    Hailea HC-500a "50.0" failure?

    Hey guys,
    I own a Hailea HC-500a chiller for over 2 years now and didn't use it in the last 6 months.
    4 days ago I wanted to switch it on again, just for a cooling run of my test-setup and the display shows "50.0".
    I can set the temperature to reach as usual, but it doesn't show me the actual water-temp.
    The chiller starts and runs, but the display is always showing "50.0".
    I don't know what to do.

    I sent an e-mail to Hailea already but no response yet.

    Any advices?

  2. #2
    Xtreme Member
    Join Date
    Jun 2007
    Location
    Germany
    Posts
    137
    No hints for me?

  3. #3
    Xtreme Member
    Join Date
    Oct 2007
    Posts
    292
    just sounds like the sensore is stuck, maybe a loose connection or something.
    "Computers in the future may weigh no more than 1.5 tons."
    - Popular Mechanics, 1949

    "I think there is a world market for maybe five computers."
    - Thomas Watson, chairman of IBM, 1943


    Heat

  4. #4
    Xtreme Addict
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    2,267
    sensors can go... They are usually pretty easy to replace if needed.
    Regards, Stew.....

    - This message brought to you by Frank Lee E. Snutz

  5. #5
    Xtreme Member
    Join Date
    Jun 2007
    Location
    Germany
    Posts
    137
    Okay, but there's a problem.
    I don't have a clue where to buy a new sensor.
    Hailea is not responding on my emails and I don't know any reseller except Aquatuning.de who sells these chillers.
    Aquatuning cannot "deliver" such a sensor.

  6. #6
    Xtreme Mentor
    Join Date
    Feb 2007
    Location
    Victoria, British Colombia
    Posts
    2,677
    the water is getting cold correct?
    mentally confused and prone to wandering

  7. #7
    Xtreme Member
    Join Date
    Jun 2007
    Location
    Germany
    Posts
    137
    Okay, I opened the chiller.
    They connection between controller and sensor is connected and good.
    I switched the chiller on and the display shows 50.0, then I set the temp to reach and it chills.
    But the chiller cannot reach the temp so it chills constantly.

  8. #8
    Xtreme Addict
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    2,267
    I'm not particularly privy to you particular unit; perhaps a few pictures of the offending device could help.

    Anyways, this is what's happening.

    You have a faulty temperature sensor. Your water is reaching the appropriate temperature, but the sensor is telling the controller that the temp hasn't changed. The temp it reports is erroneous, but your controller doesn't know that; it keeps on working as if the temp is unchanged.

    Do you have any kind of manual or documentation on this unit?
    Regards, Stew.....