    Views
    12,572

    Sorry folks, I was on my way to solving the...

    Sorry folks, I was on my way to solving the problem until the company from which I've ordered the service kit and spare valve decided to put my order on hold due to an obsolete part number.

    That's...
  2. Replies
    7
    Views
    12,572

    Ok. No thanks to Parker, I found myself a...

    Ok. No thanks to Parker, I found myself a solenoid valve repair kit. I'm gonna crack the thing open and check for blockages, etc.

    I've also gotten a back-up TXV if that needs to be replaced as...
  3. Replies
    7
    Views
    12,572

    And FYI, I decided to make it official and buy a...

    And FYI, I decided to make it official and buy a recovery machine and cylinder instead of borrowing.

    Borrowing has worked out in the past.... but I'd rather have ready access.
  4. Replies
    7
    Views
    12,572

    Always fine with people throwing ideas on the...

    Always fine with people throwing ideas on the wall. :)

    I'm mostly disappointed that I didn't check the solenoid valve and decided to go ahead with the redesign and rebuild of the liquid line. As...
  5. Replies
    7
    Views
    12,572

    I thought about it.... :p: Time to recover...

    I thought about it.... :p:

    Time to recover refrigerant and check the TXV and Solenoid valves like I should have before... After thinking about why the liquid injection worked, that told me the...
  6. Replies
    7
    Views
    12,572

    In retrospect, it may have been wise to replace...

    In retrospect, it may have been wise to replace the TXV just to be safe... but I didn't... and so it goes...

    Liquid Pressure: 325PSI
    Suction Pressure: 70PSI
    Superheat: 8-10F

    I experimented...
  7. Replies
    7
    Views
    12,572

    Rebuilt - Repeat Problem

    Ok, so I've finally recharged and started back with testing. The same problem has presented itself.

    When the sight glass was still bubbling, the liquid pressure was climbing above 300PSI, Suction...