    Hi i'm planing out a cascade to cool 2x high end GPUs and I was wondering which of these two designs would work the best. I know that it would have hold a lot of heat.

    1. 3 stage cascade, r404/1150/1150 with dual heads.

    2. 2hp compressor as first stage cooling 2 separate 2nd stage loops each with its own compressor 1.5hp.

    Second option I could run either 1 or 2 heads depending on the benching one or 2 gpus.

    1st stage condenser...

    http://img28.imageshack.us/img28/8292/bild0941.jpg

    Thanks
    Last edited by fatguy1992; 08-08-2010 at 02:50 AM.

  2. #2
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Germany
    Posts
    401
    how much load do you need on your evaps? 300watts each?
    which displacements have your compressors?

    are you using ethene on the second stages? no cold problem with the gpus?
    i would choose 20-24ccm in your second stages r1150 and 48ccm in the first stage r404a or r507

  3. #3
    Xtreme Addict
    Join Date
    Jun 2008
    Posts
    1,676
    I was thinking about 300-350watts for each GPU. The 2nd stages would have R1150 in them and if the GPUs have a cold bug then I won't bench them

  4. #4
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Germany
    Posts
    401
    then go with the 24ccm rotarys on the second stages.
    on first stage i´m not really shure what size you should choose.

    toaster has build a strong cascade with only one compressor and one evaporator on second stage.
    400watts on second stage evap. first stage was a 36ccm rotary.
    so if you double the size of the first stage you end up at 70ccm which could be a maneurop mtz40 (68ccm, 11,8m³/h)
    you can calculate your unit with coolpack and refrigeration utilities. i end at 9-10m³/h on first stage

  5. #5
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    Sounds like a fun project...
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  6. #6
    Xtreme Addict
    Join Date
    Jun 2008
    Posts
    1,676
    Alright thanks, so you think the 2nd design would be the best one?


    Quote Originally Posted by sdumper View Post
    Fatguy are you in the US? Im wondering because if you go as big as your describing then 115v compressor wont be available in the sizes your after.
    No i'm in Australia, I already have the 2hp compressor in a 2x headed GPU SS.

  7. #7
    Xtreme Addict
    Join Date
    Jun 2008
    Posts
    1,676
    BTW has anyone built a 2x headed cascade before? If so is there a link to their build log? I couldn't find any.

  8. #8
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Germany
    Posts
    401
    here we go but with one compressor in the second stage:
    http://www.extremecooling.de/forum/t...Rotary-Kaskade

  9. #9
    Xtreme Addict
    Join Date
    Jun 2008
    Posts
    1,676
    Thanks any newer builds? So that end up 2x 180watts @ -69C with smaller compressors then I would be using.

  10. #10
    Xtreme Member
    Join Date
    Jan 2005
    Location
    Germany
    Posts
    401
    http://www.xtremesystems.org/forums/...ad.php?t=70265
    but i don´t know if it has ever worked.

    here are some pictures of that unit:
    http://rapidshare.com/files/41184843...ap_cascade.rar

  11. #11
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    Wait didnt kayl do one?


    He is also in OZ right?
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

  12. #12
    /dev/zero
    Join Date
    Nov 2002
    Location
    Germany, Berlin
    Posts
    3,625
    LittleDevil tried to do one, but got into problems with load balancing...
    http://benchtec.co.uk/forums/showthread.php?t=525
    Xtremesystems.org
    i7-4820K * ryba 2-stager + 1-stager * EVGA X79 Dark * 32G Team Xtreem 2666C11 * EVGA GTX 680 SC Sig. * Intel G2 80G * Corsair HX1000 * Lian Li PC-70B * Watercool Heatkiller, EK Fullcover/Backplate for GTX, MCP355 Dual Setup@Koolance RP-402X2, PA120.3+Alphacool 360, Tubing 16/10.


  13. #13
    Xtreme Member
    Join Date
    Aug 2008
    Location
    USA mn
    Posts
    324
    easiest way would be two cascade in the same case.
    how about a 3tons in the 1st stage and 3ton on the second with dual heads

  14. #14
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Sounds wastefully big.


    If you have a cooling question or concern feel free to contact me.

  15. #15
    Xtreme Member
    Join Date
    Dec 2009
    Location
    Southern California
    Posts
    175
    3 compressors does sound like overkill!
    Am I completely off basis, or are we talking about two evaporators in parallel? I imagine there would be difficulty if the load was different between the two heads, as the pressure differential would be different...
    I hope this goes through! I would love to learn/hear about it!
    What if the hokey pokey really is what it is all about?

