View Full Version : Expansion Valve Orifice choice



supercoolin
02-07-2009, 11:04 PM
I am starting to build a little cascade system to run my Phenom II around -50 -60C under full load (will run 5-6hrs loaded, so hose temps are easy to insulate) and I have picked up a Danfoss TUA expansion valve. I will be running a 700BTU @ -40C compressor on HC502a for the first stage and have picked up a #2 orifice set. If any one has used one of the these expansion valves and possibly has a recommendation if this is the wrong choice, it would ba appreciated.

teyber
02-07-2009, 11:40 PM
no idea but with a decent sized compressor dual stage cascade in the past most people use a 00 but thats with a ts2/tes2, im sure they are the same

EvoCarlos
02-08-2009, 04:01 AM
I am starting to build a little cascade system to run my Phenom II around -50 -60C under full load (will run 5-6hrs loaded, so hose temps are easy to insulate) and I have picked up a Danfoss TUA expansion valve. I will be running a 700BTU @ -40C compressor on HC502a for the first stage and have picked up a #2 orifice set. If any one has used one of the these expansion valves and possibly has a recommendation if this is the wrong choice, it would ba appreciated.

i agree with reed most people use the ts2/tes2 for r404/r507 txv with ether a 0X-00 orifice on the 1st stage.

tua N range valve w/0 orifce @-40c is rated @ 0.34kw from the documetation
page 7 http://rc.danfoss.com/TechnicalInfo/literature/manuals/01/DKRCCPDAG0A202.pdf

but depends on what valve type you have and gas type in bulb
on another note the tua rage dont do a r502 txv
have a look around the pdf above it should shed a bit more light for you
carl...

-EC-UnRockStar
02-08-2009, 04:14 AM
i used a 05 orifice on the 1st stage. :D

teyber
02-11-2009, 09:58 PM
i used a 05 orifice on the 1st stage. :D

05 for the 5 stage :p: did you use a 4 on the second stage? :shrug: jk