Page 2 of 10 FirstFirst 12345 ... LastLast
Results 26 to 50 of 230

Thread: captaincascade's help+stuff=thread

  1. #26
    Xtreme Member
    Join Date
    Jun 2002
    Posts
    240
    Originally posted by captaincascade
    you think i could see some designs you have,,, just so i got an idea of what im workin with?.
    Bowman posted a picture of my block.

    http://www.xtremesystems.org/forums/...&pagenumber=18

    Post #438

    baker18

  2. #27
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    christ baker, thats about as hardcore as i could have imagined.... im in....

    i only wanted to use 1 phase seporato.. this being more of a expierament... ill get started on the standard cascade thiks weekend.

  3. #28
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    oh and a big thanks to enigma for puttin those pics up. and the drawing he made. .....good man


    oh and if you guys wanna know how i found this place... anigma, pointed me here.
    Last edited by captaincascade; 09-26-2003 at 08:43 AM.
    If i was an animal Id be a freezer.

  4. #29
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    lol looks like i might have to break my own rule..... i dont have 2 scrap compressors that are the same kind, lying around. so i may have to use 2 different ones. eh well its a small load anyway. whats the btu output of a normal processer
    Last edited by captaincascade; 09-26-2003 at 08:54 PM.
    If i was an animal Id be a freezer.

  5. #30
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    heres a link to sporlan goes into alot of stuff i think you might find it useful

    http://www.acalny.com/201ME.pdf
    If i was an animal Id be a freezer.

  6. #31
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    1st stage is complete ill post some pics when anigma wakes up.
    my interstage only got to -35c., but i think thatll be fine
    If i was an animal Id be a freezer.

  7. #32
    Xtreme Relic
    Join Date
    Jun 2002
    Location
    Hilton Head, S.C.
    Posts
    5,240
    Cool! Can't wait to see the pics!
    I hate to advocate drugs, alcohol, violence, or insanity to anyone, but they've always worked for me.
    Hunter S. Thompson (1939 - 2005)

  8. #33
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    http://www.subz3ro.net/1st%20stage%20001.jpg



    ok theres the first stage. i know how everyone likes to see ice so they know its runnin so this pic is taken shortly after start up. the condenser is a little over size for no load so i had to pulse my big as fan to maintain propper head pressure. i used 404a and cap tube. you can see i just wired the start components right there next to it. i ended up puttin on a txv by the end of the night.

    Im not gunna try and be all cool. this is a pain in the but. im not used to improvising from scratch. im only alowed to use old parts so its kinda restrictive. christ it took me an hour to find that fan and mount it. im now whining and thats ok with me i thought i could do this in a night boy was i wrong. thisll take at least 3 nights.

    http://www.subz3ro.net/1st%20stage%20002.jpg




    and heres a pic of my thermometer for some reason. i didnt catch it at -35. i think my senser placeing is kinda screwed up its right there on the inlet of interstage. im gunna soder on a little port for my sensor.

    i dont have a match for the compressor so i may have to compremise.

    ps...by nights i mean 1200am to sunrise.
    Last edited by captaincascade; 09-27-2003 at 04:47 PM.

  9. #34
    Xtreme Addict
    Join Date
    Jun 2002
    Location
    usa,va.
    Posts
    2,007
    good luck.

    it never is as easy as it seams.expecially when you need to do it in a hurry,never fails ....small problems will set you back.

    keep at it,do it to relax, not because it is a job..or it will burn you out...

    good luck again Capt

  10. #35
    Xtreme Member
    Join Date
    Jun 2002
    Posts
    240
    Just got back from CaptainCascade's hideout.

    Here is a picture of CaptainCascade's cooler with a baker block......
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	cascade3.jpg 
Views:	1043 
Size:	60.7 KB 
ID:	4300  

  11. #36
    Xtreme Member
    Join Date
    Jun 2002
    Posts
    240
    another picture.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	cascade2.jpg 
Views:	856 
Size:	60.3 KB 
ID:	4301  

  12. #37
    Xtreme Member
    Join Date
    Jun 2002
    Posts
    240
    CaptainCascade's playground.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	dsc00031.jpg 
Views:	1042 
Size:	59.7 KB 
ID:	4302  

  13. #38
    Xtreme Member
    Join Date
    Jun 2002
    Posts
    240
    Finally......

    -80C freezer....................
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	dsc00029.jpg 
Views:	809 
Size:	61.8 KB 
ID:	4303  

  14. #39
    Xtreme Relic
    Join Date
    Jun 2002
    Location
    Hilton Head, S.C.
    Posts
    5,240
    AWESOME!

    I hate to advocate drugs, alcohol, violence, or insanity to anyone, but they've always worked for me.
    Hunter S. Thompson (1939 - 2005)

  15. #40
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    On the autocascade:



    It seems to me that if the condenser had parallel runs (as opposed to serpentine) with headers at each end, the hot gas could enter the middle of the header on one end, and exit top and bottom of the header on the other end. This would combine the condenser and phase separator.

    Assuming the condenser is like the drawing, the non-condensing (high pressure) refrigerant will tend to collect in the top of the serpentine condenser, while the condensing (low pressure) refrigerant will exit the bottom of the condenser in liquid form. At the very least, this could cause the operation to be very erratic.
    Last edited by Gary Lloyd; 09-28-2003 at 03:13 AM.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  16. #41
    Xtreme Member
    Join Date
    Sep 2003
    Location
    Austin, Texas
    Posts
    386
    Hi Cappy! :-)

    This is the first time I have browsed your entire thread. I noticed something in one of your pics. Your TEV cover cap on your expansion valve is missing. the TEV should be operated with the cap on the valve. Not to get off on the wrong foot, but you will be interested in the following phenomenon:

    Try this sometime. check your superheat (in whatever manner you do - multiple temperature, or temperature/pressure) and remove the cap on the TEV. See what happens. Then put the cap back on and see what happens. The cap serves NOT to keep the valve from leaking (the adjustment stem packing serves that job), but to insulate the adjustment stem from the ambient temperature [also] (if you wish to speculate that it is a secondary leak protection). The stem will conduct the ambient heat into the valve body and affect your superheat setting.

