-10K and my R290 SST/Evap difference is near 30K (EDIT and I am at my max working pressure), then I dont have any room to add more R290 without going past the max working pressure for my compressor. See what im saying? Anyway, here are the new temps after adding some R23.

    R23
    Evap Exit: -56ÂșC ( i added a little)
    SST: -64ÂșC (1.6barg, 23psi)
    SCT: -12ÂșC (16.6barg, 240psi)

    R290
    Evap Exit: 15ÂșC
    SST: -18ÂșC (1.6barg, 23psi)
    SCT: 52ÂșC (16.6barg, 240psi)

    Air in: 22ÂșC
    Air out: 26ÂșC

    You can read what the manufacturer has written about the compressor, im guessing that the max working pressure is 25bara. What do you think?

    http://www.cubigel.com/java/X?cgi=cu...rmaciontecnica
    Last edited by Russell_hq; 02-16-2004 at 06:41 AM.

  2. #102
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    The R23 looks just right now.

    The heat exchanger is working very well.

    Good airflow.

    Looks like it could still use a little more R290.

    It seems unlikely that the R290 cap tube is too restrictive, being 10 feet of .031, but autocascades are new to me.

    What is the CPU temp?


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  3. #103
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    I removed the thermocouple from the front of the cpu and attatched it to the evap exit. So im using the motherboard to measure the cpu temp, its got a thermistor which presses against the back of the cpu. Currently its measuring -19ÂșC. This doesnt look good when the evap is boiling at -64ÂșC . Though I know that the evap works well, so I just dont trust the reading too much. Its more of a relative measurement I get from it.

    The R290 is a strange one on me too. I just keep adding it bit by bit, but I cant shift the exit temps past 14-15ÂșC

  4. #104
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    I went back and had a look at an old post. You can see what I mean about not trusting the temp it reports.
    http://www.xtremesystems.org/forums/...052#post355052

    I had a thermocouple right beside the core and my fluke was reading -37ÂșC (100% sure it wasnt touching the evap) while the motherboard was reporting -7ÂșC. Draw your own conclusions.

  5. #105
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    The R290 is a strange one on me too. I just keep adding it bit by bit, but I cant shift the exit temps past 14-15ÂșC
    This would be another indication that the cap tube is too restrictive.

    What are all of the temps and pressures doing as you add the R290?


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  6. #106
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    R290 evap exit temp rises just after I add a little bit. Then it slowly begins to fall. I added a little bit then went for a shower and this is what I have got:

    R23
    Evap Exit: -55ÂșC ( i added a little)
    SST: -64ÂșC (1.6barg, 23psi)
    SCT: -11ÂșC (17.4barg, 240psi)

    R290
    Evap Exit: 17ÂșC
    SST: -18ÂșC (1.6barg, 23psi)
    SCT: 53ÂșC (17.4barg, 240psi)

    Air in: 22ÂșC
    Air out: 26ÂșC

    Notice that the Evap exit has risen from 15-17ÂșC. Its definatly not dropping as I add more R290.

  7. #107
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    The good news is that the high side pressure isn't rising, either. This may be the best we can get with this cap tube. I think we need to remove about 2 feet of the R290 cap tube. Better yet would be to replace it with a TXV.

    Even with complete flooding of the R290 evaporator, I don't think the bottom line temps are going to get much lower without a larger compressor, but I could be wrong. Possibly a shorter cap tube would provide significant improvement.
    Last edited by Gary Lloyd; 02-16-2004 at 07:39 AM.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  8. #108
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    Thats what I was afraid of. Well im going to crank up the heat and see what happens As there is not much else I can do to the system, Im going to up the load and see where I can take it

  9. #109
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    We also need to shut it off and warm it to room temp to see what the static pressure is. If it is too high, we may need an expansion tank.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  10. #110
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    When you crank up the heat load, tell us all of the temps and pressures, so we can see what effect heavy load has on it.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  11. #111
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    What's too high? What should I be looking for?

  12. #112
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    Ok, I'm going to need more R23 in it to cope with the extra load.

  13. #113
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    You are a long way from the 26 bar limit.

