Compressor
Compressor will not run. Does not try to start.
1. Main power switch open.
2. Fuse blown or tripped circuit breaker.
3. Thermal overloads tripped.
4. Defective contactor or coil.
5. System shut down by safety devices.
6. Open thermostat or control. No cooling required.
7. Liquid line solenoid will not open.
8. Loose wiring.
Compressor hums, but will not start.
1. Improperly wired.
2. Low line voltage.
3. Loose wiring.
4. Defective start or run capacitor.
5. Defective start relay.
6. Motor windings damaged.
7. Internal compressor mechanical damage.
Compressor starts, but trips on overload protector.
1. Improperly wired.
2. Low line voltage.
3. Loose wiring.
4. Defective start or run capacitor.
5. Defective start relay.
6. Excessive suction or discharge pressure.
7. Tight bearings or mechanical damage in compressor.
8. Defective overload protector.
9. Motor windings damaged.
10. Overcharged system.
11. Shortage of refrigerant.
12. Suction or discharge pressure too high.
13. Inadequate ventilation.
14. Operating system beyond design conditions.
Compressor short cycles.
1. Low pressure control differential set too low.
2. Shortage of refrigerant.
3. Low airflow at evaporator(s).
4. Discharge pressure too high.
5. Compressor internal discharge valves leaking.
6. Incorrect unit selection (oversized).
Contact welded stuck on start relay
1. Short cycling.
2. No bleed resistor on start capacitor
Start capacitor burns out
1. Improperly wired.
2. Short cycling.
3. Low line voltage.
4. Relay contacts sticking.
5. Incorrect capacitor.
6. Start winding remaining in circuit for prolonged period.
Compressor noisy or vibrating.
1. Flood back of refrigerant.
2. Improper piping support on the suction or discharge lines.
3. Broken or worn internal compressor parts.
4. Incorrect oil level.
5. Scroll compressor rotating in reverse (three phase).
6. Improper mounting on unit base.
Discharge pressure too high.
1. Non-condensables in the system.
2. System overcharged with refrigerant.
3. Discharge service valve partially closed.
4. Condenser fan not running.
5. Dirty condenser coil.(air-cooled condensers)
6. Dirty tubes. (water-cooled condensers)
7. Defective or improperly set water regulating valve. (water-cooled condensers)
8. Defective or improperly set flooded head pressure control.
Discharge pressure too low.
1. Low suction pressure.
2. Cold ambient air.
3. Suction service valve partially closed.
4. Shortage of refrigerant.
5. Defective or improperly set water regulating valve. (water-cooled condensers)
6. Defective or improperly set flooded head pressure control.
Compressor will not run. Does not try to start.
1. Main power switch open.
2. Fuse blown or tripped circuit breaker.
3. Thermal overloads tripped.
4. Defective contactor or coil.
5. System shut down by safety devices.
6. Open thermostat or control. No cooling required.
7. Liquid line solenoid will not open.
8. Loose wiring.
Compressor hums, but will not start.
1. Improperly wired.
2. Low line voltage.
3. Loose wiring.
4. Defective start or run capacitor.
5. Defective start relay.
6. Motor windings damaged.
7. Internal compressor mechanical damage.
Compressor starts, but trips on overload protector.
1. Improperly wired.
2. Low line voltage.
3. Loose wiring.
4. Defective start or run capacitor.
5. Defective start relay.
6. Excessive suction or discharge pressure.
7. Tight bearings or mechanical damage in compressor.
8. Defective overload protector.
9. Motor windings damaged.
10. Overcharged system.
11. Shortage of refrigerant.
12. Suction or discharge pressure too high.
13. Inadequate ventilation.
14. Operating system beyond design conditions.
Compressor short cycles.
1. Low pressure control differential set too low.
2. Shortage of refrigerant.
3. Low airflow at evaporator(s).
4. Discharge pressure too high.
5. Compressor internal discharge valves leaking.
6. Incorrect unit selection (oversized).
Contact welded stuck on start relay
1. Short cycling.
2. No bleed resistor on start capacitor
Start capacitor burns out
1. Improperly wired.
2. Short cycling.
3. Low line voltage.
4. Relay contacts sticking.
5. Incorrect capacitor.
6. Start winding remaining in circuit for prolonged period.
Compressor noisy or vibrating.
1. Flood back of refrigerant.
2. Improper piping support on the suction or discharge lines.
3. Broken or worn internal compressor parts.
4. Incorrect oil level.
5. Scroll compressor rotating in reverse (three phase).
6. Improper mounting on unit base.
Discharge pressure too high.
1. Non-condensables in the system.
2. System overcharged with refrigerant.
3. Discharge service valve partially closed.
4. Condenser fan not running.
5. Dirty condenser coil.(air-cooled condensers)
6. Dirty tubes. (water-cooled condensers)
7. Defective or improperly set water regulating valve. (water-cooled condensers)
8. Defective or improperly set flooded head pressure control.
Discharge pressure too low.
1. Low suction pressure.
2. Cold ambient air.
3. Suction service valve partially closed.
4. Shortage of refrigerant.
5. Defective or improperly set water regulating valve. (water-cooled condensers)
6. Defective or improperly set flooded head pressure control.