This is my latest project, it’s a lot bigger and much more different than the normal units we all see, My thinking behind it was to have two condensers with the 93cfm fans blowing from either side to try and keep the compressor and gass nice and cool as you will see I have made a small SLHX and hope to have the unit running a mixture of R402a and R410a which will make things run that bit hotter than normal.
The unit is not finished yet as I am still awaiting Chilly1’s new evap, once this has been fitted and pressure tested I will then do some more paintwork to the compressor and some pipe work.
As you will see i have made two trunking compartments for all the cabling, one section for 240v and another for data and ELV cables, the system is fully protected to 16th edition wireing regs has thermal and overcurrent protection,it also has a safty presuer cutoff switch incase the presuer gets above the set limit.
A Big thanks to SoddemFX for all his input and help
Anyway that’s enough waffle hears some pics.
http://img356.imageshack.us/img356/9707/phasesetupev7fi9.jpg
http://img138.imageshack.us/img138/1027/pict0068do4.jpg
http://img341.imageshack.us/img341/7292/pict0130ki3.jpg
http://img135.imageshack.us/img135/8901/pict0136mo6.jpg
http://img150.imageshack.us/img150/3237/pict0137hb8.jpg
http://img341.imageshack.us/img341/7800/pict0141wd5.jpg
http://img135.imageshack.us/img135/901/pict0143yq6.jpg
http://img142.imageshack.us/img142/8886/pict0144mm1.jpg
http://img89.imageshack.us/img89/5000/pict0146ae1.jpg
Sacha
{.bLanK} GoD
03-17-2007, 02:35 AM
Very clean.
I think I like it ;)
I'm looking forward to seeing some results.
Brettbeck
03-17-2007, 03:03 AM
Yeah very clean :D. How long did you spend cleaning the brazed joints hehe :p:?
So is it basicly a single stage? The design seems a bit confusing :confused: . Or maybe it's just me (just woke up). I will read it again later see if I can make more sense lol :).
aasmaukr
03-17-2007, 03:06 AM
Good-looking :D
LittleDevil
03-17-2007, 03:26 AM
Nice project ;)
Regards
jimmsch
03-17-2007, 03:31 AM
Love the case. Too bad it is so....HUGE! Looks great though.
sacha35
03-17-2007, 04:51 AM
Thanks for your coments Guys, yes this is one big case,big enough to build a small cascade, but as said this unit will be running hot so i wanted to have plenty of space for cooling and to be able to enclose all cables and control gear in protective trunking, as you see i have two condensers to increase the volume and also the way i have laid this out at 45 degree angle will allow the two 93cfm fans to cool the refrigerant and hopfully keep the compressor nice and cool.
Sacha
Marvin
03-17-2007, 05:41 AM
nice case. I like the condensers displacemant too.
Looks like a shark:banana:
Clemmaster
03-17-2007, 06:05 AM
Very nice work, like mc donald : "I'm lovin' it" :D.
Just 2 comments :
- You should have made the HP a bit longer (rolled up) because compressors sometimes strongly vibrate on start up.
- I deffinetly don't understand why you're still obstinated with SLHX :| . If you check the design features you'll see that this compressor isn't able to carry any big load under -45° (holds sth like 100w under -35° :/) and trying to reduce the LP won't help it to do its work properly as you reduce in the same time the flow...
sacha35
03-17-2007, 06:15 AM
Very nice work, like mc donald : "I'm lovin' it" :D.
Just 2 comments :
- You should have made the HP a bit longer (rolled up) because compressors sometimes strongly vibrate on start up.
- I deffinetly don't understand why your still obstinated with SLHX :| . If you check the design features you'll see that this compressor isn't able to carry any big load under -45° (holds sth like 100w under -35° :/) and trying to reduce the LP won't help it to do its work properly as you reduce in the same time the flow...
Hi there thanks for your coments, i am just trying this compressor out first to see how well or not it works with this setup, as you see there is loads of room so i could easy fit a nice SC18 in there which should be more than big enough for this setup to work.
As for a desuperheat coil i have opted to not have one as this would increase the capacity even more, to get over the vibration the condensors will be mounted on rubber mounts so this should take up any vibration as both the compressor and condensors will both be able to move when the comprssor is starting and running.
Thanks again for your active coments though.
Sacha
Clemmaster
03-17-2007, 07:15 AM
I think it won't be enough because I suppose they will be attached by the feet?! When the unit starts (not every time, juste sometimes, I don't know exactly why but I think it depends to the position of the piston....) it "jumps ahead" and even if they're attached compressor will "compress" the pipe :p
About SLHX's : It's not because someone uses it on his systems that you have to make the same on every one : It's useless when you haven't got a powerfull compressor, able to carry much more load than ever requiered by the systems : You use a part of the power to help gas being condensed at lower pressure and so the unit is able to work at some "pressure" it's not designed for. Keep in mind that the power of the compressor don't make everything : If you compare the danfoss nl11f and SC10G (both 1/3hp) you'll be surprised by the capability of these 2 compressors :
- Danfoss NL11F is able to carry 105w under -35°
- Danfoss SC10G isn't able to carry more than 23w under the same temperature xD
Both are using the same gas, R134a, condensing at 55°.
Another exemple :
http://clemmaster.free.fr/sc18G_vs_SC18CL.jpg
on the left : Danfoss SC18CL
on the right : Danfoss SC18G
Both are 500w compressors, one runs with R134a condensing at 55° (G), the other one with R404a condensing at 45° (CL). The SC18CL works at even worse conditions (the high pressure is higher).
n00b 0f l337
03-17-2007, 07:24 AM
We run these so out of spec, many people have gotten -40C with 200 watts of load. Look at little devils builds.
Clemmaster
03-17-2007, 07:42 AM
I know that, the condensing temperature isn't as high as in the CECOMAF certifications, I've gotten the same too but if you look at the temp reached : -40° : there's no need to add any SLHX to reach theses temperatures as the R404a, R402a, R507c... is still around 1bar BP
Dimas
03-17-2007, 08:15 AM
nice case...and buld too, waiting for temps;)
sacha35
03-17-2007, 09:13 AM
I think it won't be enough because I suppose they will be attached by the feet?! When the unit starts (not every time, juste sometimes, I don't know exactly why but I think it depends to the position of the piston....) it "jumps ahead" and even if they're attached compressor will "compress" the pipe :p
About SLHX's : It's not because someone uses it on his systems that you have to make the same on every one : It's useless when you haven't got a powerfull compressor, able to carry much more load than ever requiered by the systems : You use a part of the power to help gas being condensed at lower pressure and so the unit is able to work at some "pressure" it's not designed for. Keep in mind that the power of the compressor don't make everything : If you compare the danfoss nl11f and SC10G (both 1/3hp) you'll be surprised by the capability of these 2 compressors :
- Danfoss NL11F is able to carry 105w under -35°
- Danfoss SC10G isn't able to carry more than 23w under the same temperature xD
Both are using the same gas, R134a, condensing at 55°.
Another exemple :
http://clemmaster.free.fr/sc18G_vs_SC18CL.jpg
on the left : Danfoss SC18CL
on the right : Danfoss SC18G
Both are 500w compressors, one runs with R134a condensing at 55° (G), the other one with R404a condensing at 45° (CL). The SC18CL works at even worse conditions (the high pressure is higher).
I think you are referring to the Transient starting phase angle, yes this would have a big impact if the condensers were mounted to something rigged, but as explained they will be able to move with the compressor as they will be mounted on rubber mounts from the back plate thus allowing up/down and sideways movement.
I take what you are saying with regards the SLHX and I think you have seen where some have good and bad results with them, if this proves to be problematic then it will not be a big job to remove this and connect in conventional way, but saying this, this is why we try and push the boundaries of phase change seeing what gasses and compressors can do under different conditions, this is how we learn about the cause and effect of things that are happening.
As n00b 0f l337 said we run these so out of spec, many people have gotten -40C with 200 watts of load. Look at little devils builds, this is why we try different things, and some work and some don’t.
sacha
Really nice dude. Has some very very high tech but also arty feel to it and more! I like the idea of the airflow being directed at the side of it.
Can you tell me how you got your gauges to stay in place? If you have any photos of that PM them over saves spaming your topic.
Hope it all goes okay dude
Pete
sacha35
03-19-2007, 02:49 AM
Hi there pete, thanks for the coments, they are just ashcroft Gauges with a u Clamp bracket to hold them in, you can see this in the photos posted.
Link:
http://www.ashcroft.com/products.cfm?doc_id=192
Hi there pete, thanks for the coments, they are just ashcroft Gauges with a u Clamp bracket to hold them in, you can see this in the photos posted.
Link:
http://www.ashcroft.com/products.cfm?doc_id=192
So the bracket stop it from moving ether way...umm looks like i'm going to steal that idea for mounting the ones in my rig. Guess just make the plate and use a nut to hold it in place
andybg
03-21-2007, 04:09 PM
Looks good but that ferrule on the suction tap has to piss you off :D .
Clemmaster
03-22-2007, 07:09 AM
Clemmaster,
First you're comparing two compressors opperating at approx 0.7bar suction with r134a (not realistic) the two compressors having displacements of 10.3cc and 11.2cc
Instinctivly the NL11 will be the better compressor due to the higher displacement and it does perform better than the SC10. As the evaporating temperature rises the SC10 does pull back against the NL11 and at higher suction pressures the capacity differences become that of the displacement difference.
The reason is the SC range don't do so well in LBP opperation, but you can't get the NL series with 18cc of displacement either...
With the second comparison you cant compare them like that, you're running two different refrigerants. To be honest wether a compressor is rated at 1/3IHP or 12000BTU's or 500W is fairly irrelevant for us as we're not evaporating, condensing at the pressures or in most cases even running the manufactures specified refrigerant.
All that matters for us is the displacement, rpm, efficiency (in our conditions) and wether the motor is capable of running under the loads we subject it to.
The idea of a SLHX being used to transfer sensible heat from the gas state refrigerant into the liquid line to decrease enthlapy of the liquid refrigerant, at the expense of suction line gas density is not the main point with this, it's a nice side effect at best.
The idea is that as the swing in load can be very large. Without using a true suction line accumulator there needs to be some means of evaporating the return liquid under idle conditions, this is provided by the small SLHX which will provide this energy from the warm liquid but also via conduction from the condensors.
When the system is under full load the gas heat exchange from 10" of 1/4" inside 1/2" will be small and hopefully not have too much of an effect on suction gas density. As the system is capillary tube regulated the superheat under full load will already be high, but the aim is that by using this SLHX the full load superheat can be decreased by increasing the systems charge, the SLHX preventing liquid return under idle.
Manufacturers data isn't very usefull when you have 20% less suction gas density under full load.
Tom
Displacement doesn't justify such difference between the to compressors. You can compare the SC12G that is a 1/2hp with 12.9cm^3 displacement compressor to the nl11f as you please and you'll see that the first one isn't able to carry more than 65w compared to the 100w the nl11f is able to carry with only 1/3hp and 11.2cm^3 displacement. both tested with in the same conditions. So That confirm what I'm saying : the power doesn't mean anything itself.
About gases : I've made simulation with Coolpack and if you set the condensing pressure and evaporating temperature, results are almost similar between R134a and R404a : one has got an higher "volume throughput" (don't know how to say in english :D) and a lower density (R134a), and the reverse for R404a : they compensate each other. Only true limit may be that the motor is "speed-limited".
Unfortunatelly there is no documentation about the SC18B that is a SC18CL running with R134a and that we can compare to the SC18G, i've got one and I can affirm that they're performing better in LBP than SCxxG do (I had got 1 SCxxG and SCxxB and I've seen the difference between them two : the SC18B is able to carry my waterchiller evap under -50°, the SC10G wasn't able to freeze completely an smaler one under -30° :/ (without any load of course).
