My compressor has a maximum working pressure, so I dont want to go beyond that. So if I reach an R23 SST/Evap exit difference between 5-10K and my R290 SST/Evap difference is near 30K (EDIT and I am at my max working pressure), then I dont have any room to add more R290 without going past the max working pressure for my compressor. See what im saying? Anyway, here are the new temps after adding some R23.
R23
Evap Exit: -56ÂșC ( i added a little)
SST: -64ÂșC (1.6barg, 23psi)
SCT: -12ÂșC (16.6barg, 240psi)
R290
Evap Exit: 15ÂșC
SST: -18ÂșC (1.6barg, 23psi)
SCT: 52ÂșC (16.6barg, 240psi)
Air in: 22ÂșC
Air out: 26ÂșC
You can read what the manufacturer has written about the compressor, im guessing that the max working pressure is 25bara. What do you think?