    After making a TEV adjustment, you should always re-install the cap (even just finger tight will suffice between adjustments) and allow the valve to "settle in", before checking and making any other adjustments. I just thought that you would find that interesting. If you try what I say, your lightbulb will come on.

    Anyway, I have a few questions for you. One will not find compressors rated for, say R-170 @ -80F. What is the criteria of compressor selection for these cryogenic refrigerants and applications?

    I have (re)charged the second stage of a cascade, only once. It was refrigerant grade ethane, I believe. It was contained in a silver high pressure gas cylinder (like an oxygen bottle, ya' know) with a blue cap. Could you possibly confirm the refrigerant I was using (it was 8 years ago). the charging was accomplished by hooking up the bottle, and letting the system stand for 12hrs @ 75F room temperature at a particular pressure (75psi, or something like that).

    If I build a cascade, I would like to utilize R-404A first stage, and ethane for the second stage. I don't suppose that R-23, 508B, or any of the refrigerants that you have posted the properties of would have lower stauration temperatures than the ethane, if I recall my browsing of P/T charts properly.

    I am of the opinion that a couple of my tecumseh TPA1390 compressors, back to back, first stage @ 0F to -10F, R-134A @ 950btuh, cooling the second stage, ethane @ ??F (don't have P/T chart, now) anticpated 400btuh (150watt), may serve the task. what do ya' think?

    I might point out, in regard to the pump-down type systems, and the application of receivers, that these configurations are not utilized with cap-tube applications. Cap tube systems are "critically charged". I noticed that you are using TEV's, as such receivers and pump-down are good practice (you must use a receiver with a TEV for proper operation).

    Anyway, your insight in regard to compressor selection and ethane refrigerant thingie would be greatly appreciated.

    see ya'

  17. #42
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    loyd


    if i run my outlet off the top of the condenser. Am i looking a a potential place for oil to sit? on the bottom part of the condenser?

    herefishy

    yer dam right about the txv. didnt even think about it. good lookin out man thanks. please if any of you see something wrong , let me know. im pretty dam far from perfect.

    we retrofit 95 in 170 systems without any problems

    170 is grey/silver bottle, yeah id say thats what ya got.

    i think 170 is alot like 503.

    its kind of a rollin of the dice, to pick a suitable compressor. if you look on the wich compressor for cascade systems thread, i posted some model #s

    id say go for it, just make sure your 1st stage works right. before turning on your second
    If i was an animal Id be a freezer.

  18. #43
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    try to keep in mind i made this cascade system in less than 24 hours. the cap tube baker has is to small and to long. but the block kicked but. the coldest we got it was -55. ill shorten the cap and we'll get -80 no prob



    im not even going to tell you my 2nd stage head pressure.
    Last edited by captaincascade; 09-28-2003 at 09:31 AM.

  19. #44
    Xtreme Member
    Join Date
    Sep 2003
    Location
    Austin, Texas
    Posts
    386
    Originally posted by captaincascade
    its kind of a rollin of the dice, to pick a suitable compressor. if you look on the wich compressor for cascade systems thread, i posted some model #s

    id say go for it, just make sure your 1st stage works right. before turning on your second
    10-04 dude,

    I think that I will employ either a thermostat on the interstage heat exchanger, in order to control the second stage. either that, or a high-side pressure control on the second stage. I think the second-stage high-side pressure would be best, I'm thinking as I type. Any thoughts?

    see ya'

  20. #45
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    http://www.xtremesystems.org/cc/cas7.jpg

    i made a ladder diagram of simple wiring

    see if it makes sense
    If i was an animal Id be a freezer.

  21. #46
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    you can even use a low side pressure cut in on first stage to turn on second stage.

  22. #47
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    if i run my outlet off the top of the condenser. Am i looking a a potential place for oil to sit? on the bottom part of the condenser?
    Read my post again. Outlets top AND bottom.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  23. #48
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    ohhhhhhhhhhhhhhhhhhhhhhhh it is a serpentine condenser.....are you asking if its a paralel flow condenser?

    so you guys keep up with what we're talking about.

    http://www.narsa.org/acj/archive/acj...AC%20focus.pdf


    idea....
    what kind of reluts do you think id get, say,... if i were to use a paralell flow condenser, and i tried to use it as the phase seporator and condenser,,, ataching the inlet in the middle or top lets say and pipin the hot gas off the top of the thing and pipin the liquid from the bottom

    do you think i could use it as a phase sep and condenser?
    it doesnt sound right to me. hmmmmmmmm....loyd.
    Last edited by captaincascade; 09-28-2003 at 07:58 PM.
    If i was an animal Id be a freezer.

  24. #49
    X.I.P.
    Join Date
    Jul 2003
    Location
    Darby FL, USA
    Posts
    2,115
    Actually, I think the condenser and separator have to be combined, because the condensing causes the separation.


    Author - Refrigeration Trouble Shooting Books

    Want to learn more? Click Here

  25. #50
    Freezer Racer
    Join Date
    Sep 2003
    Location
    la,ca
    Posts
    608
    this is the same design condenser as on the auto cascades i work on. but i see what you mean.
    If i was an animal Id be a freezer.

Page 2 of 10 FirstFirst 12345 ... LastLast

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •