Does it matter which ends of tubing you swag when you make the connections.
Also I a bit confused how the 3/8's evap coil I'm going to use is plumbed I'm going with a TXV
http://img218.imageshack.us/img218/1755/expansionvalve3od.jpg (http://imageshack.us)
I'm not sure where the small 1/4 fitting on the valve goes to.
expansionvalve
12-13-2005, 03:41 AM
The 1/4 fitting on the valve needs to be connected to an access port on the evap outlet/suction pipe close by the tev bulb, something like the picture..
the valve you have is externally equalised thus the 1/4 fitting.
if it was a ts2 it would be internally equalised with no 1/4 fitting.
catkicker
12-13-2005, 04:05 PM
Ok. Now in the diagram it shows the 1/4" access port on the evap located between the TEV Bulb and compressor.. How close should it be to the bulb?
http://img527.imageshack.us/img527/4471/txvinstaldiagram0cl.jpg (http://imageshack.us)
and should I run the 3/8" tubing(suction line) all the way to compressor and then reduce it to
connect to compressor.
Another question as far as schrader valve placement I have one on the compressor and one should be placed just before condensor. Should I install any others for checking presures?
expansionvalve
12-15-2005, 03:57 AM
hi, I would look into fitting 1/4 access valve within inches of the tev bulb.
I can't say for 100% your system will be good for 3/8 suction to compressor. I know very little about your system, what I can say is, I run 3/8 back to compressor and it's fine for me, 134a 1/3hp>1/4 liquid line>tev>twin coil 1/4evap>3/8 suction to compressor.
schrader valves, well at very minimum I'd go one suction on the compressor, one discharge on discharge line somewhere, for tweaking/setup I would also put another valve right by the tev bulb so thats two there now and one on the liquid line, that's how i'd go about it.
catkicker
12-17-2005, 08:01 PM
Thank's for the info.