    The ideal is to have 5-10C difference between SST and evap outlet with maximum load.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  14. #114
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    We need to see the full list of temps and pressures.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  15. #115
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    rgr that gary. heat load shoud now be in the region of 110Watts (from 68 watts). I will tune the R23 SST/evap out temperature difference to between 5-10K then report back.

  16. #116
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    Gary, I was thinking about the R290 evaporator exit temperature. Should I be able to get this below zero and within 5-10K of SST with no load on the system? I say yes, but I dont think it will do it from what I have experienced of it so far, if thats the case can you conclude anything important from this that will help me get the temp down?

  17. #117
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    It doesn't seem as if it is going to allow that additional flow with this cap tube size, and I don't think no load operation is going to do it. If anything, adding more R23 to tune the evaporator under heavy load may force a little more R290 through, but that seems unlikely also. Keep in mind that I have zero experience with autocascades, so I am learning too. I am waiting to see what effect the additional R23 has, as well as the heavy load. Have you added the R23 under heavy load yet? Do you have temps and pressures for me?


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  18. #118
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    Not yet. I should be getting some more thermocouples in the next couple days, so I can stick them to the system and see whats going on. I have 1 on the R23 evap exit and 1 on the R290 evap exit. Could you list in order of importance where you would like me to put the rest of the thermocouples, you can assume that I have as many as the number of temp readings you would like, thanks.

  19. #119
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    Gary these are just for you before I go off to bed. I had to give it a good bit of head pressure by adding more R23 to get the Evap exit with 5-10k of SST,


    R23
    Evap Exit: -52ÂșC
    SST: -63ÂșC (1.7barg)
    SCT: -3ÂșC (22barg)

    R290
    Evap Exit: 18ÂșC
    SST: -17ÂșC (1.7barg)
    SCT: 64ÂșC (22barg)

    Air in: 24.5ÂșC
    Air out: 28.6ÂșC

    CPU: -13ÂșC

    The condensor in is hot and out is mild/cool (measured using my body thermometer ) thats the best I can give you at the moment.

  20. #120
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    Checked static pressure this morning, its around 110psi with room temps about 21ÂșC.

  21. #121
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    I've been going over all of the numbers, and everything keeps pointing to the cap tubes.

    The R23 cap tube worked beautifully at the lower load, but we needed to add considerable pressure to push enough refrigerant through for the higher heat load. I think we need to shorten this cap tube a couple feet, which should give it roughly 40-50 watts more capacity (guestimating).

    The R290 cap tube hasn't come close to flooding the heat exchanger even under minimum load with full sight glass, and doesn't budge no matter how much pressure is pushing the refrigerant through. The cap tube is much too restrictive. Not even in the ballpark. We need to cut off several feet. I would cut off 3 feet, at least.

    I don't think we are going to have a problem with static pressure in this system. The minimum liquid R23 strategy seems to be working very well.
    Last edited by Gary Lloyd; 02-17-2004 at 06:58 AM.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  22. #122
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    Thats good news, I will try and get some cap tube cut off the system today and see what happens. And I will get back to you. 3 feet of the R290 and 2 feet off the R23. That will leave me 96" on the R23 and 94" on the R290. The original sizes where 120" R23 and 130" R290.

  23. #123
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    I gave the cap tubes the chop, hooked it up to the computer and put 120 watt (approx.) load on it. Here is what I have:

    R23
    Evap Exit: -49ÂșC
    SST: -59ÂșC (2.2barg)
    SCT: -5ÂșC (21barg)

    R290
    Evap Exit: 18ÂșC
    SST: -12ÂșC (2.2barg)
    SCT: 62ÂșC (21barg)

    CPU: -5ÂșC

    As you can see I still have the problem with the R290 exit temps. I took 3 feet off the cap tube, and the sight glass is full.

  24. #124
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    The R23 cap tube looks just about right.

    The R290 evap has dropped the exit superheat from 35K to 30K, but it is still too restrictive. We are looking for 5-10K.

    Just to get an apples to apples comparison, we might drop the load back down to 68W, and see how all of the temps compare.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  25. #125
    Xtreme Enthusiast
    Join Date
    Sep 2003
    Posts
    651
    I like apples to apples. I was seeing how far I could push my cpu, just cant help myself Thats why the load was up.

    I set up the cpu the same and see what we can do, what about the charge, do you want me to get it in any pressure range?