View Full Version : waterchiller problem


Dimas
11-22-2004, 08:18 AM
Hi, i've i little problem with my killer, the evap don't gets all cold with ice, i used a 5 meters of 0,9mm capillary tube.
http://dimas.altervista.org/foto/giac.jpg
http://dimas.altervista.org/foto/sys2.jpg
another thing my red manometer don't move, what can i do for check if it are broke.
i let the sistem run with r404 and i get temp lower than -49.9(:banana::banana::banana::banana: termomether),room temp about 10 degrees C.
bye and thanks

berkut
11-22-2004, 08:55 AM
Shorten the cap tube to about 2-3m.

Malachia
11-22-2004, 09:18 AM
capillary is too big and can't reggere the temps when charged!

eh che ci vuoi fa se nn mi ricordavo l'inglese :D




x berkut

i have found CO2 in bottles like MAPP, do you think it's ok to use by expanding it in a phase change sistem?

Dimas
11-22-2004, 09:46 AM
ok, i'll do but how many watts i can dissipate with 3 mt capillary tube?
malachia anche tu qui??azz mi hai scoperto :D
bye

berkut
11-22-2004, 10:17 AM
you can not use CO2 in a normal cooler

Malachia
11-22-2004, 10:46 AM
you can not use CO2 in a normal cooler


well i want to simply expand it in a block and then loose it...not a circuit like phase changes...i founded a bottle big like mapp gas at 13€...

gkiing
11-22-2004, 10:48 AM
Where did you find Co2 in a mapp gas bottle???? i desperatly need some.

Malachia
11-22-2004, 10:50 AM
Where did you find Co2 in a mapp gas bottle???? i desperatly need some.


well if you come to milan :D


i found in a mega-store all for bricolage...

cold_ice
11-22-2004, 11:11 AM
Where did you find Co2 in a mapp gas bottle???? i desperatly need some.
Go to a DIY store (don't know if this is the right word), you may find little bottles with CO2 there.
Here in Austria they look like the first grey bottle:
http://www.cfh-gmbh.de/bild/gasloeten/52512.jpg

Dimas
11-22-2004, 11:27 AM
someone can help me with the high side manometer??when i charge for check leaks it works, after opening the low side for charging it stops working.

gkiing
11-22-2004, 06:04 PM
Are you using a professional manifold gauge? If the manifold is malfunctioning you may need to change the gauge for a new one or get a new manifold.

Dimas
11-22-2004, 09:32 PM
it have four ways ref ,low, vac, high.
bye

gkiing
11-22-2004, 09:38 PM
When you want to charge connect the low side and high side hoses to your system, the vac to your vacuum pump, and the ref to your tank of refrigerant.

Open ALL the valves on the manifold (but dont open the valve on the refrigerant tank)

Vacuum the system for an hour.
Close the vacuum valve
Open the refrigerant tank valve so that the pressure rises up to Opsi
Close the refrigerant valve
Open vacuum valve
Vacuum for another hour
Close the vacuum valve
Open the refrigerant tank valve so the manifold reads 0psi again
Close the refrigerant tank valve
open vacuum valve
Vacuum for 2 hours
Close the vacuum valve
Close the High side (red) valve
Start up the system (the only valves open now are the refrigerant and the low side)
Slowly add refrigerant to the system until the suction pressure reaches about 4" of mercury.

This is what I do and I havent had any problems with moisture or charging.

Dimas
11-23-2004, 06:23 AM
ok, i understand, i do the same thing but i switch vacuum pump with the ref tank, i don't use an entry(the ref), because i haven't a hose. so if the red don't move, probably will be broke??
bye

gkiing
11-23-2004, 02:50 PM
If your red valve wont move its probably broken. I suggest that you get a new manifold. Ritchie yellow jacket and robinair make good manifolds, you might want to look into them.

kayl
11-23-2004, 03:15 PM
someone can help me with the high side manometer??when i charge for check leaks it works, after opening the low side for charging it stops working.

you may need to adjust the valve in the red hose.
look inside it the little metal pin might not be stick out enough to depress the valve to take a pressure measurement, its happened to me when i changed the rubber seals in the hoses.
Never know it could be that simple

gkiing
11-23-2004, 09:22 PM
you may need to adjust the valve in the red hose.
look inside it the little metal pin might not be stick out enough to depress the valve to take a pressure measurement, its happened to me when i changed the rubber seals in the hoses.
Never know it could be that simple

Yeah, shrader valves and depressors are picky things. Just dont push the shrader valve in if theres presure in the system otherwise the gas will escape and hit you in the face (i know from experience... always look away from the shrader when disconnecting your gauges.)

Dimas
11-23-2004, 09:34 PM
i know, already tried, it is not so beautiful :D, red manifold now is ok, now i go for leaking another time and then charge, thanks at all
bye

Dimas
11-25-2004, 03:59 AM
Hi, after leaking test pressurizing system and shave foam, i've charged the system, temperature go down very slow, and after 1 hour with no load i get -23.
temp amb is around 10 degrees.
low side pressure -3.63 psi(down 2 from the 0 i hope)
high side pressure 130.9 psi
3mt of 0.036 cap tube

DGeNeRaT3
11-25-2004, 05:11 AM
I would think you should get lower temps than that. What Gas are you charging with?

Malachia
11-25-2004, 05:20 AM
I would think you should get lower temps than that. What Gas are you charging with?


i think r404a....then dimas try to have low pressure side at -0,1bar ;)

Dimas
11-25-2004, 05:55 AM
yes,now i have -0.1 bar and on the high side i have 123,25 psi,i'm using this compressor: TECUMSEH thb1355ys lra 10.0 fla 0.88 R134 about 122 watt