  16. #16
    Xtreme Member
    Join Date
    Aug 2008
    Location
    USA mn
    Posts
    324
    fatguy what kind of load temps are you okay with?

  17. #17
    Xtreme Addict
    Join Date
    Jun 2008
    Posts
    1,676
    Quote Originally Posted by Patrickclouds View Post
    http://www.xtremesystems.org/forums/...ad.php?t=70265
    but i don´t know if it has ever worked.

    here are some pictures of that unit:
    http://rapidshare.com/files/41184843...ap_cascade.rar
    Quote Originally Posted by SAE View Post
    LittleDevil tried to do one, but got into problems with load balancing...
    http://benchtec.co.uk/forums/showthread.php?t=525
    Dam shame they never worked well.

    Quote Originally Posted by sdumper View Post
    Wait didnt kayl do one?


    He is also in OZ right?
    Yeah from memory he tried a 3 headed cascade, 1 CPU and 2 GPUs. It couldn't handle the heat load.

    Quote Originally Posted by EliTE22 View Post
    easiest way would be two cascade in the same case.
    how about a 3tons in the 1st stage and 3ton on the second with dual heads
    I don't really have that much money, hence why I'm wanting to re-use most if not all the parts I already have.

    Quote Originally Posted by cdolphin View Post
    3 compressors does sound like overkill!
    Am I completely off basis, or are we talking about two evaporators in parallel? I imagine there would be difficulty if the load was different between the two heads, as the pressure differential would be different...
    I hope this goes through! I would love to learn/hear about it!
    Heres a quick ms paint drawing of what i'm talking about not great but it should do...



    Uploaded with ImageShack.us

    Quote Originally Posted by EliTE22 View Post
    fatguy what kind of load temps are you okay with?
    I was thinking about 300-350watts each head in the -80c's.

  18. #18
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    I wouldn't do it that way. Under that circumstance, should you not run one of them, you have a ton of wasted flow. Options are...
    Either run two TXV's. Or, make one larger self-coiled heat exchanger. Something like 20 ft of 1/2" tubing with two 3/16" run through it. Then put a TXV on that.


    If you have a cooling question or concern feel free to contact me.

  19. #19
    Xtreme Member
    Join Date
    Oct 2008
    Location
    NC
    Posts
    360
    Quote Originally Posted by fatguy1992 View Post
    Heres a quick ms paint drawing of what i'm talking about not great but it should do...



    Uploaded with ImageShack.us



    I was thinking about 300-350watts each head in the -80c's.

    You have the two plate HXs in parallel. Thats is one big bi**h to load balance. Put them in series and drop in an accumulator between them and the compressor. It will save you some major head aches.

  20. #20
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    You sure Ultralo? That doesn't seem like it'll balance them.


    If you have a cooling question or concern feel free to contact me.

  21. #21
    Diablo 3! Who's Excited?
    Join Date
    May 2005
    Location
    Boulder, Colorado
    Posts
    9,412
    Solenoids + PIDs are the solution



    Just throwing something out there since we're all doing it.

  22. #22
    Xtreme Member
    Join Date
    Oct 2008
    Location
    NC
    Posts
    360
    Quote Originally Posted by n00b 0f l337 View Post
    You sure Ultralo? That doesn't seem like it'll balance them.
    It doesnt balance them. It creates a bigger HX. You will have to do the brute force method. Balancing two evaps on the same system is hard, then if you put it into a dynamic situation, it is exponetially harder.

    Here a few questions to ponder regarding the parallel setup:
    1: How are you going to ensure that both metering devices are getting the correct flow?
    2: How are you going to adjust superheat on each HX?
    3: How are you going to ensure that each HX are responding correclty in a dynamic situation?
    4: If using TXs how is one TX hunting going to affect the other TX since, suction pressure will be varying?

  23. #23
    Xtreme Mentor
    Join Date
    Aug 2006
    Location
    Atlanta
    Posts
    3,286
    Quote Originally Posted by [XC] gomeler View Post
    Solenoids + PIDs are the solution



    Just throwing something out there since we're all doing it.
    Never empower an idiot with a response....

    http://en.wikipedia.org/wiki/Troll_%28Internet%29

    Seller/Buyer Reputation:
    Heatware: http://www.heatware.com/eval.php?id=50905
    Ebay: {Family Account} Kasyg3 http://myworld.ebay.com/kasyg3/
    Ebay: {My personal Account} Sdumper http://myworld.ebay.com/sdumper/
    iTrader: http://www.blazingpc.com/forum/itrader.php?u=28

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •