  1. #126
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Excellent work! If only 1/2" benders weren't $100!


    If you have a cooling question or concern feel free to contact me.

  2. #127
    INTEL inside
    Join Date
    Oct 2004
    Location
    Québec, Canada
    Posts
    3,258
    wow, subscribed

    too bad we don't have ultra low temperature class at school, only "big/commercial" refrigeration.
    retired computer enthusiast

  3. #128
    -100c Club Member
    Join Date
    Apr 2003
    Location
    Riverside, California
    Posts
    4,740
    Quote Originally Posted by mytekcontrols View Post
    Something like Noranda makes. Yes it has excellent heat exchange, but sometimes the small passageways can hold on to oil in the wrong place, and next thing you know, you're blocked by frozen oil. I think it was about 21 years ago we tried building an entire stack with this tubing. It worked great for a few hours, and then suddenly started loosing capacity. It would freeze up about 2/3 up from the bottom.

    Of course this was before we ever heard of a coalescing oil filter such as what Temprite makes. And we also didn't know it until much later, that the new compressor we were using was a major oil pumper. Had to get the manufacturer to add a 3rd ring for oil control.
    Yes I can see that but there are perpendicular as well as horizontal finned tube Perpendicular one I can see problem but horizontal one might not have that...
    [SIGPIC]http://www.vapoli.com/Images/Forum/vapoli.jpg[/SIGPIC]

    Single Stage Work Logs

    Quote Originally Posted by killermiller View Post
    Those ccb's will die if you look at them wrong.

    heatware: jinu117

  4. #129
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    No doubt, time to get r23 me thinkies
    And watching with incredible rapt attention, do you think those capillary lengths are good though? Any reason to them or calculation? Seem sorta long after reading other lengths from Cryo-Tek.


    If you have a cooling question or concern feel free to contact me.

  5. #130
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    ...do you think those capillary lengths are good though? ...Seem sorta long after reading other lengths from Cryo-Tek
    Actually they have slightly more flow then what I calculated from Cryo-Tek's example. Remember that the system that Cryo-Tek's captubes were specified for has a compressor with 3.6 times the displacement of mine.

    If you are concerned about the length, also remember that I am using all the same ID captube. Cryo-Tek's example was using several different ID's, which is fine if you have many different ones to chose from. I tried to keep it simple by only using a single ID and ordered a 100 foot roll. Also keep in mind that captubes work best when the length is kept somewhere between 5 and 15 feet. Less then 5 feet starts to act more like an orifice, and can produce greatly different flow rates with only a few inches of change.

    No doubt, time to get r23 me thinkies
    Ethane works just as well, and can be used as direct substitute (might be cheaper).
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  6. #131
    Xtreme Member
    Join Date
    May 2007
    Posts
    251
    Quote Originally Posted by mytekcontrols View Post
    The first 2 heat exchangers (aux and 1st cascade) have 2 inner tubes which are part of the discharge (or high pressure circuit).
    That explains it. Cheers Michael, that HX is really nice looking too
    PC: Intel E8400
    MB: Asus P5k
    PSU: OCZ StealthXStream 600w
    GPU: XFX XXX 8800GT
    Monitor: Samsung Pebble 17"
    Cooling: XSPC Water cooling custom
    HDD: 160GB Seagate
    RAM: OCZ PC8000 Platinum XTC

  7. #132
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Nah ethanes more expensive it would seems.
    Well no actually hmm, just checked matheson...
    $100 will get me 3lbs of ethane. Is it just as good as r23? I'd imagine since its lighter it might not be able to hold a load as well. Also, what about ethylene? would r170/r1150 work decently theroetically?
    Last edited by n00b 0f l337; 11-25-2007 at 06:32 AM.


    If you have a cooling question or concern feel free to contact me.

  8. #133
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    That explains it. Cheers Michael, that HX is really nice looking too
    Thanks Freddie I'm glad you brought it up. Often times I find it helps me do a better job at documenting a project, when people ask me to explain different aspects of it. Thanks also for your appreciation of the HX, because it was a bit of a struggle to build it that way. It sure would have been nice if the lever bender I was using, could have been separated into 2 parts after doing each bend. I'm almost wondering if I could make my own bender from something like a pulley.

    $100 will get me 3lbs of ethane. Is it just as good as r23? I'd imagine since its lighter it might not be able to hold a load as well. Also, what about ethylene? would r170/r1150 work decently theroetically?
    I do believe ethane (R-170) works just fine as a substitute for R-23, boiling points are virtually the same, and on the positive side it has better solubility with the oil. I made up a charge last week for a large Polycold unit I was working on, and increased the ratio of ethane as compared to the R-23 (15 psi R-23, 65 psi ethane) it worked quite fine, and even exceeded specification. I suspect I could have just gone with 80 psi of ethane, and eliminated the R-23 all together (have to try that some day).

    As for ethylene (R-1150) being used in combination with the ethane, yes this would also be a viable mixture, although it wont get you quite as cold as using R-14 which boils 15C colder (R-1150 = -104C, R-14 = -120C).

    Edit: Correction, R14 boils at -128C.
    Last edited by mytekcontrols; 10-03-2010 at 08:51 AM.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  9. #134
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Well what about r14 in combination.


    If you have a cooling question or concern feel free to contact me.

  10. #135
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Well what about r14 in combination.
    No benefit in using R-1150 (ethylene) and R-14 together.

    Edit (10/10/2009): I have recently discovered that R1150 and R14 can play well together. Of course this depends upon what other refrigerants are being used in combination with, and how many stages are in the AutoC. Under the right conditions, the R1150 and R14 combo will yield evaporator temperatures with a smaller gradient from the the inlet to the outlet.

    However R-170 (ethane) and R-14 would be fantastic
    Last edited by mytekcontrols; 10-10-2009 at 06:04 AM.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  11. #136
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Just trying to see what might be decent with what I have
    Hmmm r170 or r23....


    If you have a cooling question or concern feel free to contact me.

  12. #137
    Diablo 3! Who's Excited?
    Join Date
    May 2005
    Location
    Boulder, Colorado
    Posts
    9,412
    I'm going to see what Airgas will do with me tomorrow for R1150/R170, just opened an account with them and crossing my fingers that they'll be able to supply me with decent prices.

  13. #138
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Mathesons got good selection and great prices, but that hazmat fee is driving me nutters.
    They have good prices on ethane, argon, butane hell just about everything.


    If you have a cooling question or concern feel free to contact me.

  14. #139
    Xtreme Enthusiast
    Join Date
    Feb 2004
    Location
    Netherlands
    Posts
    757
    I tried r1150 in an autocascade but didn't have good results with it. r170 works much better. I think the leap between r290/r507 etc and r1150 is too big.

  15. #140
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    I dont think its so much the leap as the lack of a gas like r11 or r123 that killed your setup thuogh Unknown.


    If you have a cooling question or concern feel free to contact me.

  16. #141
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    How about a $4.00 3/8" od tubing bender? Only took a slight modification of an off-the-shelf 3" garage door pulley (used file to elongate holes in bracket). It works great for making a trombone style heat exchanger, clamp the pulley's shaft nut in a vice, and just walk the part you are bending around the pulley.

    The v-shaped pulley helps to prevent the tubing from flattening out, and the bend radius = 1.5" which matches the one on my 1/2" bender. This ends up producing a better match for the 1/2" od heat exchangers, and allows it to sit perfectly on top of them (makes for a cleaner stack). So I'll be scrapping my original concept drawing for Cascade #2 and #3. I will provide details later.

    Well here it is:
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	pulley-bender1.jpg 
Views:	1087 
Size:	46.8 KB 
ID:	67845   Click image for larger version. 

Name:	pulley-bender2.jpg 
Views:	1085 
Size:	30.3 KB 
ID:	67846   Click image for larger version. 

Name:	pulley-bender3.jpg 
Views:	1071 
Size:	23.8 KB 
ID:	67847   Click image for larger version. 

Name:	pulley-bender4.jpg 
Views:	1071 
Size:	55.6 KB 
ID:	67848  
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  17. #142
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Here's a close-up of the completed pulley bender. The slot allows you to adjust the bracket for a tight fit on the tubing, this helps prevent the tube from kinking. The secret to using it, is to try and keep the part you are bending underneath the bracket, and maintain tension on both sides of the tubing (It can be a little tricky at first).
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	pulley-bender5.jpg 
Views:	1138 
Size:	30.9 KB 
ID:	67850  
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  18. #143
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    And here's what the first HXC produced with the pulley bender looked like (I miscalculated on the length, so ended up adding a swaged extension tube to make it right).

    Edit: You'll notice that I reduced the number of turns by one from my original drawing. I needed the extra room, and felt that a little less length on the last 2 cascades was acceptable.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Cascade2-3.jpg 
Views:	1401 
Size:	38.9 KB 
ID:	67854  
    Last edited by mytekcontrols; 11-26-2007 at 12:19 AM.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  19. #144
    Xtreme Member
    Join Date
    Jul 2007
    Location
    Munich, Germany
    Posts
    400
    Reminds me of Tim Tayler on "Tool Time"

    Great work! I look forward every morning to looking on this thread!

    Regards,

    Philipp

    PS: I am planning on an autocascade in a very similar way like your drawing (I studied all the old threads by you and Cryo-Tek). Now that I have a starting point about capillary length (thanks to you), I think about the charge. How do you charge a unit like this? Do you mix the gasses up previously in an empty bottle and then charge from there or do you charge one refrigerant at a time up to a certain pressure? Or do you charge a unit while running up to certain points, eg. Ref#1 until HX#1 reaches -XX degrees, then Ref#2 until HX2 reaches -xx deg. and so on? I would appreciate the info very much.

  20. #145
    -150c Club Member
    Join Date
    Dec 2006
    Location
    Santa Rosa, California
    Posts
    819
    Reminds me of Tim Tayler on "Tool Time"
    I wonder if Binford ever made an autocascade? If they did, you know it would be powerful and get very very cold
    Great work! I look forward every morning to looking on this thread!
    I'm glad you are enjoying it
    How do you charge a unit like this?
    If you have an electronic scale, and your unit is not too heavy:
    • Place the unit on the scale
    • Zero the reading
    • Charge in your 1st, 2nd, 3rd... liquid refrigerant (R123,R22,ect.) into discharge side only
    • When all liquids have been charged, open all valves on manifold, allow pressure to balance, take pressure reading
    • Add gases by pressure (allow 5 minutes for soak-in before going on to next gas, top off if needed, wait another 5 minutes, and repeat top off if needed --- repeat until pressure no longer drops)


    If your unit is too heavy for a scale, then use a cylinder as a transfer tank. Same procedure as above, but when adding gases shake the cylinder to speed up soak-in.
    Do the following when the entire charge has previously been put into the transfer cylinder:
    • Connect hose from cylinder to unit
    • Open valve, purge line with refrigerant
    • Invert cylinder (for liquid), and open discharge valve only on manifold
    • When flow slows down, open all valves on manifold and allow pressure to balance
    • If compressor has suction valve, front seat it and close off discharge valve on manifold
    • Run compressor and allow it to suck in remaining gases from cylinder


    If you have a charging glass instead of an electronic scale, you can pre-charge the glass with the liquids, add them first, and then proceed with the gases, same as was done in the first example.

    If your system has an expansion tank, you'll need direct access to it when adding your gases (a way to bypass the restrictive captube).

    Of course this all assumes that you know what your total charge is going to be. When first developing the charge, you'll want to start out with about 2/3 of what you think you'll probably need. Later when the system is running, and based on temperatures seen at the exit of each heat exchanger, you can test adding small amounts of the different refrigerants. If the compressor discharge is running hot (0ver +125C), then very slowly add in additional liquids an ounce at a time through the suction port.

    When adding gases, it is good to add these from a standard size cylinder with a known volumetric ratio as compared to the system volume.
    For instance; before charging your refrigeration system, fill a small cylinder with nitrogen or argon to 100 psi. Put a gage on the cylinder, and a gage on the refrigeration system. Allow gas to flow from the cylinder into the refrigeration system until the system pressure has gone up 5 psi, and then stop the flow. Take note of how far the pressure has dropped in the cylinder (i.e.; dropped from 100 to 85, or 15 psi). Now you have a way to measure in a specific amount of gas (every 15 psi taken out of the cylinder will equal a 5 psi increase in the refrigeration system's static balance pressure). Of course this would be added into the suction side of a running unit.

    Later as I get into the charging phase of my unit, I'll give you the refrigerants and amounts I will be starting out with (haven't gotten that far yet).

    Have I forgotten anything? It's late, so my mind is getting a bit fuzzy, and this is a lot of stuff to cover.
    Michael St. Pierre

    • Worked 15 years for Polycold Systems
    • Now Self-Employed
    • Manufacture Heat Load Controllers
    • Also do contract service work on Polycold units

    Side note: I usually don't respond to PM's or emails regarding the projects that I post in the forums. I feel it's much more fair to all, to answer questions within the forum topics themselves.

  21. #146
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Picked up a 4" garage pulley and damn your right, just what I've been looking for!


    If you have a cooling question or concern feel free to contact me.

  22. #147
    Here to help
    Join Date
    Nov 2002
    Posts
    1,977
    Isnt the internal volume of those bullet strainers too low? Flow rates through a low volume tube like that would be too high to allow for phase seperation, wouldnt they?

    Or are these bullet strainers larger than we are used to seeing?

    Regards

    John.

    Edit: Meant refrigerant stream velocity, not flow rate.
    Last edited by pythagoras; 11-26-2007 at 05:09 PM.

    "Thermodynamics is a funny subject. The first time you go through it, you don't understand it at all. The second time you go through it, you think you understand it, except for one or two points. The third time you go through it, you know you don't understand it, but by that time you are so used to that subject, it doesn't bother you anymore".

  23. #148
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    I think we've been overestimating the need for this kind of separation. If you have a liquid seal at the bottom, gas will leave gas passage


    If you have a cooling question or concern feel free to contact me.

  24. #149
    Here to help
    Join Date
    Nov 2002
    Posts
    1,977
    Quote Originally Posted by n00b 0f l337 View Post
    I think we've been overestimating the need for this kind of separation. If you have a liquid seal at the bottom, gas will leave gas passage
    But liquid droplets can leave at gas outlet if the velocity isnt slowed or the droplets hit an impingement screen. And gas disolved in liquid will escape the liquid seal if not given enough time to come out of suspension

    Regards

    John.

    "Thermodynamics is a funny subject. The first time you go through it, you don't understand it at all. The second time you go through it, you think you understand it, except for one or two points. The third time you go through it, you know you don't understand it, but by that time you are so used to that subject, it doesn't bother you anymore".

  25. #150
    -150c Club Member
    Join Date
    May 2005
    Location
    Northeast, USA
    Posts
    10,090
    Which is true, but the way his seps are setup the mix comes in and heads to the bottom, a liquid seal is then created.


    If you have a cooling question or concern feel free to contact me.