I added more liquid refrigerant on the high side until it would not take anymore, the superheat only got to 16.9C. and the suction line stop sweating. The TXV is a Sporlan FSE-1/2-ZP and my compressor 1/2HP, so I think the TXV is sized correctly.
Yes, the pressures are different...this is what I have this morning with the system off.
Attachment 76035
I'm not sure what the load is for the pump....I'll do a test to find out.
By the way guys, I appreciate your advice and help. :D