    Cascade: Refrigerant blending and Oil Management

    Guys, I normally use r-1150 in 2 stage cascades because frankly its usually pointless to use anything else.

    That said I have a client that wishes to use r-23 and also would like it to hold on the contact point -80c under loads ranging from 100 watts to 250 watts.

    Given the following properties of both I dont think im going to be able to obtain a guaranteed temp of -80c am I correct?

    r-23
    Appearance: Clear, colourless liquid and vapour.
    Physical State: Gas at ambient pressure and temperature.
    Chemical Formula: CHF3
    Odour: Faint ethereal odour.
    pH Neutral
    Boiling Point: -82.1oC (-115.7oF)
    Freezing Point: -155oC (-247oF)
    Vapour Pressure: 42.4 Bar at 21oC (70oF)
    Vapour Density (Air =1.0) 2.4


    r-1150
    APPEARANCE, ODOR AND STATE: Colorless gas at normal temperature and pressure; faint, sweet, musty odor.
    MOLECULAR WEIGHT: 28.05
    SPECIFIC GRAVITY (air=1) at 32?F (0?C) and 1 atm: 0.978
    GAS DENSITY at 32?F (0?C) and 1 atm: 0.0787 lb/ft3 (1.261 kg/m3)
    SOLUBILITY IN WATER, vol/vol at 32?F (0?C) and 1 atm: 0.26
    BOILING POINT at 1 atm: -154.62?F (-103.68?C)
    MELTING POINT at 1 atm: -272.9?F (-169.4?C)
    % VOLATILES BY VOLUME: 100
    Last edited by sdumper; 01-19-2013 at 11:01 AM. Reason: Please change the Title to "Cascade: Refrigerant blending and Oil Management"
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  2. #2
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Hi Scott,

    Do you have access to R14? Adding a small amount of this to R23 wil allow you to better achieve your stated goal. Since you are only looking for -80 under load, it won't take much R14 to do this.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  3. #3
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    I do have access to r-14 but I thought its condensing temp was -74c?

    Also any ideas what might be happening here with these charts? Do you think the TXV isnt adjusted for a steady temp?

    Not sure why I cant upload a picture but here is a graph of whats happening.



    It basically holds at -80c for 4 hours or so and then it starts to spike and recover.

    Ideas:
    Oil Return causing spike
    TXV adjusted incorrectly
    Water vapor in system
    excess ambient heat (room constant 68f)
    Last edited by sdumper; 12-21-2012 at 12:08 PM.
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  4. #4
    Xtreme Enthusiast
    Join Date
    Mar 2005
    Location
    North West London
    Posts
    776
    Quote Originally Posted by mytekcontrols View Post
    Hi Scott,

    Do you have access to R14? Adding a small amount of this to R23 wil allow you to better achieve your stated goal. Since you are only looking for -80 under load, it won't take much R14 to do this.
    That's very usefull information, had no idea R14 could be used like that. Thanks.



    Sorry sdumper can't offer you advice, still learning myself, good luck, hope you achieve your goal.

  5. #5
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Quote Originally Posted by DFI pit bull View Post
    That's very usefull information, had no idea R14 could be used like that. Thanks.
    Basically it's how blends such as R507 are made. Most refrigerants, especially ones within the same family, have some degree of solubility with each other. However when combining ones that have a wide spread of boiling points, such as R23 and R14 in a single-stage it is important to take condensing temperatures/pressures into consideration as Scott pointed out. So that is why I recommended using only a small amount of R14, and the best way to do this would be to add it to pure R23 in a running fully loaded system just a little at a time until the target temperature is achieved. Keep in mind that the more R14 added, the higher will be you're compressor discharge pressure and temperature.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  6. #6
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    I had them adjust the txv and it ran for a little over 12 hours at -82c on the heating element and then this morning it started to spike. Im wondering if the shop temperature is cycling up since its a holiday weekend and the office is empty?

    Details: Cased unit
    Stage 1: 3/4 hp low temp 230 volt Embraco
    Stage gas: r402a
    Stage2: 1/2 hp low temp 230 volt Embraco
    Stage 2 gas: r1150




    Pictures at my place while I was working on it.


    Last edited by sdumper; 12-22-2012 at 06:19 AM.
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  7. #7
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    Hmm im wondering if maybe it might have some moisture build up in the line...
    It ran for a solid 12 hours before it fluctuated and recovered.

    Last edited by sdumper; 12-28-2012 at 09:30 AM.
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  8. #8
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    Bump any thoughts? Does it seem like maybe its moisture? Strange thing is the original design had no filter/drier on the second stage and I didnt add one.
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  9. #9
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    it seems more like frozen oil then moisture but those are very possible explanations to the problem. What were the running pressures


    If you have a cooling question or concern feel free to contact me.

  10. #10
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    200psi under load 145 no load...
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  11. #11
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    I mean the pressure during the spike


    If you have a cooling question or concern feel free to contact me.

  12. #12
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    Id like to know too but its in California and Im not sure if they have a way to log the pressure.
    Ill ask...
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  13. #13
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Germany
    Posts
    401
    maybe it is the oil seperator that opens at the moment for oil return.
    that causes higher suction pressure and temperature increase.
    or didn't you use an oil sep?

  14. #14
    -100c Club Member
    Join Date
    Jul 2005
    Location
    England
    Posts
    1,422
    Quote Originally Posted by Patrickclouds View Post
    maybe it is the oil seperator that opens at the moment for oil return.
    that causes higher suction pressure and temperature increase.
    or didn't you use an oil sep?

    i would tend to agree with patrick the oil sep would need to open at some point if fitted
    1. The first rule of Bench Club is, you do not talk about Bench Club
    2. The second rule of Bench Club is, you do not talk about Bench Club
    3. If someone says stop, goes limp, taps out, the the benching is over
    4. No bummers in the batcave, apart from unkie dave
    5. One Bench at a time
    6. No air, no water
    7. Benching will go on as long as they have to
    8. If this is your first night at Bench Club, you have to Bench

  15. #15
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    Yes its using a floated oil sep.

    Maybe a larger 2nd stage compressor to help compensate?
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  16. #16
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Germany
    Posts
    401
    you can use a long captube from oil sep to suction line.

    and maybe a small filter to collect the oil after the oil sep.

  17. #17
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    Thank you sir!!
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  18. #18
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Germany
    Posts
    401
    but a very long and thin one.
    maybe 4-5m 0,7mm captube

  19. #19
    Xtreme Member
    Join Date
    Oct 2011
    Posts
    163
    Quote Originally Posted by mytekcontrols View Post
    Basically it's how blends such as R507 are made. Most refrigerants, especially ones within the same family, have some degree of solubility with each other. However when combining ones that have a wide spread of boiling points
    With this idea, is there something to expect with a blend of R1150/R50 ? Regardless of higher discharge pressure obviously !

  20. #20
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    Depends on the condensing temp/pressure of methane.
    What temp does methane condense at?
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  21. #21
    Xtreme Enthusiast
    Join Date
    Mar 2008
    Location
    Wherever I may roam
    Posts
    678
    -161 degrees C ?
    ____________________________________________

    More & more very expensive, quickly obsolete parts!!

  22. #22
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    I think that must be boiling point what would be useful is to know the condensing temps at varies pressures.
    Methane is going to be very tough to condense considering that r1150 condenses at around -40c at a 100 psi...
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  23. #23
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    100psi? More like 195 psi/14.5 bar.


    If you have a cooling question or concern feel free to contact me.

  24. #24
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    Thanks Adam.


    Expat Griz that makes it even worse ...
    I dont think r50 and r1150 is going to give you much but MyTekControls is probably the best one to answer
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  25. #25
    Xtreme Member
    Join Date
    Oct 2011
    Posts
    163
    That question was already treated on my thread, but I didn't recall if we discussed about ethylene/methane together lowering the evap temp @ given pressure ...