Hi XS'ers,
I have been studying autocascade cycles using Aspen Hysys software. I believe I have a good cycle using only three hydrocarbons (iso-pentane, ethane, and methane). The cycle uses two phase separators along with an auxilary condenser. Cycle efficiency is good with a COP of 0.26. I would use a 15,000 Btu/hr 410a window AC unit (compressor displacement 15 cc/rev) with a cooling duty of 270W. The main problem I see is the fact that the auxilary condenser has a very high cooling duty 1900W and its discharge temperature is only -75C. I guess a Temprite coalesing oil-separator could be used to avoid frozen oil before the first phase separator. The pressure-ratio is a good match for a 410a rotary compressor at PR=4 with suction pressure at 6.5-bar_abs and discharge pressure at 26 bar_abs. Cooling with 270W load to -125C blows away any 2-stage cascade (and likely 3-stage cascades as well). The cost of a 15,000 Btu/hr AC window unit is about $500 and probably an additional $1000 may be needed for all the modifications (HX's etc.).
Standard R410a AC cycle has a suction pressure of about 10-bar (45F) and discharge of 30-bar (120F) so the compressor loading should closely match the standard AC cycle and therefore yield good electrical efficiency.
I would post the cycle simulation results but it is still not possible to upload a jpeg to this blog (I hope this will be fixed soon).
Kevin