About SLHX's now : it actually decrease enthalpy and they're useless on nl11F-designed system as This compressor isn't designed to work at such pressures. The only thing I find good si that by decreasing HighSide pressure and increasing a bit the vapor density you descrease the Pressure ratio and that's a good point for compressors that perform at best with a ratio around 6. You just reach lower evaporating temperature but once loaded if you still want it to make effect you've got to charge more gas and then the effects that goes with.
Warning, I'm not saying that they are useless on every systems, with big compressors that are able to carry lot more than enough at low pressure it helps him to work at even lower pressure. A rotary with R410A and SLHX may be the best using :D
Edit : round 2
http://clemmaster.free.fr/nl11f_vs_sc12g.jpg
Barnsley-Bill
03-22-2007, 12:12 PM
Looks realy nice sacha35 very clean and pro looking once again love to see how it gose mate :).
sacha35
03-22-2007, 02:25 PM
Looks realy nice sacha35 very clean and pro looking once again love to see how it gose mate :).
Just awating Chillys new evap kit, which i should have by the end of next week, then it will be all systems go with tuning and testing and tuning.
{.bLanK} GoD
03-22-2007, 02:37 PM
And more testing and tuning :P lol
Good luck dude.
Have you pressure tested what you have done so far?
sacha35
03-22-2007, 03:31 PM
Thanks there {.blank} God, yes some pressure testing has been done and all is ok so far, so when i have the evap it will just mean testing this then brazing it all together and retesting the whole thing, and then like you said And more testing and tuning :P lol
Clemmaster
03-30-2007, 03:44 PM
I've just read what you're saying and I realize that we agree each other. When I compare SC18 angainst SC10 I know that there is an enormous power difference between them but I know how the system would perform if there where the same power (as I runned them without any load, even if it takes more time to freeze with the SC10G) : I just compare SCxxCL/B against SCxxG and I'm sure that the CL or CLX do perform very well in vaccum (they're designed that for...), and a SCxxG may like "pushing". SC18B is LBP designed compressor, like the SC18CL. All I want to say is tht most of phase-change make don't really know what they're building their systems with, they just do compare 2 compressors with their "power rating", they're not looking at the pressures they are designed for and that's why some of them don't understand why, for example, the nl11f can carry such load.
About SLHX's I think we agree to that most of them are fully oversized and they are not playing the role they're supposed to play because system must be overcharged to freeze it entire and it becomes finally useless.
When I say ratio 6 I know that we are running out of this, and on well-powered system I may reduce the ratio a bit :). What would be interesting to test is the serial compressors single stage unit. A LBP compressor such as nl11f do vaccum work, compress a bit the gas around 3-4bar (to reach ratio 6-8) and a MBP compressor compress the gas again and works in the pressures it's designed for : >2.4bar at succion line and a High pressure around 16bar. It may work wery well with R410A, I know that's used in the industry and I don't know if anybody has ever done the same.
Xeon th MG Pony
03-30-2007, 05:19 PM
You designed the unit very well, how ever vibration will work harden the tubing leading to cracking in the tubing prematurely. hence the vibration dampener between condenser and compressor.
Other then that very nice well layed out system!
sacha35
03-30-2007, 05:26 PM
You designed the unit very well, how ever vibration will work harden the tubing leading to cracking in the tubing prematurely. hence the vibration dampener between condenser and compressor.
Other then that very nice well layed out system!
Thanks for your coments Xeon, as said in post 10, i have overcome the vibration problem by mounting the condensors on rubber mounts so this should take up any vibration as both the compressor and condensors will both be able to move when the comprssor is starting and running.
Xeon th MG Pony
03-30-2007, 05:41 PM
No this will not as torquing forces within the tube leading to the condenser will still be exerted and the inertial mass of the condensers will yield the loading on the joints. The rubber will remove harmonics being transfered to the case but will not cancel out the stresses being imposed onto the tubing.
When the compressor starts force must be exerted on the tubing to get the condensers to move, this force will harden and then eventually crack the tube.
sacha35
03-30-2007, 05:45 PM
But if the compressor and the condensors are mounted on the same platform that moves with each outher then how can there be stress on the pipwork when they are both moving in tandam
Xeon th MG Pony
03-30-2007, 09:09 PM
inertial lag, you can only accelerate the condensers so fast. All tubing work hardens, but with proper allowances we can greatly delay the effects.
Clemmaster
03-31-2007, 01:29 AM
Yes i think so mainly, although the point of the SLHX on this wasn't to increase capacity and the way it's done i think it will work well for what it's intended (higher capacity without liquid return).
Series compressors i'm not sure about, oil will be a problem. Also the high suction temperature on the second compressor could give a nasty discharge temp for that compressor. Small displacement cascaded systems with normal (powerful) single stage performance could achieve the low compression ratios you're talking about tho. The efficiency of each stage could be exceptionally high (compared to what we're used to) if the right refrigerants and compressor were used...
Tom
I don't know exactly how those systems are designed but I know that exist and perform very well. Maybe they're using a bit of the liquid return to decrease the discharge gas temperature of the LBP stage, If I get a new SC10G I think I'll couple it with a nl11f, just for fun :D.
About cascaded system, I've though about that :
1st : SC12G (MBP) - R507C @ -20° evap (sth like 3 bar)
2nd : SC12G (MBP - R170 @ - -65° evap (sth like 3 bar)
3rd : nl11f (LBP) - R1150 @ -110° (sth like <1bar) //or SCxxCLX
Each compressor would work with pressures it's designed for and @ these temperatures, SC12G can become very powerfull (600w and even more), more over the COP will be around >2, that's good for power comsumption :D
I can't find one single stage round here which has a compression ratio of 6. It's more like 14 to 18 for the large r402 systems round here, even for very small r404a systems it's about 10 :) It would be very nice if it were as low as that as it'd increase compressor performance a fair bit...
Tom
Hey Tom! My autocascade has a compressor ration 2:14= 1:7 ... If we could build small autocascades, that would increase the performance...
R290/R744 is also quite easy to do.
sacha35
06-03-2007, 09:12 AM
Well guys as promised I have finally sorted out the S/S unit and have some temperature results for you all to see, as you can see I have used my load tester which is within +- 2 watts and the fluke is also within +- 1c, so after other commitments and a few problem of which are sorted now here are some pics for your viewing.
-68c, First run up know load, very small amount of flood back at compressor, 5 minute run
http://img490.imageshack.us/img490/9218/pict0208dz8.jpg
50 watt load applied, -54.5c, know flood back at all.10 minute run
http://img472.imageshack.us/img472/6940/pict0218nx2.jpg
151 watt applied -51.5c,1 hour run
http://img472.imageshack.us/img472/9864/pict0217bp1.jpg
254 watts applied -48.1c,1 hour run.
http://img490.imageshack.us/img490/7067/pict0213ib2.jpg
272 watts applied -38.4c,1 hour run.
http://img472.imageshack.us/img472/8624/pict0212ml1.jpg
282 watts applied -32.3c, 1 hour run, this was the limit of the unit as when i tried for 290 watts it started to drop below -20,
http://img472.imageshack.us/img472/9264/pict0209vz5.jpg
Then back to the start again with know load, notice that this is slitly higher then when i started as the unit is very hot now. -59.5c.
http://img138.imageshack.us/img138/9448/pict0222sr0.jpg
teyber
06-03-2007, 09:18 AM
didn't you finish this around christmas?
aer you waterboy from extremeoverclocking?
looks good, seems to hold pretty massive loads!
{.bLanK} GoD
06-03-2007, 06:48 PM
Nice one Sacha. How long before you get that sucker bolted to a hot CPU?
Brettbeck
06-04-2007, 09:25 AM
Great job sacha! I notice the case is now black too? Any pics of the entire unit :)?
4Qman
06-04-2007, 12:05 PM
Great job sacha! I notice the case is now black too? Any pics of the entire unit :)?
Thats the load tester dude. I am sure Sacha will gets some pics up once its all polished up. :up:
Polizei
06-04-2007, 01:36 PM
Nice temps even at high load.
Good job.
Nosfer@tu
06-04-2007, 01:59 PM
didn't you finish this around christmas?
aer you waterboy from extremeoverclocking?
Yep he is :) (http://forums.extremeoverclocking.com/t253742.html)
gosmeyer
06-04-2007, 02:02 PM
hope to have the unit running a mixture of R402a and R410a which will make things run that bit hotter than normal.
Sacha
Nice job.
Is this what you were using in load test?
sacha35
06-05-2007, 06:29 AM
Thanks for all the comments guys, well in the end i did use a mix of refrigerants, the main part is 402a about 85%, then 15% of 410a which brought the pressure up-to 270 PSI on the high side under full load so i added a about 5% of 134a which seems to give a nice all-round use of temps under different loads and has drooped the high side pressure down to about 245-250 under full 282watts of load and this was run for over an hour at this load and stayed within -32c - 33c and has been test again over a few days just to make sure nothing has changed.
Again this has not been an easy build with its complexity, but i think you will all agree that with the load temperatures i have got from this unit it has turned out very well for a small NL11 compressor
I have got a lot of cleaning and finishing touches to do to this unit and then i will post some final pics for your viewing.
Thanks again everyone for your kind comments,
I would also like to thank SoddemFX which helped me in the design of this unit, also Bazx which has been a great help, 4Qman without his garage we would have been stuck,also the guys that i bought these parts from, Chilly1 evap, the new one works so much better than his old one, Unseen for his controller that works like a charm.
Again this has not been an easy build with its complexity, but i think you will all agree that with the load temperatures i have got from this unit it has turned out very well.
Brettbeck
06-05-2007, 07:48 AM
Thats the load tester dude. I am sure Sacha will gets some pics up once its all polished up. :up:
Oops lol :rolleyes: . Never thought about that for some reason. Maybe I should look closer at the pictures or post when i'm more awake lol :p: .
Blaster
06-05-2007, 08:15 AM
Nice compressor you got there!
At 250 watts suction pressure is 0 as i can see from temp, and high side at 250 psi... wow my nl11f cant hold that compression ratio. Good job !
sacha35
06-07-2007, 09:20 AM
OK Guys as requested some more pics of the finished item, one question for you guys now, what do you think is more important to you, out right performance from a S/S or looks or both.
Thanks again for your coments.
sacha35
http://img459.imageshack.us/img459/8900/pict0223yy2.jpg
http://img471.imageshack.us/img471/6243/pict0229ve7.jpg
http://img471.imageshack.us/img471/6689/pict0238tg6.jpg
http://img471.imageshack.us/img471/5562/pict0243co0.jpg
http://img471.imageshack.us/img471/3959/pict0250ya1.jpg
http://img471.imageshack.us/img471/1696/pict0257hm8.jpg
http://img471.imageshack.us/img471/4782/pict0261dr3.jpg
gosmeyer
06-07-2007, 09:31 AM
One in the same as far as I'm concerned.
Nice job!
Brettbeck
06-07-2007, 10:19 AM
Nice one Sacha!
I think it depends who is going to use the single-stage as to whether outright performance or looks is the most important thing.
If it's a benching unit for at home then I don't think there's any need to make it look all that fancy (if it's going to cost). Are you going to sell it or keep it yourself?
Barnsley-Bill
06-07-2007, 11:51 AM
it looks brilliant Sacha and the testing results are great imo.
Im making a load tester something like yours with a variac a 3amp mcb and 300watt heat cartridge Id like to pick your brains about wiring it up right if you dont mind Im going to use a plug in wattage and current meter to messure the watts.
:)
sacha35
06-07-2007, 12:42 PM
it looks brilliant Sacha and the testing results are great imo.
Im making a load tester something like yours with a variac a 3amp mcb and 300watt heat cartridge Id like to pick your brains about wiring it up right if you dont mind Im going to use a plug in wattage and current meter to messure the watts.
:)
Hi there any questions regarding help with making a load tester move to PM mate and i will help you out as much as i can.
Thanks for your comments.
Sacha
Nosfer@tu
07-03-2007, 03:21 AM
I think it is one of the cooler builds here on xs :D
The design ROX.
one_servant
07-03-2007, 07:14 AM
Man, that enclosure is excellent! I admire the design and your fit and finish is superb. Well done. :rocker: